Environment
Environment | ||
|---|---|---|
Operating temperature 1) | -25°C to +70°C | Reduction of the output power according to Fig. Output current over ambient temperature |
Storage temperature | -40°C to +85°C | For storage and transport |
Output load reduction | 1.6W/°C 3W/°C | +45°C to +60°C / +60°C to +70°C |
0.33A/1000m or 5°C/1000m | For altitudes >2000m (6560ft), see Fig. Output current over installation altitude | |
The derating is not hardware-controlled. The user must take this into account in order to stay below the reduced current limits, so that device overload is avoided. | ||
Moisture | 5 to 95% r.h. | According to IEC 60068-2-30 Do not energize if there is condensation. |
Oscillation, sinusoidal 2) | 2–17.8Hz: ±1.6mm; 17.8-500Hz: 2g 2 hours/axis | According to IEC 60068-2-6 |
Impacts 2) | 30g 6ms, 20g 11ms 3 impacts / direction, 18 impacts in total | According to IEC 60068-2-27 |
Atmospheric pressure | 110-54kPa | see Fig. Output current over installation altitude |
Installation altitude | up to 5000m | see Fig. Output current over installation altitude |
Overvoltage category | III | According to IEC 60664 -1, installation altitudes up to 2000m |
II | According to IEC 60664 -1, installation altitudes above 2000m | |
Degree of pollution | 2 | According to IEC 62477-1, non-conductive |
LABS-free | The device does not release any silicones or other paint-wetting impairment substances and is suitable for use in paint shops. | |
Corrosive gas | Tested according to ISA-71.04-1985, Severity Level G3, IEC 60068-2-60 Test Ke Method 4 for a service life of at least 10 years in these environments. | |
Audible noises | In the event of no-load, overload or short circuit, the power supply unit emits audible noises. | |
1) The working temperature is identical to the room temperature or the ambient temperature and is defined as the air temperature 2cm below the device.
2) Tested in conjunction with DIN rails according to EN 60715 with a height of 15mm and a thickness of 1.3mm and standard mounting position.
Fig.15: Output current over ambient temperature; output current over installation altitude