Contact assignment
WARNINGBring the bus terminal system into a safe, powered down state before starting installation, disassembly or wiring of the Bus Terminals!
Terminal point | No. | Comment |
V | 1 | Terminal point for voltage measurement (internally connected with terminal point 5) |
COM | 2 | Ground (internally connected with terminal point 6) |
10 A | 3 | Terminal point for current measurement, 10 A range |
Shield | 4 | Shield (internally connected with terminal point 8) |
V | 5 | Terminal point for voltage measurement (internally connected with terminal point 1) |
COM | 6 | Ground (internally connected with terminal point 2) |
1 A | 7 | Terminal point for current measurement, 1 A range |
Shield | 8 | Shield (internally connected with terminal point 4) |
WARNINGFor voltages greater than 25 VAC (42 V peak) or 60 VDC the fuse opening must be covered by an additional terminal or the EL9011 end terminal. Risk of electric shock!
The current branch for 10 A is not fuse-protected. The device may be damaged if the current in the 10 A branch exceeds 10 A.