Terminals and wiring

The terminals are designed to be finger-safe according to IP20 and are suitable for field and factory wiring.

Technical data

Input

Output

EtherCAT

Connection cross-section

e*: max. 6 mm²

f*:  max. 4 mm²

a*: max. 4 mm² (d < 2.8 mm)

e*: max. 6 mm²

f*:  max. 4 mm²

a*: max 4 mm² (d < 2.8 mm)

Bus interface:
2 x RJ45

Data transfer medium:
Ethernet/EtherCAT cable (min. Cat 5), shielded

Connection cross section (AWG)

e*: AWG 20-10

f*: AWG 20-10

a* AWG 20-10 (d <2.8 mm)

e*: AWG 20-10

f*: AWG 20-10

a* AWG 20-10 (d<2.8 mm)

Strip length

10 mm / 0.28 inch

10 mm / 0.28 inch

e* = single-wire, solid wire

f* = stranded wire

a* = with ferrule

Wiring instructions:

  • Use suitable copper cables that are designed for at least the following working temperatures:
    +60°C for ambient temperatures up to +45°C and
    +75°C for ambient temperatures up to +60°C and
    +90°C for ambient temperatures up to +70°C.

Terminals and wiring 1:

  • Observe the national installation rules and regulations!
  • Insert the wire into the opening (A).
  • Turn the lever (B).
  • To disconnect the cable, proceed in reverse order.
  • Make sure that all single wires of a strand are connected to the terminal!
  • Ferrules are permitted.
  • Do not use the device without PE connection.

Series connection of power supply units

Series connection (looping from one power supply output to the next) is not allowed. Use a separate distribution terminal strip as shown in Fig. Using distribution terminals.

Terminals and wiring 2:Fig.11: Using distribution terminals