Notes regarding analog equipment - shielding and earth
Meticulous application of the term “earth” is required, particularly when it comes to reliable use of analog (measuring) signals. The conductive coupling of different potentials, such as earth potential and a housing potential or the earth points of analog devices, can have different aims:
  1. Earthing as protective measure against the occurrence of dangerous touch voltages (PE)
  2. Earthing for definition of a common signal potential, in order to ensure the function of analog measurements, for example
  3. Earthing for discharging of interference or internally generated emissions (FE); keywords: interference immunity and interference emission
In each case the user should be clear which of the above aims is to be achieved through the respective measures. The respective reference earth can have different potential!
The observations, measures and effects described below primarily refer to 3. “FE/functional earth”, taking into account the requirements of 2. “Common reference potential”. Information and specifications relating to 1. “PE” can be found in the relevant guidelines, such as VDE0100, and is not part of this section on analog equipment. The focus and application area of the following notes is for the scope of analog signal transmission.
Notes regarding analog equipment - shielding and earth 1:
The terms “protective earth” and “functional earth”
This section primarily deals with functional earth (FE,
symbol: Notes regarding analog equipment - shielding and earth 2:) as a functionally relevant regular part of an installation, in contrast to protective earth (PE, symbol: Notes regarding analog equipment - shielding and earth 3:), which is intended to protect persons from excessive touch voltages.
Notes regarding analog equipment - shielding and earth 4:
This document
This document provides general recommendations based on practical experience, without taking into account specific features of particular installations. These recommendations should be regarded as a collection of technical solution options. System manufacturers should check to what extent the measures described here are applicable to their system, and which of the suggested measures should be implemented. To this end, different measuring and testing techniques should be used. Any problems should be examined thoroughly, in order to ascertain the trigger and the fault location.
This document attempts to deal with a complex issue and does not claim to be exhaustive. We gladly accept suggestions or critical comments.
Notes regarding analog equipment - shielding and earth 5:
Lightning protection
Lightning protection aspects are not considered.
Notes regarding analog equipment - shielding and earth 6:
Potentially explosive areas
Special regulations and procedures may apply for potentially explosive atmospheres and supply lines for such areas, which are not covered by this documentation.
Notes regarding analog equipment - shielding and earth 7:
Reference to individual documents
Special instructions and documentation relating to the devices used must be followed.
Recommended procedure in the event of a conspicuousness
  1. Use this document, other publicly available documents/standards and manufacturer documentation to familiarise yourself with the background and practical characteristics of EMC interference.
    Reflect on the mechanism of action between source of interference → transfer path → interference sink.
  2. Use the specified diagnostic methods to isolate the interference sink, i.e. the location/device that does not work properly
  3. Reflect on how the fault could have occurred, taking into account the background information from section 1.
  4. Use the information and solution proposals provided to weigh up system-specific options or normative specifications/restrictions. We recommend to only change one component at a time, in order to verify the effectiveness of the respective measure.
  5. At the same time, use the specified diagnostic methods to ascertain whether the source of interference or the transfer path has been found.
Functional chain: source of interference – coupling – interference sink
The undesirable effect of a source of interference on an interference sink via the coupling can be reduced or completely suppressed through the measures described below. A fault results in modification of a wanted signal. In the worst case, the recipient of the wanted signal is no longer able to interpret the information content, or its operation is disturbed due to the modified amplitude/frequency or even electrical damaged.
The fault can be transferred by wire or by radiation.
Notes regarding analog equipment - shielding and earth 8:
A device can simultaneously act as source of interference and as interference sink (depending on the effective direction).
A cable/device acts as source of interference Notes regarding analog equipment - shielding and earth 9:through strong/weak interference effect (emissions, interference emission) due to (e.g.)
A cable/device acts as interference sink Notes regarding analog equipment - shielding and earth 10:through strong/weak susceptibility to interference, i.e. inadequate immunity to interference due to (e.g.)
In general, the following mechanisms are available for coupling a fault with the wanted signal:
Notes regarding analog equipment - shielding and earth 11:
Shielding measures or interference generation prevention may be applied as remedial action.
Galvanic coupling – measures against transfer:
Notes regarding analog equipment - shielding and earth 13:
Capacitive coupling – measures against transfer:
Inductive coupling – measures against transfer:
Wireless coupling - measures:
Common signal potential, basic measures and notices
In some applications the reference potentials of different devices have to be linked, e.g. in order to be able to perform a measurement.
FE/shielding, basic measures and information
A list of exemplary measures, taking into account the information provided above, which may be considered in order to reduce interference, is provided below.
Notes regarding analog equipment - shielding and earth 15:
- Pig tails (braid twisted at the end or wire attached to the braid) significantly reduce the effectiveness of the shield coupling. In principle, this is not advisable, particularly with regard to the requirements for interference immunity.
Notes regarding analog equipment - shielding and earth 16:
Notes regarding analog equipment - shielding and earth 18:
The coupling capacitor C must have sufficient dielectric strength. If necessary, a resistor R in the MΩ range can be connected in parallel with the capacitor.
CAUTION
In hazardous areas
Note special regulations for hazardous areas!
Notes regarding analog equipment - shielding and earth 22:
Equalization of potential difference
Additional safety measures
Practice-oriented diagnostic methods for system examination
The following section lists some options for checking the effectiveness of shielding measures: