Data exchange, function
Control Byte for process data exchange
The control byte is transmitted from the terminal to the controller. It can be used in register mode (REG = 1) or in process data exchange (REG = 0) (see note in the annex). For setting up data exchange (handshake), the control and the status byte are used in process data exchange.
MSB
REG=0 | OL2 | OL1 | OL0 | 0 | IR | RA | TR |
Status byte in process data mode
The status byte is transmitted from the terminal to the controller. It contains the data required for handshake.
MSB
REG=0 | IL2 | IL1 | IL0 | BUF_F | IA | RR | TA |
TR/TA: TRANSMIT-REQUEST/TRANSMIT-ACCEPTED bits
The handshake for data transmission is provided via this bit. A change of state in TR causes the data set defined via OL0-OL2 (5 bytes maximum) to be loaded into the transmission FIFO. The terminal signals execution of this instruction via TA.
Example
Output | Input | Comment |
00000000 | 0XXXX0X0 | Start data transmission |
00100001 | 0XXXX0X0 | The controller instructs the terminal to send 2 data |
00100001 | 0XXXX0X1 | The terminal has loaded 2 data into transmission FIFO; the command is executed |
01010000 | 0XXXX0X1 | The controller instructs the terminal to send 5 data (D0-D4) |
01010000 | 0XXXX0X0 | The terminal has loaded 5 data into transmission FIFO; the command is executed |
RA/RR: REICEIVE-ACCEPTED/RECEIVE-REQUEST
The terminal notifies the controller via a change of state in RR that the data quantity displayed in IL0-IL1 is located in D0-D4. The data shift is acknowledged in the control byte using RA; only then will new data be transmitted by the terminal to the controller.
Example:
00000000 | 0XXXX00X | Start data transmission |
0XXX000X | 0011X01X | The terminal instructs the controller to accept 3 data from D0-D2 |
0XXX001X | 0011X01X | The controller has accepted data |
0XXX001X | 0101X00X | The terminal instructs the controller to accept 5 data from D0-D4 |
0XXX000X | 0101X00X | The controller has accepted data |
IR/IA: INIT-REQUEST/INIT-ACCEPTED
If IR is high, the terminal initializes. The send and receive functions are blocked, the FIFO pointers are reset and the interface is initialized with the values from the relevant registers (R32-R35, R18). The completion of the initialization is acknowledged by the terminal using IA.
Example:
0XXXXXXX | 0XXXXXXX | Start data transmission |
00000100 | 0XXXXXXX | Initialization is requested by the controller |
00000100 | 00000100 | The terminal has completed the initialization |
00000000 | 00000100 | The controller requests data exchange |
00000000 | 00000000 | The terminal is ready |
BUF_F: BUFFER-FULL_Flag
The receive FIFO is full. Data received now will be lost.
Error handling
If a parity, framing or overrun error occurs, the corresponding data is lost in transmission and will not be loaded into the receive FIFO of the terminal.
If the buffer is full, incoming data will be ignored.
In the event of an error, the corresponding diagnostic bits are set to R6