Overview implemented RTD transformations
Some Beckhoff IO devices (IP20 terminals, plug-in modules, box‑modules) support the evaluation of resistance sensors for temperature measurement (RTD) as Pt100, Pt1000, NTC1K etc.
The following are the characteristic curves partially implemented there depending on the device. The table values given are the basis for the evaluation in the device.
- Pt, Ni, KTY: the table values are stored in the device accordingly; intermediate values are interpolated. For KL terminals the temperature is calculated deviating from this via an approximation polynomial.
- NTC: the table values were used for determination of the Steinhart-Hart coefficients and by these coefficients the terminal determines the temperature.
Version 2026-02
Pt-RTD
Values in Ω | Pt100 | Pt1000 | Pt500 | Pt200 |
[°C] (ITS-90) | -200…+850°C | -200…+850°C | -200…+850°C | -200…+850°C |
-200 | 18.520 | 185.200 | 92.600 | 37.040 |
-190 | 22.825 | 228.250 | 114.125 | 45.650 |
-180 | 27.096 | 270.960 | 135.480 | 54.192 |
-170 | 31.335 | 313.350 | 156.675 | 62.670 |
-160 | 35.543 | 355.430 | 177.715 | 71.086 |
-150 | 39.723 | 397.230 | 198.615 | 79.446 |
-140 | 43.876 | 438.760 | 219.380 | 87.752 |
-130 | 48.005 | 480.050 | 240.025 | 96.010 |
-120 | 52.110 | 521.100 | 260.550 | 104.220 |
-110 | 56.193 | 561.930 | 280.965 | 112.386 |
-100 | 60.256 | 602.560 | 301.280 | 120.512 |
-90 | 64.300 | 643.000 | 321.500 | 128.600 |
-80 | 68.325 | 683.250 | 341.625 | 136.650 |
-70 | 72.335 | 723.350 | 361.675 | 144.670 |
-60 | 76.328 | 763.280 | 381.640 | 152.656 |
-50 | 80.306 | 803.060 | 401.530 | 160.612 |
-40 | 84.271 | 842.710 | 421.355 | 168.542 |
-30 | 88.222 | 882.220 | 441.110 | 176.444 |
-20 | 92.160 | 921.600 | 460.800 | 184.320 |
-10 | 96.086 | 960.860 | 480.430 | 192.172 |
0 | 100.000 | 1,000.000 | 500.000 | 200.000 |
10 | 103.903 | 1,039.030 | 519.515 | 207.806 |
20 | 107.794 | 1,077.940 | 538.970 | 215.588 |
30 | 111.673 | 1,116.730 | 558.365 | 223.346 |
40 | 115.541 | 1,155.410 | 577.705 | 231.082 |
50 | 119.397 | 1,193.970 | 596.985 | 238.794 |
60 | 123.242 | 1,232.420 | 616.210 | 246.484 |
70 | 127.075 | 1,270.750 | 635.375 | 254.150 |
80 | 130.897 | 1,308.970 | 654.485 | 261.794 |
90 | 134.707 | 1,347.070 | 673.535 | 269.414 |
100 | 138.506 | 1,385.060 | 692.530 | 277.012 |
110 | 142.293 | 1,422.930 | 711.465 | 284.586 |
120 | 146.068 | 1,460.680 | 730.340 | 292.136 |
130 | 149.832 | 1,498.320 | 749.160 | 299.664 |
140 | 153.584 | 1,535.840 | 767.920 | 307.168 |
150 | 157.325 | 1,573.250 | 786.625 | 314.650 |
160 | 161.054 | 1,610.540 | 805.270 | 322.108 |
170 | 164.772 | 1,647.720 | 823.860 | 329.544 |
180 | 168.478 | 1,684.780 | 842.390 | 336.956 |
190 | 172.173 | 1,721.730 | 860.865 | 344.346 |
200 | 175.856 | 1,758.560 | 879.280 | 351.712 |
210 | 179.528 | 1,795.280 | 897.640 | 359.056 |
220 | 183.188 | 1,831.880 | 915.940 | 366.376 |
230 | 186.836 | 1,868.360 | 934.180 | 373.672 |
240 | 190.473 | 1,904.730 | 952.365 | 380.946 |
250 | 194.098 | 1,940.980 | 970.490 | 388.196 |
260 | 197.712 | 1,977.120 | 988.560 | 395.424 |
270 | 201.314 | 2,013.140 | 1,006.570 | 402.628 |
280 | 204.905 | 2,049.050 | 1,024.525 | 409.810 |
290 | 208.484 | 2,084.840 | 1,042.420 | 416.968 |
300 | 212.052 | 2,120.520 | 1,060.260 | 424.104 |
Pt-RTD (continuation)
310 | 215.608 | 2,156.080 | 1,078.040 | 431.216 |
320 | 219.152 | 2,191.520 | 1,095.760 | 438.304 |
330 | 222.685 | 2,226.850 | 1,113.425 | 445.370 |
340 | 226.206 | 2,262.060 | 1,131.030 | 452.412 |
350 | 229.716 | 2,297.160 | 1,148.580 | 459.432 |
360 | 233.214 | 2,332.140 | 1,166.070 | 466.428 |
370 | 236.701 | 2,367.010 | 1,183.505 | 473.402 |
380 | 240.176 | 2,401.760 | 1,200.880 | 480.352 |
390 | 243.640 | 2,436.400 | 1,218.200 | 487.280 |
400 | 247.092 | 2,470.920 | 1,235.460 | 494.184 |
410 | 250.533 | 2,505.330 | 1,252.665 | 501.066 |
420 | 253.962 | 2,539.620 | 1,269.810 | 507.924 |
430 | 257.379 | 2,573.790 | 1,286.895 | 514.758 |
440 | 260.785 | 2,607.850 | 1,303.925 | 521.570 |
450 | 264.179 | 2,641.790 | 1,320.895 | 528.358 |
460 | 267.562 | 2,675.620 | 1,337.810 | 535.124 |
470 | 270.933 | 2,709.330 | 1,354.665 | 541.866 |
480 | 274.293 | 2,742.930 | 1,371.465 | 548.586 |
490 | 277.641 | 2,776.410 | 1,388.205 | 555.282 |
500 | 280.978 | 2,809.780 | 1,404.890 | 561.956 |
510 | 284.303 | 2,843.030 | 1,421.515 | 568.606 |
520 | 287.616 | 2,876.160 | 1,438.080 | 575.232 |
530 | 290.918 | 2,909.180 | 1,454.590 | 581.836 |
540 | 294.208 | 2,942.080 | 1,471.040 | 588.416 |
550 | 297.487 | 2,974.870 | 1,487.435 | 594.974 |
560 | 300.754 | 3,007.540 | 1,503.770 | 601.508 |
570 | 304.010 | 3,040.100 | 1,520.050 | 608.020 |
580 | 307.254 | 3,072.540 | 1,536.270 | 614.508 |
590 | 310.487 | 3,104.870 | 1,552.435 | 620.974 |
600 | 313.708 | 3,137.080 | 1,568.540 | 627.416 |
610 | 316.918 | 3,169.180 | 1,584.590 | 633.836 |
620 | 320.116 | 3,201.160 | 1,600.580 | 640.232 |
630 | 323.302 | 3,233.020 | 1,616.510 | 646.604 |
640 | 326.477 | 3,264.770 | 1,632.385 | 652.954 |
650 | 329.640 | 3,296.400 | 1,648.200 | 659.280 |
660 | 332.792 | 3,327.920 | 1,663.960 | 665.584 |
670 | 335.932 | 3,359.320 | 1,679.660 | 671.864 |
680 | 339.061 | 3,390.610 | 1,695.305 | 678.122 |
690 | 342.178 | 3,421.780 | 1,710.890 | 684.356 |
700 | 345.284 | 3,452.840 | 1,726.420 | 690.568 |
710 | 348.378 | 3,483.780 | 1,741.890 | 696.756 |
720 | 351.460 | 3,514.600 | 1,757.300 | 702.920 |
730 | 354.531 | 3,545.310 | 1,772.655 | 709.062 |
740 | 357.590 | 3,575.900 | 1,787.950 | 715.180 |
750 | 360.638 | 3,606.380 | 1,803.190 | 721.276 |
760 | 363.674 | 3,636.740 | 1,818.370 | 727.348 |
770 | 366.699 | 3,666.990 | 1,833.495 | 733.398 |
780 | 369.712 | 3,697.120 | 1,848.560 | 739.424 |
790 | 372.714 | 3,727.140 | 1,863.570 | 745.428 |
800 | 375.704 | 3,757.040 | 1,878.520 | 751.408 |
810 | 378.683 | 3,786.830 | 1,893.415 | 757.366 |
820 | 381.650 | 3,816.500 | 1,908.250 | 763.300 |
830 | 384.605 | 3,846.050 | 1,923.025 | 769.210 |
840 | 387.549 | 3,875.490 | 1,937.745 | 775.098 |
850 | 390.481 | 3,904.810 | 1,952.405 | 780.962 |
Ni-RTD
Values in Ω | Ni100 | Ni120 | Ni1000 | Ni1000 TK5000 |
α according to DIN43760 | typ. 6180 pmm/K | typ. 6720 pmm/K | typ. 6180 pmm/K | typ. 5000 pmm/K |
[°C] (ITS-90) | -60..50°C | -60..320°C | -60..250°C | -30..160°C |
-60 | 69.52 | 80.943 | 695.200 |
-50 | 74.255 | 87.011 | 742.550 |
-40 | 79.131 | 93.251 | 791.310 |
-30 | 84.146 | 99.667 | 841.460 | 871.690 |
-20 | 89.296 | 106.261 | 892.960 | 913.480 |
-10 | 94.582 | 113.038 | 945.820 | 956.240 |
0 | 100 | 120.000 | 1,000.000 | 1,000.000 |
10 | 105.552 | 127.151 | 1,055.520 | 1,044.790 |
20 | 111.236 | 134.494 | 1,112.360 | 1,090.650 |
30 | 117.056 | 142.033 | 1,170.560 | 1,137.620 |
40 | 123.011 | 149.772 | 1,230.110 | 1,185.710 |
50 | 129.105 | 157.712 | 1,291.050 | 1,234.950 |
60 | 135.34 | 165.859 | 1,353.400 | 1,285.450 |
70 | 141.721 | 174.214 | 1,417.210 | 1,337.150 |
80 | 148.25 | 182.783 | 1,482.500 | 1,390.120 |
90 | 154.934 | 191.567 | 1,549.340 | 1,444.390 |
100 | 161.779 | 200.572 | 1,617.790 | 1,500.000 |
110 | 168.789 | 209.798 | 1,687.890 | 1,556.980 |
120 | 175.972 | 219.251 | 1,759.720 | 1,615.370 |
130 | 183.335 | 228.934 | 1,833.350 | 1,675.190 |
140 | 190.887 | 238.850 | 1,908.870 | 1,736.470 |
150 | 198.635 | 249.002 | 1,986.350 | 1,799.270 |
160 | 206.589 | 259.394 | 2,065.890 | 1,863.600 |
170 | 214.758 | 270.029 | 2,147.580 |
180 | 223.153 | 280.911 | 2,231.530 |
190 | 231.783 | 292.042 | 2,317.830 |
200 | 240.66 | 303.427 | 2,406.600 |
210 | 249.795 | 315.069 | 2,497.950 |
220 | 259.2 | 326.971 | 2,592.000 |
230 | 268.887 | 339.136 | 2,688.870 |
240 | 278.868 | 351.569 | 2,788.680 |
250 | 289.156 | 364.271 | 2,891.560 |
260 |
| 377.247 |
270 |
| 390.501 |
280 |
| 404.035 |
290 |
| 417.853 |
300 |
| 431.958 |
310 |
| 446.354 |
320 |
| 461.044 |
KT/KTY-RTD
Values in Ω | KT100.. | KTY81/82-110… | KTY81-121 | KTY81-122 | KTY81-151 | KTY81-152 |
[°C] (ITS-90) | -50..150°C | -50..150°C | -50..150°C | -50..150°C | -50..150°C | -50..150°C |
-50 | 518 | 515 | 510 | 520 | 502 | 528 |
-40 | 570 | 567 | 562 | 573 | 553 | 582 |
-30 | 625 | 624 | 617 | 630 | 608 | 639 |
-20 | 685 | 684 | 677 | 690 | 667 | 701 |
-10 | 748 | 747 | 740 | 755 | 729 | 766 |
0 | 815 | 815 | 807 | 823 | 794 | 835 |
10 | 886 | 886 | 877 | 895 | 864 | 908 |
20 | 961 | 961 | 951 | 971 | 937 | 985 |
30 | 1,040 | 1,040 | 1,029 | 1,050 | 1,014 | 1,066 |
40 | 1,123 | 1,122 | 1,111 | 1,134 | 1,094 | 1,150 |
50 | 1,209 | 1,209 | 1,196 | 1,221 | 1,178 | 1,239 |
60 | 1,300 | 1,299 | 1,286 | 1,312 | 1,266 | 1,331 |
70 | 1,394 | 1,392 | 1,378 | 1,406 | 1,357 | 1,427 |
80 | 1,492 | 1,490 | 1,475 | 1,505 | 1,453 | 1,527 |
90 | 1,594 | 1,591 | 1,575 | 1,607 | 1,551 | 1,631 |
100 | 1,700 | 1,696 | 1,679 | 1,713 | 1,654 | 1,738 |
110 | 1,810 | 1,805 | 1,786 | 1,823 | 1,759 | 1,850 |
120 | 1,923 | 1,915 | 1,896 | 1,934 | 1,867 | 1,963 |
130 | 2,041 | 2,023 | 2,003 | 2,044 | 1,973 | 2,074 |
140 | 2,128 | 2,124 | 2,103 | 2,146 | 2,071 | 2,178 |
150 | 2,235 | 2,211 | 2,189 | 2,233 | 2,156 | 2,266 |
NTC-RTD
Values in Ω | NTC 1k8 | NTC 1k8 | NTC 2k2 | NTC 3k | NTC 5k | NTC 10k | NTC 10k | NTC 10k |
R0 | R0=4940 | R0=5200 | R0=7373 | R0=9822 | R0=16325 | R0=27280 | R0=29490 | R0=29588 |
C1 1) | 1.25835E-03 | 1.09447E-03 | 1.46042E-03 | 1.39183E-03 | 1.28772E-03 | 9.01568E-04 | 1.02381E-03 | 1.00996E-03 |
C2 1) | 2.69483E-04 | 3.06398E-04 | 2.39847E-04 | 2.39480E-04 | 2.35694E-04 | 2.49334E-04 | 2.39960E-04 | 2.42461E-04 |
C3 1) | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 |
C4 1) | 1.79850E-07 | -8.80292E-08 | 9.14512E-08 | 8.72452E-08 | 9.52328E-08 | 1.99664E-07 | 1.53713E-07 | 1.41928E-07 |
[°C] (ITS-90) | -40..130°C | -30..150°C | -50..130°C | -30..80°C | -40..100°C | -40..110°C | -30..150°C | -50..130°C |
-50 |
| 154,464 | 205,800 | 333,914 | 329,200 | 441,300 | 454,910 |
-40 | 35,480 |
| 77,081 | 102,690 | 167,835.5 | 188,400 | 239,800 | 245,089 |
-30 | 20,659 | 24,500 | 40,330 | 53,730 | 88,341.5 | 111,300 | 135,200 | 137,307 |
-20 | 12,443 | 14,000 | 22,032 | 29,346 | 48,487 | 67,740 | 78,910 | 79,729 |
-10 | 7,730 | 8,400 | 12,519 | 16,674 | 27,649 | 42,250 | 47,540 | 47,843 |
0 | 4,940 | 5,200 | 7,373 | 9,822 | 16,325.4 | 27,280 | 29,490 | 29,588 |
10 | 3,241 | 3,330 | 4,487 | 5,976 | 9,951.75 | 17,960 | 18,790 | 18,813 |
20 | 2,177 | 2,200 | 2,814 | 3,750 | 6,246.85 | 12,090 | 12,260 | 12,272 |
25 | 1,800 | 1,800 | 2,252 | 3,000 | 5,000 | 10,000 | 10,000 | 10,000 |
30 | 1,496 | 1,480 | 1,814 | 2,417 | 4,028 | 8,310 | 8,190 | 8,195 |
40 | 1,049 | 1,040 | 1,199 | 1,598 | 2,662.45 | 5,820 | 5,590 | 5,593 |
50 | 750 | 740 | 811.5 | 1,081 | 1,800.5 | 4,160 | 3,890 | 3,894 |
60 | 545 | 540 | 561 | 747 | 1,243.55 | 3,020 | 2,760 | 2,763 |
70 | 403 | 402 | 395.5 | 527 | 875.8 | 2,220 | 1,990 | 1,994 |
80 | 303 | 306 | 284 | 378 | 628.09 | 1,660 | 1,460 | 1,462 |
90 | 230 | 240 | 207.4 |
| 458.06 | 1,260 | 1,080 | 1,088 |
100 | 178 | 187 | 153.8 |
| 339.32 | 970 | 820 | 821 |
110 | 139 | 149 | 115.8 |
| 255.03 | 750 | 620 | 628 |
120 | 110 | 118 | 88.3 |
| 194.3 |
| 480 | 486 |
130 | 87 | 95 | 68.3 |
| 149.91 |
| 380 | 380 |
140 | 71 | 77 |
| 117.04 |
| 300 |
150 |
| 64 |
| 92.4 |
| 240 |
1) Coefficient for the Steinhart-Hart equation
NTC-RTD (continuation)
Values in Ω | NTC 10k | NTC 10k | NTC 10k | NTC 10K | NTC 20K | NTC 100k | NTC 100k |
R0 | R0=32639 | R0=32650 | R0=32660 | R0=32770 | R0=70200 | R0=326600 | R0=327240 |
C1 1) | 1.13048E-03 | 1.12119E-03 | 1.12715E-03 | 1.11312E-03 | 1.15399E-03 | 6.09783E-04 | 9.04083E-04 |
C2 1) | 2.33905E-04 | 2.35346E-04 | 2.34458E-04 | 2.36910E-04 | 2.12816E-04 | 2.29282E-04 | 1.53712E-04 |
C3 1) | 0 | 0 | 0 | 0 | 0 | 0 | 6.30765E-06 |
C4 1) | 8.86105E-08 | 8.34620E-08 | 8.63055E-08 | 7.53186E-08 | 9.51018E-08 | 6.84669E-08 | -1.02569E-07 |
[°C] (ITS-90) | -40..130°C | -30..150°C | -50..130°C | -50..130°C | -20..150°C | -40..130°C | -30..270°C |
-50 |
| 667,830 | 672,300 | 692,700 | 1,667,570 |
-40 | 333,562 | 335,670 | 337,200 | 344,700 | 813,440 | 3,366,000 |
-30 | 176,081 | 176,680 | 177,200 | 180,100 | 415,480 | 1,770,000 | 1,733,200 |
-20 | 96,807 | 96,970 | 97,130 | 98,320 | 221,300 | 971,200 | 959,050 |
-10 | 55,252 | 55,300 | 55,340 | 55,790 | 122,470 | 553,400 | 551,410 |
0 | 32,639 | 32,650 | 32,660 | 32,770 | 70,200 | 326,600 | 327,240 |
10 | 19,901 | 19,900 | 19,900 | 19,930 | 41,560 | 199,000 | 199,990 |
20 | 12,493 | 12,490 | 12,490 | 12,500 | 25,350 | 124,900 | 125,245 |
25 | 10,000 | 10,000 | 10,000 | 10,000 | 20,000 | 100,000 | 100,000 |
30 | 8,055 | 8,060 | 8,056 | 8,055 | 15,890 | 80,580 | 81,000 |
40 | 5,324 | 5,320 | 5,326 | 5,323 | 10,210 | 53,260 | 53,500 |
50 | 3,600 | 3,600 | 3,602 | 3,599 | 6,720 | 36,020 | 35,899 |
60 | 2,486 | 2,490 | 2,489 | 2,486 | 4,520 | 24,880 | 25,000 |
70 | 1,751 | 1,750 | 1,753 | 1,753 | 3,100 | 17,510 | 17,550 |
80 | 1,255 | 1,260 | 1,258 | 1,258 | 2,120 | 12,560 | 12,540 |
90 | 915 | 920 | 917 | 919 | 1,540 | 9,164 | 9,100 |
100 | 678 | 680 | 679 | 682 | 1,120 | 6,792 | 6,710 |
110 | 509 | 510 | 511 | 513 | 820 | 5,108 | 5,070 |
120 | 388 | 390 | 389 | 392 | 610 | 3,894 | 3,850 |
130 | 299 | 300 | 301 | 303 | 460 | 3,006 | 2,940 |
140 |
| 230 |
| 350 |
| 2,271 |
150 |
| 180 |
| 270 |
| 1,770 |
160 |
| 1,414 |
170 |
| 1,122 |
180 |
| 896 |
190 |
| 719 |
200 |
| 582 |
210 |
| 483 |
220 |
| 396 |
230 |
| 328 |
240 |
| 273.7 |
250 |
| 230 |
260 |
| 194.6 |
270 |
| 165.6 |
280 |
| 141.7 |
290 |
| 122 |
300 |
| 105.6 |