Control and Status Byte IP/IE5109
Process data mode
Control byte
The control byte is only visible if the Fieldbus Box is operated in complete mode. It is located in the output image, and can be read or written.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
CNT_SET |
EN_LAT_EXT / |
EN_LATC |
Name |
Description |
RegAccess |
0bin: Register communication off (process data mode) |
CNT_SET |
A rising edge at CNT_SET will set the counter to the value specified in the process data. |
EN_LAT_EXT |
The external latch input is activated. The value of the counter is entered into the latch register at the first external latch pulse after the EN_LAT_EXT bit becomes valid. When this bit is set, the subsequent pulses do not have any effect on the latch register. It is necessary to ensure that the corresponding latch-valid bit (LAT_EXT_VAL) is cleared by the module before activating the null pulse. This functionality can be set in the feature register (default setting). |
RD_PERIOD |
The length of the period between two positive edges at input A is measured with a resolution of 200 ns. When the bit is set, this duration is output in data bytes D3 and D4. This functionality can be set in the feature register. |
EN_LATC |
The null point latch (C input) is activated. The value of the counter is entered into the latch register at the first external latch pulse after the EN_LATC bid becomes valid (it has a higher priority than EN_LAT_EXT). When this bit is set, the subsequent pulses do not have any effect on the latch register. It is necessary to ensure that the corresponding latch-valid bit (LATC_VAL) is cleared by the module before activating the null pulse. (The LATC_VAL bit can only be reset by the module when the C pulse is at a low level.) |
Status byte
The status byte is only visible if the Fieldbus Box is operated in complete mode. It is located in the Fieldbus Box's input image, and can only be read.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
STATUS_INPUT |
OVERFLOW |
UNDERFLOW |
CNTSET-ACC |
LAT_EXT_VAL/ |
LATC_VAL |
Name |
Description |
RegAccess |
0bin: Acknowledgement for process data mode |
STATUS_INPUT |
The state of the status input can be represented with this bit. (Can be set via the feature register.) |
OVERFLOW |
This bit is set if the 16-bit counter overflows (65535 to 0). It is reset when the counter exceeds one third of its measuring range (21845 to 21846) or immediately an underflow occurs. |
UNDERFLOW |
This bit is set if the 16-bit counter underflows (65535 to 0). It is reset when the counter drops below two thirds of its measuring range (43690 tp 43689) or immediately an overflow occurs. |
CNTSET_ACC |
The data for setting the counter is accepted from the module. |
LAT_EXT_VAL |
An external latch pulse has occurred. Data D3 and D4 in the process image corresponds to the current counter value when the bit is set. In order to reactivate the latch input, it is necessary for EN_LAT_EXT first be cleared and then to be set once more. |
RD_PERIOD_Q |
Data bytes 3 and 4 contain the length of the period. |
LATC_VAL |
A zero point latch has occurred. Data D3 and D4 in the process image corresponds to the current counter value when the bit is set. In order to reactivate the latch input, it is necessary for EN_LATC first be cleared and then to be set once more. |
Register Communication
Measured values cannot be transmitted during register communication.
Control byte
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
R/W |
Register number | |||||
Name |
Description |
RegAccess |
1bin: Register communication switched on |
R/W |
0bin: Read |
Register number |
Number of the register that is to be read or written. |
Status byte
The status byte is only visible if the Fieldbus Box is operating in complete mode. It is located in the input image, and can only be read.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
RegAccess |
R/W |
Name |
Description |
RegAccess |
1bin: Acknowledgement for register access |
R/W |
0bin: Read |
Register number |
Number of the register that was read or written. |