DC-OK relay contact
This function monitors the output voltage generated by the power supply itself. It is independent of a voltage fed back from a unit connected in parallel to the power supply output.
DC-OK relay contact
The contact closes
when the output voltage reaches the set output voltage.
The contact opens
when the output voltage drops more than 10% below the set output voltage.
  • Drops > 1 ms are extended to a signal length of 250 ms.
  • Drops < 1 ms are ignored.
The contact closes again
when the output voltage exceeds 90% of the set voltage.
Switching hysteresis
typ. 0.7 V
Contact load capacity
Maximum 60 Vdc 0.3 A, 30 Vdc 1 A, 30 Vac 0.5 A, ohmic load
Minimum permissible load: 1 mA at 5 Vdc
Insulation voltage
See the table in chapter Dielectric strength
DC-OK relay contact 1:Fig.9: Behavior of the DC-OK relay contact
DC-OK relay contact 2:
DC-OK function
The DC-OK function requires the output voltage to reach the rated (=set) level after power-up in order to function as specified.
  • If this level is not reached, the overload LED lights up and the DC-OK contact opens. The overload LED goes out when the set voltage is reached.
  • This is an important condition to be considered especially if the load is a battery, the power supply is used in parallel or the power supply is used for N+1 redundant systems.
