Protective functions and safety features
Protective functions | ||
Output overvoltage protection | Typ. 31 Vdc | In the event of an internal power supply fault, a redundant circuit limits the maximum output voltage. The output switches off in such a case. To attempt to restart, turn off the input power for at least 90 s. |
Protection class | IP20 | EN/IEC 60529 |
Overtemperature protection | No |
Protection against | MOV (metal oxide varistor) | For further information see EMC chapter |
Input fuse | included | Slow-blow fuse, not user-replaceable, with high braking power |
Safety features | ||
Insulation resistance | Min. 500 MOhm | In the delivery state between input and output, |
Min. 500 MOhm | In the delivery state between input and PE (Protective Earth), | |
Min. 500 MOhm | In the delivery state between output and PE, | |
Min. 500 MOhm | In the delivery state between output and DC-OK contacts, | |
Protection class | I | According to IEC 61140 |
Touch current (leakage current) | Typ. 0.30 mA / 0.75 mA | At 230 Vac, 50 Hz, TN, TT / IT network |
Max. 0.39 mA / 0.94 mA | At 264 Vac, 50 Hz, TN, TT / IT network | |