Contact assignment
WARNING
Risk of injury through electric shock and damage to the device!
Bring the Bus Terminals system into a safe, de-energized state before starting mounting, disassembly or wiring of the Bus Terminals.
Contact assignment 1:Fig.10: KL6811 - Contact assignment
Contact assignment
Terminal point
No.
Connection for
DALI +
1
DALI/DSI control cable (internally connected to terminal point no. 4)
+24 V
2
Power contact +24 V
0 V
3
Power contact 0 V
DALI +
4
DALI/DSI control cable (internally connected to terminal point no. 1)
DALI -
5
DALI/DSI control cable (internally connected to terminal point no. 8)
+24 V
6
Power contact +24 V
0 V
7
Power contact 0 V
DALI -
8
DALI/DSI control cable (internally connected to terminal point no. 5)
Notice
No mains voltage at the power contacts
The terminal points for the power contacts (+24 V, 0 V) must not be connected to 230 V mains voltage under any circumstances, since this would destroy the KL6811.
Contact assignment 2:
Contacts for the DALI control cable (DALI+, DALI-) and mains voltage
If the contacts for the DALI control line (DALI+, DALI-) are accidentally connected to 230 V mains voltage, the KL6811 is not destroyed, but switches off.
Line lengths in DALI mode
The DALI bus can be configured in a line or star topology, or in a mix of the two. The maximum cable length must not exceed 300 m!
Cable length
Wire cross section
up to 100 m
minimum 0.5 mm2
up to 150 m
minimum 0.75 mm2
up to 300 m
minimum 1.5 mm2
Further important boundary conditions derived from IEC 62386: