Peak current capability
The device can deliver peak currents (for up to several milliseconds) that are higher than the specified short-term currents.
This helps when starting loads with high current intensity. Magnetic coils, contactors and pneumatic modules often have a stationary coil and a pick-up coil. The input inrush current requirement of the pick-up coil is several times higher than the steady-state current and usually exceeds the rated output current. The situation is exactly the same when starting a capacitive load.
The peak current capability also ensures safe operation of downstream circuit breakers of load circuits. The load circuits are often individually fused with circuit breakers or fuses. In the event of a short circuit or overload in a circuit, the fuse or circuit breaker needs a certain amount of overcurrent to open in time. This prevents a voltage drop in adjacent circuits.
The additional current (peak current) is supplied by the power converter and the built-in large-size output capacitors of the power supply. The capacitors are discharged during such an event, which leads to a voltage drop at the output. The following two examples show typical voltage drops for ohmic loads:
Peak current capability 1:
10 A peak current (ohmic load) for 50 ms, the output voltage drops from 24 V to 17 V
Peak current capability 2:
25 A peak load (ohmic load) for 5 ms, the output voltage drops from 24 V to 9 V.
Peak current voltage drops
Typically from 24 V to 17 V
At 10 A for 50 ms, ohmic load
Typically from 24 V to 13 V
At 25 A for 2 ms, ohmic load
Typically from 24 V to 9 V
At 25 A for 5 ms, ohmic load