AC input
AC input | |||
AC input | Nom. | AC 100 - 240 V | Suitable for TN, TT and IT networks |
AC input range | Min. | 85 - 264 Vac |
Min. | 264 - 300 Vac | For up to 500 ms max. | |
Permissible voltage L or N to ground | Max. | 300 Vac | Continuous according to IEC 60664-1 |
Input frequency | Nom. | 50 - 60 Hz | ±6 % |
Turn-on voltage | Typ. | 82 Vac | Static, see Fig. Input voltage range; turn-on behavior definitions |
Shut-down voltage | Typ. | 72 Vac | Static, see Fig. Input voltage range; turn-on behavior definitions |
External input protection | See notes on installation requirements in chapter "Safety instructions" |
AC input |
| AC 100 V | AC 120 V | AC 230 V |
Input current | Typ. | 2.60 A | 2.17 A | 1.13 A | At 24 V, 10 A, see Fig. Input current vs. output current; power factor vs. output current |
Power factor*) | Typ. | 0.99 | 0.99 | 0.97 | At 24 V, 10 A, see Fig. Input current vs. output current; power factor vs. output current |
Peak factor**) | Typ. | 1.5 | 1.5 | 1.65 | At 24 V, 10 A |
Inrush delay | Typ. | 519 ms | 533 ms | 472 ms | See Fig. Input voltage range; turn-on behavior definitions |
Rise time | Typ. | 105 ms | 105 ms | 103 ms | At 24 V, 10 A constant current load, 0 mF load capacitance, see Fig. Input voltage range; turn-on behavior definitions |
Typ. | 120 ms | 120 ms | 120 ms | at 24 V, 10 A constant current load, 10 mF load capacitance, see Fig. Input voltage range; turn-on behavior definitions | |
Turn-on overshoot | Max. | 200 mV | 200 mV | 200 mV | See Fig. Input voltage range; turn-on behavior definitions |
*) The power factor is the ratio of real (or active) power to apparent power in an AC circuit. **) The peak factor is the mathematical ratio of the peak value to the RMS value of the input current waveform. |