Read or Write Registers (Function 23)
A number of analog outputs can be written and a number of analog inputs read with one telegram using the Read / Write Registers function. In this example the first two analog output words are written, and the first two analog inputs are read. The analog outputs start at offset 0x0800, while the inputs start at offset 0x0000. Here the offset always describes a word. Offset 0x0003 writes to the fourth word in the output process image. The length indicates the number of words, and the Byte count is formed from the combination of all the bytes that are to be written. Example: 4 words – correspond to a byte count of 8.
The data bytes contain the values for the analog outputs. In this example, two words are to be written. The first word is to receive the value 0x3FFF, and the second word is to receive the value 0x7FFF.
Query
Byte Name
Modbus RTU
Modbus ASCII
Start - Frame
0x3A
Address
11
0x0B
"0B"
0x30, 0x42
Function-Code
23
0x17
"17"
0x31, 0x17
Read Start-Address high
0
0x00
"00"
0x30, 0x30
Read Start-Address low
0
0x00
"00"
0x30, 0x30
Read Länge high
0
0x00
"00"
0x30, 0x30
Read Länge low
2
0x02
"02"
0x30, 0x32
Write Start-Address high
8
0x08
"08"
0x30, 0x38
Write Start-Address low
0
0x00
"00"
0x30, 0x30
Write Länge high
0
0x00
"00"
0x30, 0x30
v Länge low
2
0x02
"02"
0x30, 0x32
Byte Count
4
0x04
"04"
0x30, 0x34
Data 1 high
63
0x3F
"3F"
0x33, 0x46
Data 1 low
255
0xFF
"FF"
0x46, 0x46
Data 2 high
127
0x7F
"7F"
0x37, 0x46
Data 2 low
255
0xFF
"FF"
0x46, 0x46
Error Check, LRC/CRC
0x76, 0xD3
"12"
0x31, 0x32
End - Frame
t1-t2-t3
CRLF
0x0D, 0x0A
Response
The coupler replies with the start address and the length of the bytes to be transferred in Byte count. The data information follows. In this example the first word contains 0x0038 while the second word contains 0x3F0B.
Byte Name
Modbus RTU
Modbus ASCII
Start - Frame
0x3A
Address
11
0x0B
"0B"
0x30, 0x42
Function-Code
23
0x17
"17"
0x31, 0x17
Byte Count
4
0x04
"04"
0x30, 0x34
Data 1 high
0
0x00
"00"
0x30, 0x30
Data 1 low
56
0x38
"38"
0x33, 0x38
Data 2 high
63
0x3F
"3F"
0x33, 0x46
Data 2 low
11
0x0B
"0B"
0x30, 0x42
0xF8, 0xA7
"E3"
0x45, 0x33
End - Frame
t1-t2-t3
CRLF
0x0D, 0x0A