Chopper operation
Instead of a DC motor, you can connect a brake resistor (chopper) to a channel of the KL2532/KL2552 and activate brake resistor mode for this channel (see KS2000 or registers R33.0 - R33.3).
The motor must actively brake for positioning tasks. The mechanical energy is thereby converted back into electrical energy. Small amounts of energy can be absorbed by a capacitor in the KL2532/KL2552. Further storage capacities, for example in the power supply, can also take up energy. The feedback leads in each case to a voltage increase.
In order to avoid overvoltage, a brake resistor can be connected to the KL2532/KL2552 in order to dissipate the excess energy in the form of heat. When the voltage reaches 110% of the rated voltage (register R36 , e.g. 55 V for KL2552), the correctly set output stage sends a fast-pulsed current through the brake resistor (see diagram).
Chopper operation 1:
Current through the brake resistor
UCH /UN
20%
40%
60%
80%
100%
110%
130%
160%
UCH at UN = 50 V
10 V
20 V
30 V
40 V
50 V
55 V
65 V
80 V
UCH at UN = 24 V
4,8 V
9,6 V
14,4 V
19,2 V
24 V
25,2 V
31,2 V
38,4 V
Note
Dimensioning of the brake resistor
The brake resistor should be dimensioned such that it can withstand the expected heat development without damage!
A brake resistance of 10 Ω is recommended for KL2552, which results in a pulse current of approx. 5.5 A to 6.5 A. The maximum expected continuous power is 125 W. However, the value typically lies significantly below that.
Load estimation (for KL2552)
PN = IN² x R
PN = (5A)² x 10 Ω
PN = 250 W
A maximum duty cycle of 50 % is possible. This results in a maximum continuous power of 125 W.
A motor efficiency of 80 % is usual in practice.
The motor thus converts 80 % of the rated electrical power into kinetic energy when accelerating.
Conversely, when braking, the motor (as a generator) converts 80 % of the kinetic energy into electrical power.
This results in a practical brake power of:
PCH = PN/2 x 80/100 x 80/100
PCH = 125W x 80/100 x 80/100
PCH = 80 W