Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Technical data |
EPP6001-0002 |
Fieldbus | |
Fieldbus | EtherCAT |
Connection | EtherCAT P: Combined connection for EtherCAT and supply voltages Input: 1 x M8 socket, 4-pin, P-coded |
Supply voltages | |
Connection | See Fieldbus connection |
Control voltage US | |
Nominal voltage | 24 VDC (-15 % / +20 %) |
Sum current | max. 3 A 1) |
Consumers | • Module electronics: 100 mA • Remote communication station (e.g. barcode scanner) • Loads at digital outputs |
Peripheral voltage UP | |
Current consumption from UP | None. UP is only forwarded. |
Serial interface | |
Number of channels | 1 |
Interface type | Parameterizable:
Connection | RS232: 1x M12 socket RS422: 2x M12 socket RS485: 1x M12 socket |
End device supply voltage 2) | 5 VDC from the control voltage US max. 1 A, short-circuit proof |
Cable length | RS232: max. 15 m RS422/RS485: max. 1,000 m |
Data transfer rate | Parameterizable: 300 .. 115,200 baud (bit/s) |
Data format | Parameterizable: 8N1, 7E1, 7O1, 8N1, 8E1, 8O1, 7E2, 7O2, 8N2, 8E2, 8O2 |
Bit distortion | < 3 % |
1) Sum current of consumers and power transmission.
2) Supply voltage available at the connections of the serial interface.
Technical data |
EPP6001-0002 |
Digital inputs/outputs | |
Number | 2 |
Connection | 1x M12 socket |
I/O supply voltage 3) | 24 VDC from the control voltage US max. 0.5 A, short-circuit proof |
Input specification | |
Characteristics | Type 3 according to EN 61131-2, compatible with type 1 |
Input filter | 10 µs |
Signal voltage “0” | -3 .. +5 VDC |
Signal voltage "1" | +11 .. +30 VDC |
Input current | 3 mA at 24 VDC |
Output specification | |
Load type | ohmic, inductive, lamp load |
Nominal voltage | 24 VDC (-15%/+20%) from the control voltage US |
Output current | max. 0.5 A per channel, short-circuit proof |
Environmental conditions | |
Ambient temperature during operation | -25…+60 °C |
Ambient temperature during storage | -40…+85 °C |
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Mechanics | |
Weight | approx. 165 g |
Approvals and conformity | |
Approvals | CE, cULus |
3) Supply voltage available at the connection of the digital inputs/outputs.