Parameters
Channel parameters
P-CHAN-00057
Setting the default measurement type
Parameter
messtyp
Seven different measurement types are available. The required measurement type can be set with this element.
Data type
UNS16
Data range
1: Measurement travel (G100) with at least one axis,
measurement feed rate programmable via F word
2: Measurement travel (G100) with exactly one axis;
measurement feed rate is specified in the ACHS_MDS list
3: Measurement travel (G100) with at least one axis,
optionally with continued travel up to destination point
4: Measurement travel (G100) only with the maximum of three main axes,
5: Interruptible measurement travel (G310) with at least one axis,
6: Interruptible measurement travel (G310) with at least one SERCOS axis,
7: Measurement travel by moving on a fixed stop with at least one axis,
Measurement feed programmable through F-Word.
Dimension
Translatory: -
Rotatory: -
Default
Remarks
The measurement type can be modified at any time in the NC program with #MEAS MODE.
Axis parameters
P-AXIS-00086
Measuring probe stroke
Parameter
kenngr.hub_messtaster
As the stroke of mechanical measuring sensors is limited, when the measuring sensor is actuated a check is made as to whether a delay via the ramps chosen in the axis parameter list is sufficient on the basis of the acceleration ramp and the current feed rate. Therefore, the P-AXIS-00086 parameter defines the maximum permitted deceleration distance for measurement.
Data type
UNS32
Data range
0<P-AXIS-00086 <MAX(UNS32)
Dimension
Translatory: 0.1 µm
Rotatory: 0.0001°
Default
Remarks
A buffer exists between the interpolator and the position controller to calculate the parameters for feed forward control of axes. This results in a dead time between calculation of a setpoint by the interpolator and its execution in the position controller. In the worst case, an error can be produced during measurement travel because the interpolator, which monitors the stroke of the measuring probe, ignores the distance components in the buffer. This can be prevented by enlarging the actual measuring probe stroke.
P-AXIS-00113
Measured signal edge
Parameter
kenngr.mess_neg_flanke
Definition of the edge of the measured signal where the counter performs the latching operation.
Data type
BOOLEAN
Data range
0: Latching if positive measured signal edge
1: Latching if negative measured signal edge
Dimension
Translatory: -
Rotatory: -
Default
Remarks
P-AXIS-00114
Measurement travel offset
Parameter
kenngr.mess_offset
The measurement travel offset P-AXIS-00114 specifies by which distance further than the destination position programmed in the measurement block the axis may travel if the measurement probe has not yet been actuated up to the programmed destination point. An error message is issued if a measurement signal can still not be recorded within the measurement offset.
Data type
UNS32
Data range
0<P-AXIS-00114 <MAX(UNS32)
Dimension
Translatory: 0.1µm
Rotatory: 0.0001°
Default
Remarks
This parameter is used only for measurement in accordance with measurement type 2.
P-AXIS-00115
Measured signal via axis-specific control bit pattern
Parameter
kenngr.mess_signal_achs_steuer
To make it possible to take external measured signals into account as well, one bit in the axis-specific control bit pattern is treated as the measured signal. This can be activated via P-AXIS-00115.
Data type
BOOLEAN
Data range
0: No evaluation of the measured signal via the axis-specific control bit pattern
1: Evaluation of the measured signal via the axis-specific control bit pattern
Dimension
Translatory: -
Rotatory: -
Default
Remarks
The following measurement methods are permitted depending on the drive type
Measurement method
P-AXIS-00117
(mess_signal_taster)
P-AXIS-00116
(mess_signal_sercos)
P-AXIS-00115
(mess_signal_achs_steuer)
Drive simulation
X
X
Conventional
drive interface
X
X
SERCOS drive interface
X
X
X
P-AXIS-00116
Measurement with SERCOS drives
Parameter
kenngr.mess_signal_sercos
With the aid of P-AXIS-00116, you define whether the measured signal is to read in via the SERCOS interface.
Data type
BOOLEAN
Data range
0: Read measured signal via control bit pattern and hardware interface
(see P-AXIS-00115 or P-AXIS-00117)
1: Read measured signal via the SERCOS interface
Dimension
Translatory: -
Rotatory: -
Default
Remarks
P-AXIS-00117
Measuring probe signal via hardware interface
Parameter
kenngr.mess_signal_taster
Use of the NC kernel's hardware interface is selected via P-AXIS-00117.
Data type
BOOLEAN
Data range
0: Do not read the measuring probe signal via the controller's hardware interface
1: Read the measuring probe signal via the controller's hardware interface
Dimension
Translatory: -
Rotatory: -
Default
Remarks
P-AXIS-00118
Measurement axis
Parameter
kenngr.messachse
P-AXIS-00118 defines whether an axis can be involved in measurement travel.
Data type
BOOLEAN
Data range
0: Axis cannot be used as measured axis
1: Axis can be used as measured axis
Dimension
Translatory: -
Rotatory: -
Default
Remarks
P-AXIS-00215
Feed rate for measurement in accordance with measurement type 2
Parameter
kenngr.vb_messen
For measurement type 2 P-AXIS-00215 is used as feed for the measurement movement.
Data type
UNS32
Data range
0<P-AXIS-00215 <MAX(UNS32)
Dimension
Translatory:
Rotatory: 0,001°/s
Default
Remarks
Only used for measurement type 2.
P-AXIS-00060
Number of used real time bits for SERCOS drives
Parameter
kenngr.echtzeit_bit_nr
With this parameter the assignment of the realtime status and control bits for SERCOS drives is done.
The assignment is according to the following table:
P-AXIS-00060
Controlbits
Statusbits
Measurement
Enable
Measurement
done
Measurement equipment
Actuated
0,
no entry
Realtime
control bit 1
P-AXIS-00106
Realtime
status bit 2
1
Realtime
control bit 1
Realtime
status bit 1
Realtime
status bit 2
2
Realtime
control bit 2
Realtime
statusbit 2
Realtime
statusbit 1
Data type
UNS08
Data range
0≤ P-AXIS-00060 ≤ 2
Dimension
Default
0
Remarks
It is recommended to use either 1 or 2 as value for P-AXIS-00060.
P-AXIS-00257
Measurement is done in the CNC
Parameter
kenngr.probing_signal_via_plc
Latching the measured value is done in the CNC, the probing signal is handed over to the CNC via the PLC interface.
Data type
BOOLEAN
Data range
0 : Use drive based measurement
1 : Use CNC based measurement.
Dimension
Translatory:
Rotatory: -
Default
0
Remarks
P-AXIS-00330
Measuring with movement on a fixed stop
Parameter
kenngr.meas_signal_fixed_stop
With this parameter the measurement signal source "Fixed stop" is enabled.
Data type
BOOLEAN
Data range
0: No measuring on a fixed stop possible
1: Enabling of measuring on a fixed stop
Dimension
Translatory: -
Rotatory: -
Default
Remarks
The user has to ensure, that during the movement on a fixed stop in the drives involved a torque limitation is active and that the velocity is low enough.
All other measurement signal sources (e.g. P-AXIS-00116 (kenngr.mess_signal _sercos)) have to be deselected.
P-AXIS-00331
Limit for position lag
Parameter
kenngr.fixed_stop_pos_lag_limit
This parameter specifies the limit for the position lag. After exceeding this limit the fixed stop is detected and the measuring position is taken over.
Data type
UNS32
Data range
0 < P-AXIS-00331 < MAX(UNS32)
Dimension
Translatory: 0,1 µm
Rotatory: 0,0001°/s
Default
Remarks
P-AXIS-00332
Number of position controller cycles
Parameter
kenngr.fixed_stop_nbr_cycles
This parameter defines the number of position control cycles for the waiting time after exceeding of the given position lag limit P-AXIS-00331, before the measurement value is determined. The counting is started again, if during this time the limit is fallen below.
Data type
UNS32
Data range
0 < P-AXIS-00332 < MAX(UNS32)
Dimension
Translatory: -
Rotatory: -
Default
Remarks