Terminals and wiring
The terminals are designed to be finger-safe according to IP20 and are suitable for field and factory wiring.
Technical data
Input
Output
EtherCAT
Connection cross-section
e*: max. 6 mm²
f*:  max. 4 mm²
a*: max. 4 mm² (d < 2.8 mm)
e*: max. 6 mm²
f*:  max. 4 mm²
a*: max 4 mm² (d < 2.8 mm)
Bus interface:
2 x RJ45
Data transfer medium:
Ethernet/EtherCAT cable (min. Cat 5), shielded
Connection cross section (AWG)
e*: AWG 20-10
f*: AWG 20-10
a* AWG 20-10 (d <2.8 mm)
e*: AWG 20-10
f*: AWG 20-10
a* AWG 20-10 (d<2.8 mm)
Strip length
10 mm / 0.28 inch
10 mm / 0.28 inch
e* = single-wire, solid wire
f* = stranded wire
a* = with ferrule
Wiring instructions:
  • Use suitable copper cables that are designed for at least the following working temperatures:
    +60°C for ambient temperatures up to +45°C and
    +75°C for ambient temperatures up to +60°C and
    +90°C for ambient temperatures up to +70°C.
Terminals and wiring 1:
  • Observe the national installation rules and regulations!
  • Insert the wire into the opening (A).
  • Turn the lever (B).
  • To disconnect the cable, proceed in reverse order.
  • Make sure that all single wires of a strand are connected to the terminal!
  • Ferrules are permitted.
  • Do not use the device without PE connection.
Series connection of power supply units:
Series connection (looping from one power supply output to the next) is permitted as long as the average output current flowing through a connection pin does not exceed 25 A. For higher currents please use a separate distribution terminal strip as shown in Fig. Using distribution terminals.
Terminals and wiring 2:Fig.11: Series connection of outputs; using distribution terminals