Protective functions and safety features
Output overvoltage protection
Typ. 31 Vdc
Max. 34 Vdc
In the event of an internal power supply fault, a redundant circuit limits the maximum output voltage. The output switches off in such a case. To attempt to restart, turn off the input power for at least 90 s.
Protection class
IP20
EN/IEC 60529
Overtemperature protection
No
Protection against
input transients
MOV (metal oxide varistor)
For further information see EMC chapter
Input fuse
included
Slow-blow fuse, not user-replaceable, with high braking power
Safety features
Insulation resistance
Min. 500 MOhm
In the delivery state between input and output,
measured with 500 Vdc
Min. 500 MOhm
In the delivery state between input and PE (Protective Earth),
Min. 500 MOhm
In the delivery state between output and PE,
Min. 500 MOhm
In the delivery state between output and DC-OK contacts,
Protection class
I
According to IEC 61140
PE (protective conductor) connection required
Touch current (leakage current)
Typ. 0.30 mA / 0.75 mA
At 230 Vac, 50 Hz, TN, TT / IT network
Max. 0.39 mA / 0.94 mA
At 264 Vac, 50 Hz, TN, TT / IT network