Output
The output provides an SELV/PELV/ES1 nominal voltage that is electrically isolated from the input voltage.
The device is designed to supply any type of load, including capacitive and inductive loads. If very large capacitors, such as EDLCs (electrical double-layer capacitors or "UltraCaps") with a capacitance > 0.25F are connected to the output, the device can charge the capacitor intermittently.
The output is electronically protected against overload, no-load and short circuit. In the event of a protection event, audible noises may occur
Output voltage
Nom.
48V
Adjustment range
Min.
48-56V
Guaranteed value
Max.
60V
This is the maximum output voltage that can occur in the end position of the potentiometer in clockwise direction due to tolerances. It is not a guaranteed value that can be achieved.
Factory settings
Typ.
48.0V
±0.2%, single use at full load (cold device)
Typ.
47.0V
±0.2%, parallel use at 10A (cold device)
(46.6V ±0.2% at 12A and 49.0V ±0.2% at zero load)
Line regulation
Max.
10 mV
Between 85 and 300Vac
Load regulation
Max.
150 mV
Between 0 and 10A, static value, "single use"
Typ.
2000 mV
Between 0 and 10A, static value, "parallel use", see Fig. Output voltage over output current (parallel use) typ.
Residual ripple and ripple voltage
Max.
50mVSS
Bandwidth 20 Hz to 20 MHz, 50 Ohm
Output current
Nom.
12A1)
At 48 V and ambient temperature below 45°C
Nom.
10A
At 48 V and 60°C ambient temperature
Nom.
7.5A
At 48 V and 70°C ambient temperature
Nom.
10.3A1)
At 56 V and ambient temperature below 45°C
Nom.
8.6A
At 56 V and 60°C ambient temperature
Nom.
6.5A
At 56 V and 70°C ambient temperature
Linear derating between +45°C and +70°C
Safety
switch-off current
Typ.
30A
Up to 12ms once every five seconds, see Fig. Dynamic output current capacity, typ.
The fuse switch-off current is an increased transient current that contributes to the tripping of fuses on faulty output branches. The output voltage remains above 40V.
Overload behavior
Continuous current
Output voltage > 26Vdc, see Fig. Output voltage over output current, typ.
Hiccup mode 2)
Output voltage < 26Vdc, see Fig. Output voltage over output current, typ.
Short circuit current
Max.
14.8A
Continuous current, see Fig. Output voltage over output current, typ.
Typ.
15A
Intermittent current peak value for typ. 2s
Load impedance 10mOhm, see Fig. Short circuit at the output,
The discharge current of the output capacitors is not included.
max
4.7A
RMS value of the current,
Output capacity
Typ.
2500μF
Included in the power supply
Load feedback
Max.
63V
The device is resistant to load feedback and will not indicate a malfunction if a load is feeding voltage back into the power supply. It does not matter whether the power supply is switched on or off. The absorbed energy can be determined by means of the built-in large-size output capacitor.
1) This current is also available for temperatures up to +70°C with a duty cycle of 10% and/or no more than 1 minute every 10 minutes.
2) In the event of heavy overload (when the output voltage drops below 13V), the power supply provides continuous output current for 2s. The output is then switched off for about 18 seconds before a new switch-on attempt is automatically made. This cycle is repeated as long as the overload persists. After the overload has been rectified, the device will operate normally. See Fig. Short circuit at output, hiccup mode, typ.
Output 1:
Output voltage over output current (single use); output voltage over output current (parallel use)
Output 2:
Short circuit at output, hiccup mode, typ.; Dynamic output current capacity, typ.