Output

The output provides an SELV/PELV/ES1 nominal voltage that is electrically isolated from the input voltage.

The device is designed to supply any type of load, including capacitive and inductive loads. If very large capacitors, such as EDLCs (electrical double-layer capacitors or "UltraCaps") with a capacitance > 1F are connected to the output, the device can charge the capacitor intermittently.

The output is electronically protected against overload, no-load and short circuit. In the event of a protection event, audible noises may occur

Output voltage

Nom.

24V

 

Adjustment range

Min.

24-28V

Guaranteed value

Max.

30.0V

This is the maximum output voltage that can occur in the end position of the potentiometer in clockwise direction due to tolerances. It is not a guaranteed value that can be achieved.

Factory settings

Typ.

24.1V

±0.2%, single use at full load (cold device)
±0.2%, parallel use at 20A (cold device)
(23.9V ±0.2% at 24A and 25.1V ±0.2% at zero load)

Line regulation

Max.

10 mV

Between 85 and 300Vac

Load regulation

Max.

100 mV

Between 0 and 24A, static value, "single use"

Typ.

1000 mV

Between 0 and 20A, static value, "parallel use", see Fig. Output voltage over output current (parallel use) typ.

Residual ripple and ripple voltage

Max.

50mVSS

Bandwidth 20 Hz to 20 MHz, 50 Ohm

Output current

Nom.

24A1)

At 24 V and ambient temperature below 45°C

Nom.

20A

At 24 V and 60°C ambient temperature

Nom.

15A

At 24 V and 70°C ambient temperature

Nom.

20.6A1)

At 28 V and ambient temperature below 45°C

Nom.

17.1A

At 28 V and 60°C ambient temperature

Nom.

13A

At 28 V and 70°C ambient temperature

Linear derating between +45°C and +70°C

Safety
switch-off current

Typ.

60A

Up to 12ms once every five seconds, see Fig. Dynamic output current capacity, typ.
The fuse switch-off current is an increased transient current that contributes to the tripping of fuses on faulty output branches. The output voltage remains above 20V.

Overload behavior

 

Continuous current

Output voltage > 13Vdc, see Fig. Output voltage over output current, typ.

 

Hiccup mode2)

Output voltage < 13Vdc, see Fig. Output voltage over output current, typ.

Short circuit current

Max.

29.8A

Continuous current, see Fig. Output voltage over output current, typ.

Typ.

29A

Intermittent current peak value for typ. 2s
Load impedance 10mOhm, see Fig. Short circuit at the output,
The discharge current of the output capacitors is not included.

max

9.8A

RMS value of the current,
Load impedance 10mOhm, see Fig. Short circuit at the output,

Output capacity

Typ.

8500μF

Included in the power supply

Load feedback

Max.

35V

The device is resistant to load feedback and will not indicate a malfunction if a load is feeding voltage back into the power supply. It does not matter whether the power supply is switched on or off. The absorbed energy can be determined by means of the built-in large-size output capacitor.

1) This continuous power / current is permissible up to an ambient temperature of +45°C. Above +45°C, use this power / current for a maximum duty cycle of 10%, i.e. no more than 1 minute every 10 minutes.

2) In the event of heavy overload (when the output voltage drops below 13V), the power supply provides continuous output current for 2s. The output is then switched off for about 18 seconds before a new switch-on attempt is automatically made. This cycle is repeated as long as the overload persists. After the overload has been rectified, the device will operate normally. See Fig. Short circuit at output, hiccup mode, typ.

Output 1:
Output voltage over output current (single use); output voltage over output current (parallel use)
Output 2:
Short circuit at output, hiccup mode, typ.; Dynamic output current capacity, typ.