Functioning IP/IE5109
The IP/IE5109 incremental encoder interface module allows any 5 V incremental encoder to be connected to the Fieldbus or Coupler Box. A 16 bit counter with a quadrature decoder and a 16 bit latch can be read, set or enabled. In addition to the encoder inputs A, B and C, an additional latch input (24 V) and a gate input (24 V) for locking the counter are available.
It is also possible for the 16-bit up/down counter operating mode to be selected. In this mode, input A is the counter input, input B defines the direction.
The feature register permits measurement of periods. In this case, the length of the period between two positive edges in input signal A is determined with a resolution of 250 ns.
Single, double or quadruple evaluation of the encoder signals A, B and C in simple or complementary form can be parameterised via the fieldbus. The module is supplied set to function as a 4-fold quadrature decoder with complementary evaluation of the encoder signals A, B and C.
If the encoder has a fault signal output, it can be connected to the STATUS input of the module.
The encoder is supplied with the necessary 5 VDC power from the module.
Process data
Signals
Inputs A, /A
Pulse input in the module's encoder and counter operating modes
Inputs B,/B
Phase-shifted pulse input in the module's encoder operating mode
Inputs C,/C
Zero point pulse input for the module's latch register
This input is activated by means of the EN_LATC bit in the module's control byte
External latch 24 V
Additional latch input for the module
This input is activated by means of the EN_LAT_EXT bit in the module's control byte.
If this input is enabled, the counter value will be latched when the edge changes from 0 V to 24 V.
External gate 24 V
A high level at this contact halts counting in the terminal.
Status input
If the incremental encoder has a fault signal output, it can be connected to the status input (an active low input with internal pull up circuitry).
US
Power supply for the electronics and the encoder
UP, GND
In order for the module to operate, a power supply of 0 V and 24 V must be connected to these contacts.