Protective functions and safety features
Protective functions  | ||
Output overvoltage protection  | Typ. 30.5 Vdc   | In the event of an internal power supply fault, a redundant circuit limits the maximum output voltage. In such a case the output switches off and automatically attempts to restart.  |
Protection class  | IP20  | EN/IEC 60529  |
Overtemperature protection  | Yes  | Output shutdown with automatic restart.  |
Protection against  | MOV (metal oxide varistor)  | For further information see EMC chapter  |
Input fuse  | Included  | Slow-blow fuse, not user-replaceable, with high braking power  |
Safety features  | ||
Insulation resistance  | Min. 500 MOhm  | In the delivery state between input and output,  |
Min. 500 MOhm  | In the delivery state between input and PE (Protective Earth),  | |
Min. 500 MOhm  | In the delivery state between output and PE,  | |
Min. 500 MOhm  | In the delivery state between output and DC-OK contacts,  | |
Protection class  | I  | According to IEC 61140  |
Touch current (leakage current)  | Typ. 0.33 mA / 0.69 mA  | At 230 Vac, 50 Hz, TN, TT / IT network  |
Max. 0.43 mA / 0.89 mA  | At 264 Vac, 50 Hz, TN, TT / IT network  | |