AC input
The device is suitable for being supplied with AC voltage from TN, TT and IT networks. For suitable DC supply voltages see chapter DC input.
AC input | |||
AC input | Nom. | AC 100-240V | Suitable for TN, TT and IT networks |
AC input range | Min. | 85-264Vac | Continuous operation |
Min. | 264-300Vac | For up to 500ms max. | |
Permissible voltage L or N to earth | Max. | 300Vac | Continuous according to IEC 60664-1 |
Input frequency | Nom. | 50-60Hz | ±6% |
Turn-on voltage | Typ. | 82Vac | Static, see Fig. Input voltage range; switch-on behavior definitions |
Shut-down voltage | Typ. | 72Vac | Static, see Fig. Input voltage range; switch-on behavior definitions |
AC input |
| AC 100V | AC120V | AC230V |
Input current | Typ. | 5.15A | 4.26A | 2.23A | At 48V, 10A, see Fig. Input current over output current; power factor over output current |
Power factor*)
| Typ. | 0.996 | 0.996 | 0.980 | At 48V, 10A, see Fig. Input current over output current; power factor over output current |
Peak factor**) | Typ. | 1.65 | 1.63 | 1.63 | At 48V, 10A |
Start-up delay | Typ. | 450ms | 450ms | 450ms | See Fig. Input voltage range; switch-on behavior definitions |
Rise time | Typ. | 120ms | 120ms | 120ms | At 48V, 10A constant current load, 0 mF load capacity, see Fig. Input voltage range; switch-on behavior definitions |
Typ. | 170 mV | 170 mV | 170 mV | At 48 V, 10 A constant current load, 10 mF load capacity, see Fig. Input voltage range; switch-on behavior definitions | |
Turn-on overshoot | Max. | 500 mV | 500 mV | 500 mV | See Fig. Input voltage range; switch-on behavior definitions |
*) The power factor is the ratio of real (or active) power to apparent power in an AC circuit.
**) The peak factor is the mathematical ratio of the peak value to the RMS value of the input current waveform.