FC310x - PCI Cards for PROFIBUS
Sync/Freeze functionality
Sync is used for the simultaneous outputting of outputs for several slaves. Freeze is used for reading in inputs from several slaves simultaneously.
The process in TwinCAT with FC310x and Bus Couplers (in K-bus synchronous mode) would therefore be as follows (see the Synchronization chapter):
The outputs are written at the beginning (I/O at the start of the task) or the end (I/O not at the start of the task) of the task cycle
This will start the PROFIBUS cycle
A Sync/Freeze telegram is sent at the start of the PROFIBUS cycle
This will cause the Bus Couplers to start a K-bus cycle with the outputs from the last task cycle and transfer the inputs from the last K-bus cycle
The master will then send the current outputs to each slave and pick up the transferred inputs
The inputs are read at the start of the next task cycle
etc.
Outputs and inputs are therefore always one cycle old.
 syncfreeze
On the FC310x, set the Operation Mode on the "FC310x" tab (for TwinCAT 2.8 or TwinCAT 2.9) of the master to "DP/MC (equidistant)". At the boxes to be operated via Sync/Freeze, click the flag Sync/Freeze enable on the Profibus tab. The master always uses group 1 for the Sync/Freeze synchronization.