Control and Status Byte IP/IE3102
Process Data Mode
Control Byte
The Control byte is only visible, if the Fieldbus Box is operated in complete mode. The byte is located in the output image, and can be read or written.
Bit
7
6
5
4
3
2
1
0
RegAccess
  Key:
Bit
description
7
RegAccess
0bin
Register Communication switched off  (Process data mode)
6...0
reserved
Status byte
The Status byte is only visible if the Fieldbus Box is set to complete mode. The byte is located in the input image, and can only be read.
Bit
7
6
5
4
3
2
1
0
RegAccess
Error
Limit value 2
Limit value 1
Over-Range
Under-Range
Key:
Bit
description
7
RegAccess
0bin
Acknowledgement for process data mode
6
Error
general error bit
5,4
Limit value 2
00bin
Limit value 2 not active
01bin
Process data > limit value 2
10bin
Process data < limit value 2
11bin
Process data = limit value 2
3,2
Limit value 1
00bin
Limit value 1 not active
01bin
Process data > limit value 1
10bin
Process data < limit value 1
11bin
Process data = limit value 1
1
Over-Range
1bin
if R32 Bit 4 = 0: Range of measurement exceeded (>0x7FFF)
if R32 Bit 4 = 1: Measured value ≥ 10.5 V
0
Under-Range
1bin
if R32 Bit 4 = 0: Measurement is below range (> 0x8000)
if R32 Bit 4 = 1: Measured value ≤ -10.5 V
NOTICE
Note
The user scaling must be modified in order to change the under/over range limits. Example: You want to set an over range value of 10.6 V. You therefore have to activate the user scaling, and change the gain in register 34 to 0x00F0. The measuring range now goes up to 10.6 V (the maximum possible is 11.8 V).
Measured values cannot be transmitted during register communication.
Control Byte
The Control byte is only visible if the Fieldbus Box is set to complete mode. It is located in the output image, and can be read or written.
Bit
7
6
5
4
3
2
1
0
RegAccess
R/W
Register number
Key:
Bit
description
7
RegAccess
1bin:
Register Communication switched on
6
R/W
0bin
Read
1bin
Write
5...0
Register number
Number of the register that is to be read or written
Status Byte
The Status byte is only visible if the Fieldbus Box is set to complete mode. It byte is located in the input image, and can only be read.
Bit
7
6
5
4
3
2
1
0
RegAccess
R/W
Register number
Key:
Bit
description
7
RegAccess
1bin
Acknowledgement for register access
6
R/W
0bin
Read
5...0
Register number
Number of the register that has been read or written