Output
The output provides an SELV/PELV/ES1 nominal voltage that is electrically isolated from the input voltage.
The output is electronically protected against overload, no-load and short circuit. In the event of a protection event, audible noises may occur.
The output is designed to supply any type of load, including capacitive and inductive loads. Capacitive loads should not exceed 2500µF with 2.5A or 5000µF with 1.25A additional current load.
In the event of severe overload (if the output voltage drops below 14V) the power supply delivers a continuous output current for 25ms. The output is then switched off for approx. 145ms before a new start attempt is automatically made. This cycle is repeated as long as the overload exists. The device starts operating normally again once the overload has been rectified.
Output voltage  | Nom.  | 24V  |
Adjustment range  | Min.  | 24-28V  | Guaranteed value  |
Max.  | 29.0V  | This is the maximum output voltage that can occur in the end position of the potentiometer in clockwise direction due to tolerances. It is not a guaranteed value that can be achieved.  | |
Factory settings  | typ.  | 24.1V  | ±0.2%, at full load (cold device)  |
Line regulation  | Max.  | 10mV  | Between 90 and 300Vac  |
Load regulation  | Max.  | 100mV  | Between 0 and 2.5A, static value, see Fig. Output voltage over output current, typ.  |
Residual ripple and ripple voltage  | Max.  | 100mVss  | Bandwidth 20 Hz to 20 MHz, 50 Ohm  |
Output current  | Nom.  | 2.5A  | At 24V and an ambient temperature below 60°C, see Fig. Output current over ambient temperature  |
Nom.  | 2.1A  | At 24V and 70°C ambient temperature, see Fig. Output voltage over output current, typ.  | |
Nom.  | 1.9A  | At 28V and an ambient temperature below 60°C, see Fig. Output current over ambient temperature  | |
Nom.  | 1.6A  | At 28V and 70°C ambient temperature, see Fig. Output voltage over output current, typ.  | |
Overload characteristics  |
  | Continuous current  | Output voltage > 14Vdc, see Fig. Output voltage over output current, typ.  |
  | Hiccup mode  | Output voltage < 14Vdc, see Fig. Output voltage over output current, typ.  | |
Overload/short circuit current  | Max.  | 4.0A  | Continuous current, see Fig. Short circuit at output, hiccup mode, typ.  |
typ.  | 6A  | Intermittent current peak value for typ. 25ms  | |
Max.  | 2.5A  | intermittent mean current value (rms.)   | |
Output capacity  | typ.  | 900μF  | Included in the power supply  |
Load feedback  | Max.  | 35V  | The device is resistant and does not show any malfunction when a load feeds back voltage to the power supply. It does not matter whether the power supply is switched on or off. The absorbed energy can be calculated by means of the built-in large-size output capacitor.  |