Environment

Environment

Operating temperature 1)

-25°C to +70°C

Reduction of the output power according to Fig. Output current over ambient temperature

Storage temperature

-40°C to +85°C

For storage and transport

Output load reduction
(derating)

3.2W/°C / 6W/°C

+45°C to +60°C / +60°C to +70°C

15W/1000m or 5°C/1000m

For altitudes >2000m, see Fig. Output current over installation altitude

9W/-5kPa or 3°C/-5kPa

For atmospheric pressures <80kPa, see Fig. Output current over installation altitude

The derating is not hardware-controlled. The user must take this into account in order to stay below the reduced current limits, so that device overload is avoided.

Moisture

5 to 95% r.h.

According to IEC 60068-2-30
Do not energize if there is condensation.

Atmospheric pressure

110-47kPa

see Fig. Output current over installation altitude

Installation altitude

up to 6000m

see Fig. Output current over installation altitude

Overvoltage category

III

According to IEC 60664 -1, installation altitudes up to 2000m

II

According to IEC 60664 -1, installation altitudes above 2000m and atmospheric pressures between 80 and 47kPa

Degree of pollution

2

According to IEC 62477-1, non-conductive

Oscillation, sinusoidal 2)

2–17.8Hz: ±1.6mm;
17.8–500Hz: 2 g
2 hours/axis

According to IEC 60068-2-6

Impacts 2)

30g 6ms, 20g 11ms
3 impacts/direction, 18 impacts in total

According to IEC 60068-2-27

LABS-free

The device does not release any silicones or other paint-wetting impairment substances and is suitable for use in paint shops.

Corrosive gas

Tested according to ISA-71.04-1985, Severity Level G3, IEC 60068-2-60 Test Ke Method 4 for a service life of at least 10 years in these environments.

Audible noises

In the event of no-load, overload or short circuit, the power supply unit emits audible noises.

1) The working temperature is identical to the room temperature or the ambient temperature and is defined as the air temperature 2cm below the device.

2) Tested in conjunction with DIN rails according to EN 60715 with a height of 15mm and a thickness of 1.3mm and standard mounting position.

Environment 1:
Output current over ambient temperature; output current over installation altitude