Terminals and wiring
The terminals are designed to be finger-safe according to IP20 and are suitable for field or factory wiring.
Technical data | Input | Output | DC-OK signal |
Connection cross-section | e*: max. 6mm² f*: max. 4mm² a*: max. 4mm² (d<2.8mm) | e*: max. 6mm² f*: max. 4mm² a*: max 4mm² (d<2.8mm) | e*: max. 1.5mm² f*: max. 1.5mm² a*: max. 1.5mm² (d<1.6mm) |
Connection cross section (AWG) | e*: AWG 20-10 f*: AWG 20-10 a* AWG 20-10 (d<2.8mm) | e*: AWG 20-10 f*: AWG 20-10 a* AWG 20-10 (d<2.8mm) | e*: AWG 24-16 f*: AWG 24-16 a*: AWG 24-16 (d<1.6mm) |
Strip length | 7mm / 0.28inch | 7mm / 0.28inch | 7mm / 0.28inch |
e* = solid single wire
f* = stranded wire
a* = with ferrule
Wiring instructions:
- Use suitable copper cables that are designed for at least the following operating temperatures: +60°C for ambient temperatures up to +45°C, +75°C for ambient temperatures up to +60°C, and +90°C for ambient temperatures up to +70°C.
- Observe the national installation rules and regulations!
- Make sure that all single wires of a strand are connected to the terminal!
- Unused terminals should be tightened firmly.
- Ferrules are permitted.
Series connection of power supply units:
Power supply units may be connected in series.
Series connection (looping from one power supply output to the next) is permitted as long as the average output current flowing through a connection pin does not exceed 25 A. For higher currents please use a separate distributor terminal strip as shown in Fig. Using distribution terminals.
