Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT P | |
Connection | 2 x M8 socket, 4-pin, P-coded, red |
Distributed Clocks | yes |
Minimum cycle time | 700 µs |
Supply voltages | |
Connection | See EtherCAT P connection |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current: IS,sum |
max. 3 A |
Current consumption from US | 100 mA + Current consumption of connected sensors + Loads at digital outputs |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP sum current: IP,sum |
max. 3 A |
Current consumption from UP | None. UP is only forwarded. |
Diagnostics | Undervoltage detection
Pressure inputs | EPP3744-0041 | EPP3744-1041 |
Number | 4 + 1 reference input for the differential pressure measurement | |
Connections | Fittings, d = 6 mm | |
Number of mating cycles | 5 | |
Type of pressure measurement |
0 … 1 bar 1) | 0 … 7 bar 1) | |
Differential pressure measuring range 2) | -1 … +1 bar | -7 … +7 bar |
Resolution | 1 mbar per LSB | |
Measuring error | 3% of the full scale value | |
Conversion time | 5 EtherCAT cycles (Note the minimum EtherCAT cycle time, see above) | |
Permissible media | non-aggressive gases | |
Maximum overload of an input | 3 bar absolute pressure 2) | 21 bar absolute pressure 2) |
1) 0 bar = vacuum
1 bar = ambient pressure
2) Even in the case of differential pressure measurement, the absolute pressure measuring range must not be exceeded at any pressure input.
Digital inputs | |
Number | 6 |
Connection | 4 x M8 socket |
Characteristics | EN 61131-2 type 3, compatible with type 1 |
Signal voltage "0" | -3 … +5 V |
Signal voltage "1" | +11 … +30 V |
Input current | 3 mA at 24 V |
Sensor power supply | 24 VDC from the control voltage US max. 0.5 A in total, short-circuit proof |
Digital outputs | |
Number | 2 |
Connection | 2 x M8 socket (sockets X03 and X04) |
Nominal output voltage | 24 VDC from the control voltage US |
Output current | max. 0.5 A per output, individually short-circuit proof |
Housing data | |
Dimensions W x H x D | 30 mm x 126 mm x 26.5 mm |
Weight | approx. 175 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation | -25 … +60 °C |
Ambient temperature during storage | -40 … +85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Approvals / markings | |
Approvals / markings *) | CE, cULus |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |