Technical data
Technical Data | KL2521, KL2521-0015 | KL2521-0010 | KL2521-0024, | |
Number of outputs | 1 channel (2 differential outputs A, B) | |||
Load type** | Ohmic, optocoupler, differential inputs | |||
Rated load voltage** | 5 VDC internal | 5 VDC - 24 VDC, external supply | ||
Max. output current | 50 mA, RS485 specification | max. 0.5 A | ||
Base frequency | 100 Hz ... 500 kHz, default: 50 kHz | |||
Duty factor | 50 % | |||
Resolution | 16 bits over one word in the fieldbus, 24 bits usable altogether | |||
Ramp calculation | 2 ms / step | |||
Output cycle time | 1 ms (synchronous to K-bus) | |||
Dead time | 0.6 ms after K-bus cycle | |||
Number of inputs | 2 (+T, +Z) | - | 2 (+T, +Z) | |
Input current | 2.3 mA to 2.8 mA at 5 V to 30 V | |||
Electrical isolation | 500 V (K-bus/field voltage output / input) | |||
Current consumption from the K-bus | typ. 50 mA, max. 120 mA (load-dependent) | |||
Input process image | 24 bits (16 bits input data, 8 bits status) | |||
Output process image | 24 bits (16 bits output data, 8 bits control) | |||
Weight | approx. 50 g | |||
Permissible ambient temperature range during operation | 0°C ... + 55°C | |||
Permissible ambient temperature range during storage | -25°C ... + 85°C | |||
Permissible relative humidity | 95%, no condensation | |||
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |||
on 35 mm mounting rail conforms to EN 60715 | ||||
Enhanced mechanical load capacity | yes, see installation instructions for terminals with enhanced mechanical load capacity | |||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |||
EMC immunity / emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |||
Protection class | IP20 | |||
Installation position | variable | |||
Approvals/markings* | CE, UKCA, cULus, EAC, | CE, UKCA, EAC | CE, UKCA, cULus. EAC | |
**) dependent on the hardware version of the terminal, see chapter Connection of the outputs
Ex marking
Standard | Marking |
ATEX | II 3 G Ex nA IIC T4 Gc |