Output
The output provides an SELV/PELV nominal voltage that is electrically isolated from the input voltage. The device is designed to supply any type of load, including capacitive and inductive loads. If very large capacitors, such as EDLCs (electrical double-layer capacitors or "UltraCaps") with a capacitance > 1 F are connected to the output, the device can charge the capacitor intermittently. The device is equipped with a "Single Use / Parallel Use" function, which can be selected via the CoE data. The output is electronically protected against overload, no-load and short circuit. In the event of a protection event, audible noises may occur. |
Output voltage | Nom. | 48 V |
Adjustment range | Min. | 48...56 V | Guaranteed value |
Max. | 60.0 V | This is the maximum output voltage which can occur at the clockwise end position of the potentiometer due to tolerances. It is not guaranteed value which can be achieved. | |
Factory settings | Typ. | 48 V | ±0.2%, "single use" at full load and cold device |
Typ. | 47 V | ±0.2% in "Parallel Use" mode at 10 A, with cold device | |
Line regulation | Max. | 10 mV | Between 85 and 300 Vac |
Load regulation | Max. | 150 mV | Between 0 and 10 A, static value, "single use" |
Typ. | 1000 mV | Between 0 and 12 A, static value, "parallel use" | |
Residual ripple and noise voltage | Max. | 50 mVPP | Bandwidth 20 Hz to 20 MHz, 50 Ohm |
Output current for input voltage range 1 | Nom. | 12 A1) | At 48 V and up to 45°C ambient temperature |
Nom. | 10 A | At 48 V and up to 60°C ambient temperature | |
Nom. | 7.4 A | At 48 V and 70°C ambient temperature | |
Nom. | 10.3 A1) | At 56 V and up to 45°C ambient temperature | |
Nom. | 8.6 A | At 56 V and up to 60°C ambient temperature | |
Nom. | 6.35 A | At 56 V and 70°C ambient temperature | |
Linear derating between +60°C and +70°C (see chapter Environment) | |||
Output current for input voltage range 2 | Nom. | 10.5 A1) | At 48 V and up to 45°C ambient temperature |
Nom. | 8.75 A | At 48 V and up to 60°C ambient temperature | |
Nom. | 6.56 A | At 48 V and 70°C ambient temperature | |
Nom. | 9.0 A1) | At 56 V and up to 45°C ambient temperature | |
Nom. | 7.5 A | At 56 V and up to 60°C ambient temperature | |
Nom. | 5.65 A | At 56 V and 70°C ambient temperature | |
1) This continuous power / current is permissible up to an ambient temperature of +45°C. It decreases linearly between 45 and 60°C up to the nominal power / nominal current s. chapter "Environment". Above +45°C, use this power / current for a maximum duty cycle of 10%, i.e. no more than 1 minute every 10 minutes. | |||
Fig.6: Output voltage vs. output current (single use); output voltage vs. output current (parallel use)Safety | Typ. | 30 A | Up to 12 ms once every five seconds, see fig. Dynamic overcurrent capability, typ. < 12 ms |
Overload behavior | Continuous current | Output voltage > 26 Vdc, see Fig. Output voltage vs. output current | |
Hiccup mode2) | Output voltage < 26 Vdc, see Fig. Output voltage vs. output current | ||
Overload/ short-circuit current | Max. | 14.8 A | Continuous current see fig. Output voltage vs. output current typ. |
Typ. | 15 A | Intermittent current peak value for typ. 2 s | |
Max | 4.7 A | RMS value of current, | |
Output capacitance | Typ. | 2500 μF | Included in the power supply |
Load feedback | Max. | 63 V | The device is resistant to load feedback and does not show malfunctioning when a load feeds back voltage to the power supply. It does not matter whether the power supply is switched on or off. The absorbed energy can be determined by means of the built-in large sized output capacitor. |
2) In the event of heavy overload (when the output voltage drops below 13 V), the power supply provides continuous output current for 2 s. The output is then switched off for about 18 seconds before a new switch-on attempt is automatically made. This cycle is repeated as long as the overload persists. After the overload has been rectified, the device will operate normally. See Fig. Short circuit at output, hiccup mode, typ. | |||
Fig.7: Short circuit at output, hiccup mode, typ.
