Contact assignment and LED displays
WARNING | |
Risk of injury through electric shock and damage to the device! Bring the Bus Terminals system into a safe, de-energized state before starting mounting, disassembly or wiring of the Bus Terminals! |
KL2521-xxxx - Contact assignment
Terminal point | No. | Comment |
+A | 1 | Output +A |
+B | 2 | Output +B |
+T | 3 | Input T (KL2521-0010: Output T) |
GND T, Z | 4 | Signal ground for the outputs |
-A | 5 | Output -A |
-B | 6 | Output -B |
+Z | 7 | Input Z (KL2521-0010: Output Z) |
Shield | 8 | Shield |
KL2521-xxxx - LED displays
LED | Color | Description |
Signal LED A, B | green | The four LEDs light up with active signal levels of the inputs and outputs. The illumination of the LEDs for the active frequency outputs A or B at higher frequencies can only be perceived as a glow at half brightness. When the watchdog is active (Feature.2 = 0!!!) the terminal will switch the outputs off or will output a value stored in register 35 if no new process data is transferred to the terminal within 100 ms. |
Connecting the inputs (KL2521-0000, KL2521-0024)
The optically isolated inputs are protected from overload by a current limiter. Without further external circuitry the operating voltage may lies between 5 V and 24 VDC. The GND connection is the common ground for the two inputs, T and Z. The circuit diagram shows the internal circuitry of the two inputs:
Connection of the outputs
Circuit examples for output to A. The same principles apply to output B.
KL2521-0000, KL2521-0010
The outputs A and B of the EL2521 can be used in different connection modes. An integrated DC/DC converter supplies the output stage of the two channels, A and B, with an electrically isolated 5 V power supply.
- Connection to RS485/RS232 receiver
The output can be operated as RS485 or as RS232 output. The circuit generates the necessary differential signals.
- Connection to optocoupler (without external supply voltage)
The outputs can be used for direct connection of an optocoupler. The output stage supplies the necessary output current using an internal 5 V supply voltage.
Connection to optocoupler (with external supply voltage)
For connection to inputs with a large input resistance, an external supply voltage (up to 24 V) can be used with the EL2521-0024 in order to create the necessary current.
Operation with an external supply voltage is dependent on the hardware version The operation with an external supply voltage depends on the hardware version of the terminal:
- KL2521-0000 up to hardware version 03
- Instead of hardware version 04 (or higher), use the special variant KL2521-0024
See chapter Documentation issue status for the determination of the hardware version
KL2521-0024: Connection to external electronics
Note when connecting external electronics that terminal point A of the first channel and terminal point B of the second channel of a KL2521-0024 are connected to each other internally.
This allows the dual-channel connection of external electronics if the KL2521-0024 switches the ground of the connected device as shown in example 1.
Notes on connection to external electronics
KL2521-0010 Connection of additional outputs T, Z
The outputs are realized by MOSFET switches and can switch AC and DC voltages up to 230 V. The maximum current is 100 mA. DC voltages can be switched positive and negative.