Control and Status Byte IP/IE60x2
Process data mode
For setting up data exchange (handshake), the control and the status byte are used in process data exchange.
Control Byte
The control byte is transmitted from the controller to the mopdule. It is located in the output image, and can be read or written.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
OL2 |
OL1 |
OL0 |
IR |
RA |
TR |
Name |
Description |
RegAccess |
0bin: register communication switched off (Process data mode: Control and status byte in handshake) |
OL2-OL1 |
Count of the data sent |
IR |
Handshake bit for initialisation of the Bus
Terminal/module |
RA |
Handshake bit for receiving data |
TR |
Handshake bit for sending data |
Status byte
The status byte is transmitted from the module to the controller. It is located in the input image, and can only be read.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
IL2 |
IL1 |
IL0 |
BUF_F |
IA |
RR |
TA |
Name |
Description |
RegAccess |
0bin: acknowledge for Process data mode (Control and status byte in handshake) |
IL2-IL0 |
Count of the data received |
BUF_F |
Receive buffer full, any data now received will be lost |
IA |
Terminal/module |
RR |
TA |
Note: When the first data is received there is only one byte in the buffer, because the Bus Terminal/module does not yet know whether other data follows.
Examples
Example of data reception
Note: Evcen in case of the reception of more than 1 byte, there is always the indication for 1 byte in the beginning.
Output |
Input |
Description |
0000_0000 |
0xxx_x00x |
Start of data transmission |
0xxx_000x |
0011_x01x |
3 bytes in the data bytes are ready to be fetched |
0xxx_001x |
0011_x01x |
Acknowledgement that the data bytes have been fetched |
0xxx_001x |
0101_x00x |
5 bytes in the data bytes are ready to be fetched |
0xxx_000x |
0101_x00x |
Output |
Input |
Description |
0000_0000 |
0xxx_x0x0 |
0010_00x1 |
0xxx_x0x0 |
2 bytes in the data bytes are to be sent |
0010_00x1 |
0xxx_x0x1 |
2 bytes of data have been loaded into the send FIFO, data is sent |
0101_00x0 |
0xxx_x0x1 |
5 bytes in the data bytes are to be sent |
0101_00x0 |
0xxx_x0x0 |
5 bytes of data have been loaded into the send FIFO, data is sent |
Output |
Input |
Description |
0xxx_xxxx |
0xxx_xxxx |
0000_0100 |
0xxx_xxxx |
Bus Terminal/module is to be initialised |
0000_0100 |
0000_0100 |
Bus Terminal/module has completed initialisation |
0000_0000 |
0000_0100 |
Place Bus Terminal/module once more into data exchange |
0000_0000 |
0000_0000 |
Bus Terminal/module is ready to operate |
Error handling
If a parity, framing or overrun error occurs, the corresponding
data is lost in transmission and will not be loaded into the
reception FIFO buffer of the Bus Terminal/module.
If the buffer is full, incoming data will be ignored.
The appropriate diagnostic bits in register 6 are set in the event
of an error.
Register Communication
Serial data cannot be transmitted during register communication.
Control byte
The control byte is only visible if the Fieldbus Box is operated in complete mode. It is located in the output image, and can be read or written.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
R/W |
Register number | |||||
Name |
Description |
RegAccess |
1bin: Register communication switched on |
R/W |
0bin: Read |
Register number |
Number of the register that is to be read or written. |
Status byte
The status byte is only visible if the Fieldbus Box is operating in complete mode. It is located in the input image, and can only be read.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
R/W |
Name |
Description |
RegAccess |
1bin: Acknowledgement for register access |
R/W |
0bin: Read |
Register number |
Number of the register that was read or written. |