Output format
If only manufacturer scaling via the feature register is active, the output format is as follows:
- 1 digit corresponds to 1/10 °C or
- 1 digit corresponds to 1/10 Ω
If no scaling is active, the output format is as follows:
- 1 digit corresponds to 1/16 °C or
- 1 digit corresponds to 1/16 Ω
If the Siemens output format is selected, the lowest three bits are used for status evaluation. The process data is represented in bits 3 to 15, with bit 15 representing the sign bit. Scaling of the measurement reading according to the Siemens standard has to be done via user scaling.
Bit Measured value |
Bits 15-3 |
Bit 2 |
Bit 1 |
Bit 0 |
out of range |
0 |
0 |
1 |
in range |
Process data |
0 |
0 |
0 |
• R33: User scaling - offset (B_w)
16 bit signed integer
This register contains the offset of the user straight-line equation (1.6). The straight-line equation is activated via register R32.
• R34: User scaling (A_w)
16 bits signed integer* 2-8.
This register contains the scaling factor of the user straight-line equation (1.6). The straight-line equation is activated via register R32.
• R35 and R36: reserved
• R37: Filter constant
[0x0000]
Filter constants: |
First notch [Hz] |
Conversion time [ms] |
0x0000 |
25 |
250 |
0x50 |
100 |
65 |
0xA0 |
50 |
125 |
0x140 |
25 |
250 |
0x280 |
12.5 |
500 |
![]() | • Validity of the documentation This documentation applies to all terminals from firmware version 3x. The version number can be found within the serial number on the right-hand side face of the terminal: xxxx3xxx |