FM33xx-B110 - 12 and 32 channel analog thermocouple input plug (TC-Plug)
FM33xx-B110-xxxx - Technical data
Technical data
FM3312-B110-0010
FM3332-B110-1010
Power supply
24 VDC, -15…+20% (20.4 .. 28.8 V)
typical operating current
120 mA (24 V)
150 mA (24 V)
max. operating current
150 mA (24 V)
180 mA (24 V)
Power supply input protection Reverse voltage
Over voltage
min. –35 V
max. 35 V
Potential separation
Thermocouples / Fieldbus
500 V
Thermocouples / Supply Voltage
500 V
Supply Voltage / Fieldbus
100 V
Operating temperature
0 °C ... + 55 °C
Storage temperature
-25 °C ... + 85 °C
Type of protection
IP65
Vibration
EN 60068-2-6
10 Hz <= f <= 57 Hz: 0,075 mm amplitude
57 Hz <= f <= 150 Hz: 1,0 g
Shock
EN 60068-2-27
35 g @ 6 ms
Vibration
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / EMC emission
conforms to EN 61000-6-2 / EN 61000-6-4
Approvals
CE, cULus
Fieldbus/Configuration
EtherCAT/ via TwinCAT System Manager
Number of inputs
12
32
Type of Input
Differential Input, mV measurement, high impedance grounded no electrical separation
Connection
2-wire, direct connection
Wiring length (max.)
30 m
Thermocouple sensor type
Type K:-100...1370°C, Type J:-100...900°C
Common Mode
input voltage range
-8 V...+8 V
Common mode rejection
typical 90 dB (independent from conversion time)
typical 150 dB (at 50 Hz or 60 Hz Rejection
Normal mode rejection
typical 98 dB (at 50 Hz or 60 Hz Rejection)
Resolution
0.1 °C per Digit
Total measuring error (temperature)
Cold junction compensation
Internal (temperature measurement in the plug)
Conversation time (per channel)
Adjustable
50 ms (60 Hz Common Mode Rejection)
60 ms (50 Hz Common Mode Rejection)
Data update time
200 ms (60 Hz), 230 ms (50 Hz)
Wiring fail indication
Yes (Open Thermocouple)
Back Voltage Range
>10 V, < -10 V
Switch off time
3 ms max.
Input resistance for current limitation
2400 R, typ.
Input voltage
100 VACbetween TC+ and TC- of each channel
240 VAC above Protective Earth
415 VAC to other TC
Input protection mechanism
Current limitation, Channel disconnect
Range of Input protection
240 VAC/DC
Earth connection
The plug must be connected to protective earth with the earth-connector in the plug!
Dimensions (L x W x H)
approx. 120 mm x 52 mm x 129 mm
Connector hood
Han24B (Harting)
Connector to Thermocouples
Han24E
Han64D
Contacts
Hard gold plated
Coding system
With coding pins in the connector
Connctor power supply
M8
Connector fieldbus
M12
Weight
approx. 500 g