Technical data
Technical data | KL2602 / KS2602 | KL2622 / KS2622 |
Number of outputs | 2 make contacts for power contact | 2 make contacts (potential-free) |
Contact material | AgCdO | |
Switching voltage | max. 250 VAC / 30 VDC | |
Switching current | maximum 5 A | |
Maximum switching capacity | Alternating voltage: 5 A 250 VAC 1250 VA | |
Max. switching current | 2 A, 250 VAC | |
Minimum permitted load (guide value) | 10 mA at 5 VDC (in delivery state) 100 mA at 5 VDC (after a current of approx. 100 mA (or higher) has been switched once) | |
Response times with nominal load | Response time: max. 10 ms | |
Electrical isolation | 500 V (K-bus / mains voltage) | |
K-Bus current consumption | 80 mA | 85 mA |
Bit width in process image | 2 outputs | |
Service life – mechanical switching cycles | 20,000,000 switching operations | |
Service life – electrical switching cycles | at least 100,000 switching operations of an ohmic load at 250 VAC, 5 A or 30 VDC, 5 A | |
Permitted switching frequency at maximum contact load | 10 switching operations / minute | |
Contact resistance (new) max. | < 30 mΩ | |
Insulation resistance | 100 MΩ at 500 VDC | |
Test voltage between open contacts | at least 750 V (1 minute between open contacts) | |
Configuration | No address or configuration settings | |
Pluggable wiring | for all KSxxxx terminals | |
Weight | approx. 85 g | approx. 80 g |
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |
on 35 mm mounting rail according to EN 60715 | ||
Permissible ambient temperature range during operation | -25 °C ... +60 °C | |
Permissible ambient temperature range during storage | -40 °C ... +85 °C | |
Relative humidity | 95% no condensation | |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Installation position | variable | |
Protection class | IP20 | |
Approvals / markings* | CE, UKCA, cULus, EAC, DNV | |
Technical data | KL2602-0010 / KS2602-0010 | KL2622-0010 / KS2622-0010 |
Number of outputs | 2 make contacts for power contact | 2 make contacts |
Contact material | Silver alloy (stationary contact gold-plated) | |
Rated load voltage | 230 VAC/30 VDC | |
Load type | ohmic, inductive, capacitive | |
Switching current max. | typ. 5 AAC/DC per channel | |
Inductive switching current | typ. 2 AAC/DC per channel | |
Minimum permitted load | typ. 0.1 mA at 0.1 VDC | |
Electrical isolation | 500 V (K-bus / field voltage) | |
Response time with nominal load | Max. 20 ms (= 10 ms zero voltage delay at 50 Hz + 10 ms delay time of the relay) | |
Switching cycles mech. (min.) | 2 x 107 (at 18 x 103 switching cycles per hour) | |
Switching cycles electr. (min.) | 100,000 (3 A at 250 VAC, 3 A at 30 VDC and ohmic load) | |
Special features | switches at the zero voltage crossing to protect the contacts | |
Contact resistance (max.) | typ. 100 mΩ | |
Insulation | typ. 1000 MΩ at 500 VDC | |
Weight | approx. 50 g | |
on 35 mm mounting rail conforms to EN 60715 | ||
Permissible ambient temperature range during operation | 0 °C ... +55 °C | |
Permissible ambient temperature range during storage | -25 °C ... +85 °C | |
Approvals / markings* | CE, UKCA, cULus, EAC | |