EPP5001-0002
![]() | Parameterization You can parameterize the box via the "CoE - Online" tab in TwinCAT. |
![]() | EtherCAT XML Device Description The presentation matches that of the EtherCAT XML Device Description. |
Introduction
- Objects required for parameterization during commissioning
- Objects intended for regular operation, e.g. through ADS access.
- Objects for indicating internal settings (may be fixed)
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x01F51389 (32838537dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EPP5001-0002 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | - |
Index 100A Software version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | - |
Index 1011 Restore default parameters
1011:0 | Restore default parameters | Restore default parameters | UINT8 | RO | 0x01 (1dec) |
1011:01 | SubIndex 001 | If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state. | UINT32 | RW | 0x00000000 (0dec) |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x6476FE99 (1685520025dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description | UINT32 | RO | 0x00000000 (0dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1800 SSI TxPDO-Par Inputs
1801:0 | SSI TxPDO-Par Inputs | PDO parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1801:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 00 1A |
Index 1A00 SSI TxPDO-Map Inputs
1A00:0 | SSI TxPDO-Map Inputs | PDO Mapping TxPDO 1 | UINT8 | RO | 0x08 (8dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x01 (Data error)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x02 (Frame error)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x03 (Power failure)) | UINT32 | RO | 0x6000:03, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (10 bits align) | UINT32 | RO | 0x0000:00, 10 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x0E (Sync error)) | UINT32 | RO | 0x6000:0E, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (SSI Inputs), entry 0x11 (Counter value)) | UINT32 | RO | 0x6000:11, 32 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x00 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RO | 0x02 (2dec) |
1C13:01 | SubIndex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RO | 0x1A00 (6656dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0xC00B (49163dec) |
1C33:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00030D40 (0dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time | - | UINT32 | RO | 0x000001B0 (7600dec) |
1C33:08 | Command | With this entry the real required process data provision time can be measured.
The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x000001B0 (7600dec) |
1C33:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 6000 SSI Inputs
6000:0 | SSI Inputs | Length of this object | UINT8 | RO | 0x11 (17dec) |
6000:01 | Data error | SSI input error: If no data transmission occurs, the SSI input is on low signal level. | BOOLEAN | RO | 0x00 (0dec) |
6000:02 | Frame error | The data frame is wrong, i.e. the data frame was not terminated with zero (perhaps wire breakage on clock cables) | BOOLEAN | RO | 0x00 (0dec) |
6000:03 | Power failure | An encoder-specific error has occurred. This error bit is only displayed if it was previously enabled through Enable power failure bit index 0x8000:02. | BOOLEAN | RO | 0x00 (0dec) |
6000:0E | Sync error | The Sync error bit is only required for DC mode. It indicates whether a synchronization error has occurred during the previous cycle. This means a SYNC signal was triggered in the Box, although no new process data were available (0=OK, 1=NOK). | BOOLEAN | RO | 0x00 (0dec) |
6000:0F | TxPDO State | Validity of the data of the associated TxPDO (0 = valid, 1 = invalid). | BOOLEAN | RO | 0x00 (0dec) |
6000:10 | TxPDO Toggle | The TxPDO toggle is toggled by the slave when the data of the associated TxPDO is updated. | BOOLEAN | RO | 0x00 (0dec) |
6000:11 | Counter value | Counter value | UINT32 | RO | 0x00000000 (0dec) |
Index 8000 SSI Settings
8000:0 | SSI Settings | Length of this object | UINT8 | RO | 0x13 (19dec) |
8000:01 | Disable frame error | 0: Frame error is not suppressed | BOOLEAN | RW | 0x00 (0dec) |
8000:02 | Enable power failure bit | 0: Power failure bit is not active | BOOLEAN | RW | 0x00 (0dec) |
8000:03 | Enable inhibit time | 0: Inhibit time is not active | BOOLEAN | RW | 0x00 (0dec) |
8000:04 | Enable test mode | 0: Test mode is not active | BOOLEAN | RW | 0x00 (0dec) |
8000:06 | SSI-coding | 0: Binary code active | BIT1 | RW | 0x01 (1dec) |
8000:09 | SSI-baudrate | 0: reserved | BIT3 | RW | 0x03 (3dec) |
8000:0F | SSI-frame type | 0: Multi-turn analysis is active (25 bit data frame) | BIT2 | RW | 0x00 (0dec) |
8000:11 | SSI-frame size | Length of the SSI data frame (in bits) | UINT16 | RW | 0x0019 (25dec) |
8000:12 | SSI-data length | Data length | UINT16 | RW | 0x0018 (24dec) |
8000:13 | Min. inhibit time[µs] | Minimum inhibit time in µs (1 to 65535) | UINT16 | RW | 0x0000 (0dec) |
Index 800D SSI Advanced Settings
800D:0 | SSI advanced settings | SSI advanced settings |
| RW | 0x03 (3dec) |
800D:01 | Encoder power supply on | Switches the 24 V supply voltage |
| RW | 0x01 (1dec) |
800D:02 | Encoder direction pin on | Switches the 24 V supply at the direction pin |
| RW | 0x00 (0dec) |
800D:03 | Encoder reset pin on | Switches the 24 V supply at the reset pin |
| RW | 0x00 (0dec) |
F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
F000:01 | Module index distance | Index distance of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0001 (1dec) |
Index F008 Code word
F008:0 | Code word | reserved | UINT32 | RW | 0x00000000 (0dec) |
Index F010 Module list
F010:0 | Module list | Length of this object | UINT8 | RW | 0x02 (2dec) |
F010:01 | SubIndex 001 | - | UINT32 | RW | 0x000001F5 (501dec) |
