Technical data
Technical data | KM2774-0000 |
Number of power outputs | 4 x 3 make contacts |
Rated voltage of the power outputs | 80 ... 230 VAC |
Overvoltage protection at the power outputs | > 275 V |
Output current from the power outputs | 1.5 A (0.6 mA no-load current) |
Surge current | 40 A (16 ms), 3 A (30 s) |
Overcurrent limitation | Ajustable |
Switch-on time | 0.1 ... 10 ms, zero crossing |
Switch-off time | T/2 |
Residual voltage | maximum 1.5 V (60 mA ... 1 A), 150 Ω (< 60 mA) |
Number of digital outputs | 4 (1 per channel), ground switching |
Nominal voltage | 24 VDC |
Output current | maximum 20 mA, short-circuit proof |
Signal voltage "0" | -3 V ... 5 V |
Signal voltage "1" | -15 V ... 30 V |
Number of digital inputs | 12 (4 x 3) |
Nominal voltage | 24 VDC (-15 %/+20 %) |
Signal voltage "0" | -3 V ... 5 V (IEC 61132-2, type 1) |
Signal voltage "1" | -15 V ... 30 V (IEC 61132-2, type 1) |
Input filter | 3.0 ms |
Input current | typically 3 mA (IEC 61132-2, type 1) |
Power supply for the electronics | via the K-bus |
Current consumption via K-bus | typically 30 mA |
Electrical isolation | 500 V (K-bus/field voltage), 3750 VAC (1 minute) |
Bit width in the input process image | 24 bit |
Dimensions with terminals (W x H x D) | approx. 135 mm x 100 mm x 40 mm (width aligned: 132 mm), see dimensional drawing |
Weight | approx. 270 g |
Permissible ambient temperature range during operation | 0°C ... + 55°C |
Permissible ambient temperature range during storage | -25°C ... + 85°C |
Permissible relative air humidity | 95%, no condensation |
Permissible degree of pollution | 1 |
on a 35 mm mounting rail (e.g. DIN rail TH 35-7.5 conforming to EN 60715) | |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP20 |
Approvals / markings | CE |