AC input
AC input | |||
AC input | Nom. | AC 100 - 240 V | Suitable for TN, TT and IT networks |
AC input range | Min. | 90 - 264 Vac | Continuous operation |
Min. | 85 - 90 Vac | < 55°C continuous ambient temperature permissible | |
Min. | 60 - 85 Vac | Full power for 200 ms, no damage between 0 and 85 Vac | |
Min. | 264 - 300 Vac | < 500 ms | |
Permissible voltage L or N to earth | Max. | 300 Vac | Continuous according to IEC 62103 |
Input frequency | Nom. | 50 - 60 Hz | ±6% |
Turn-on voltage | typically | 80 Vac | Static, load independent, see Fig. Input voltage range; Turn-on behavior definitions |
Shut-down voltage | typically | 74 Vac | Static, load independent, see Fig. Input voltage range; Turn-on behavior definitions |
External input protection | see recommendations in chapter External input protection | ||
AC input |
| AC 100 V | AC 120 V | AC 230 V |
Input current | typically | 10.5 A | 8.6 A | 4.5 A | At 48 V, 20 A, see Fig. Input current over output current; power factor over output current |
Power factor1) | typically | 0.99 | 0.99 | 0.99 | At 48 V, 20 A, see Fig. Input current over output current; power factor over output current |
Peak factor2) | typically | 1.47 | 1.53 | 1.56 | At 48 V, 20 A |
Start-up delay | typically | 800 ms | 750 ms | 700 ms | See Fig. Input voltage range; Turn-on behavior definitions |
Rise time | typically | 16 ms | 16 ms | 16 ms | At 48 V, 20 A, 0 mF load capacity, see Fig. Input voltage range; Turn-on behavior definitions |
typically | 55 ms | 55 ms | 55 ms | At 48 V, 20 A, 20 mF load capacity, see Fig. Input voltage range; Turn-on behavior definitions | |
Turn-on overshoot | Max. | 100 mV | 100 mV | 100 mV | See Fig. Input voltage range; Turn-on behavior definitions |
1) The power factor is the ratio of real (or active) power to apparent power in an AC circuit.
2) The peak factor is the mathematical ratio of the peak value to the RMS value of the input current waveform.