Environment
Environment | ||
Operating temperature 1) | -10°C to +70°C | Reduction of the output power according to Fig. Output current over ambient temperature |
Storage temperature | -40°C to +85°C | For storage and transport |
Output load reduction | 0.1A/°C | Between +60°C and +70°C |
Load reduction due to installation altitude 3) | 0.25A/1000m or 5°C/1000m | Above 2000m, see Fig. Output current over installation altitude |
Moisture | 5 to 95% r.h. | According to IEC 60068-2-30 Do not energize if there is condensation. |
Atmospheric pressure | 110-54kPa | see Fig. Output current over installation altitude |
Installation altitude | 0 to 5000m | see Fig. Output current over installation altitude |
Overvoltage category | II | According to IEC 60664-1, for altitudes up to 5000m |
Surge voltage strength | 4kV (according to overvoltage category III) | Input to PE |
Degree of pollution | 2 | According to IEC 60664-1, non-conductive |
Oscillation, sinusoidal 2) | 2–17.8Hz: ±1.6mm; 17.8-500Hz: 2g 2 hours/axis | According to IEC 60068-2-6 |
Impacts2) | 30g 6ms, 20g 11ms 3 impacts/direction, 18 impacts in total | According to IEC 60068-2-27 |
1) The working temperature is identical to the room temperature or the ambient temperature and is defined as the air temperature 2cm below the device.
2) Tested in conjunction with DIN rails according to EN 60715 with a height of 15mm and a thickness of 1.3mm and standard mounting position.
3) The derating is not hardware-controlled. The user must take this into account in order to stay below the reduced current limits, so that device overload is avoided.
![Environment 1:](Images/png/9177846539__Web.png)