Standard objects and PDO mapping
![]() | EtherCAT XML Device Description The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions. |
![]() | Parameterization via the CoE list (CAN over EtherCAT) The EtherCAT device is parameterized via the CoE-Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE notes when using/manipulating the CoE parameters:
Index 1000 Device type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1000:0 |
Device type |
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. |
UINT32 |
RO |
0x012C1389 (19665801dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EPP3632-0001 |
Index 1009 Hardware version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1009:0 |
Hardware version |
Hardware version of the EtherCAT slave |
STRING |
RO |
Index 100A Software version
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
100A:0 |
Software version |
Firmware version of the EtherCAT slave |
STRING |
RO |
05 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x6476A909 (1685498121dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description | UINT32 | RO | 0x00110000 (1114112dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
10F0:0 |
Backup parameter handling |
Information for standardized loading and saving of backup entries |
UINT8 |
RO |
0x01 (1dec) |
10F0:01 |
Checksum |
Checksum across all backup entries of the EtherCAT slave |
UINT32 |
RO |
0x00000000 (0dec) |
Index 1A00 Analog Input TxPDO-Map Status Ch.1
1A00:0 | Analog Input TxPDO-MapStatus Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x09 (9dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (Status), entry 0x01 (Underrange)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (Status), entry 0x02 (Overrange)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (Status), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6000:03, 2 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (Status), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6000:05, 2 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (Status), entry 0x07 (Error)) | UINT32 | RO | 0x6000:07, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (Status), entry 0x0E (Sync error)) | UINT32 | RO | 0x6000:0E, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (Status), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6000:0F, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (Status), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6000:10, 1 |
Index 1A01 Analog Input TxPDO-MapSamples 1 Ch.1
1A01:0 | Analog Input TxPDO-MapSamples 1 Ch.1 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x01 (1dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x01) | UINT32 | RO | 0x6001:01, 16 |
Index 1A02 Analog Input TxPDO-MapSamples 2 Ch.1
1A02:0 | Analog Input TxPDO-MapSamples 2 Ch.1 | PDO Mapping TxPDO 3 | UINT8 | RO | 0x01 (1dec) |
1A02:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x02 ()) | UINT32 | RO | 0x6001:02, 16 |
Index 1A03 Analog Input TxPDO-MapSamples 3 Ch.1
1A03:0 | Analog Input TxPDO-MapSamples 3 Ch.1 | PDO Mapping TxPDO 4 | UINT8 | RO | 0x01 (1dec) |
1A03:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x03 ()) | UINT32 | RO | 0x6001:03, 16 |
Index 1A04 Analog Input TxPDO-MapSamples 4 Ch.1
1A04:0 | Analog Input TxPDO-MapSamples 4 Ch.1 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x01 (1dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x04 ()) | UINT32 | RO | 0x6001:04, 16 |
Index 1A05 Analog Input TxPDO-MapSamples 5 Ch.1
1A05:0 | Analog Input TxPDO-MapSamples 5 Ch.1 | PDO Mapping TxPDO 6 | UINT8 | RO | 0x01 (1dec) |
1A05:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x05 ()))) | UINT32 | RO | 0x6001:05, 16 |
Index 1A06 Analog Input TxPDO-MapSamples 6 Ch.1
1A06:0 | Analog Input TxPDO-MapSamples 6 Ch.1 | PDO Mapping TxPDO 7 | UINT8 | RO | 0x01 (1dec) |
1A06:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x06 ()) | UINT32 | RO | 0x6001:06, 16 |
Index 1A07 Analog Input TxPDO-MapSamples 7 Ch.1
1A07:0 | Analog Input TxPDO-MapSamples 7 Ch.1 | PDO Mapping TxPDO 8 | UINT8 | RO | 0x01 (1dec) |
1A07:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x07 ()) | UINT32 | RO | 0x6001:07, 16 |
Index 1A08 Analog Input TxPDO-MapSamples 8 Ch.1
1A08:0 | Analog Input TxPDO-MapSamples 8 Ch.1 | PDO Mapping TxPDO 9 | UINT8 | RO | 0x01 (1dec) |
1A08:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x08 ()) | UINT32 | RO | 0x6001:08, 16 |
Index 1A09 Analog Input TxPDO-MapSamples 9 Ch.1
1A09:0 | Analog Input TxPDO-MapSamples 9 Ch.1 | PDO Mapping TxPDO 10 | UINT8 | RO | 0x01 (1dec) |
1A09:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x09 ()) | UINT32 | RO | 0x6001:09, 16 |
Index 1A0A Analog Input TxPDO-MapSamples 10 Ch.1
1A0A:0 | Analog Input TxPDO-MapSamples 10 Ch.1 | PDO Mapping TxPDO 11 | UINT8 | RO | 0x01 (1dec) |
1A0A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0A ()) | UINT32 | RO | 0x6001:0A, 16 |
Index 1A0B Analog Input TxPDO-MapSamples 11 Ch.1
1A0B:0 | Analog Input TxPDO-MapSamples 11 Ch.1 | PDO Mapping TxPDO 12 | UINT8 | RO | 0x01 (1dec) |
1A0B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0B ()) | UINT32 | RO | 0x6001:0B, 16 |
Index 1A0C Analog Input TxPDO-MapSamples 12 Ch.1
1A0C:0 | Analog Input TxPDO-MapSamples 12 Ch.1 | PDO Mapping TxPDO 13 | UINT8 | RO | 0x01 (1dec) |
1A0C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0C ()) | UINT32 | RO | 0x6001:0C, 16 |
Index 1A0D Analog Input TxPDO-MapSamples 13 Ch.1
1A0D:0 | Analog Input TxPDO-MapSamples 13 Ch.1 | PDO Mapping TxPDO 14 | UINT8 | RO | 0x01 (1dec) |
1A0D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0D ()) | UINT32 | RO | 0x6001:0D, 16 |
Index 1A0E Analog Input TxPDO-MapSamples 14 Ch.1
1A0E:0 | Analog Input TxPDO-MapSamples 14 Ch.1 | PDO Mapping TxPDO 15 | UINT8 | RO | 0x01 (1dec) |
1A0E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0E ()) | UINT32 | RO | 0x6001:0E, 16 |
Index 1A0F Analog Input TxPDO-MapSamples 15 Ch.1
1A0F:0 | Analog Input TxPDO-MapSamples 15 Ch.1 | PDO Mapping TxPDO 16 | UINT8 | RO | 0x01 (1dec) |
1A0F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0F ()) | UINT32 | RO | 0x6001:0F, 16 |
Index 1A10 Analog Input TxPDO-MapSamples 16 Ch.1
1A10:0 | Analog Input TxPDO-MapSamples 16 Ch.1 | PDO Mapping TxPDO 17 | UINT8 | RO | 0x01 (1dec) |
1A10:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x10 ()) | UINT32 | RO | 0x6001:10, 16 |
Index 1A11 Analog Input TxPDO-MapSamples 17 Ch.1
1A11:0 | Analog Input TxPDO-MapSamples 17 Ch.1 | PDO Mapping TxPDO 18 | UINT8 | RO | 0x01 (1dec) |
1A11:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x11 ()) | UINT32 | RO | 0x6001:11, 16 |
Index 1A12 Analog Input TxPDO-MapSamples 18 Ch.1
1A12:0 | Analog Input TxPDO-MapSamples 18 Ch.1 | PDO Mapping TxPDO 19 | UINT8 | RO | 0x01 (1dec) |
1A12:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x12 ()) | UINT32 | RO | 0x6001:12, 16 |
Index 1A13 Analog Input TxPDO-MapSamples 19 Ch.1
1A13:0 | Analog Input TxPDO-MapSamples 19 Ch.1 | PDO Mapping TxPDO 20 | UINT8 | RO | 0x01 (1dec) |
1A13:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x13 ()) | UINT32 | RO | 0x6001:13, 16 |
Index 1A14 Analog Input TxPDO-MapSamples 20 Ch.1
1A14:0 | Analog Input TxPDO-MapSamples 20 Ch.1 | PDO Mapping TxPDO 21 | UINT8 | RO | 0x01 (1dec) |
1A14:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x14 ()) | UINT32 | RO | 0x6001:14, 16 |
Index 1A15 Analog Input TxPDO-MapSamples 21 Ch.1
1A15:0 | Analog Input TxPDO-MapSamples 21 Ch.1 | PDO Mapping TxPDO 22 | UINT8 | RO | 0x01 (1dec) |
1A15:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x15 ()) | UINT32 | RO | 0x6001:15, 16 |
Index 1A16 Analog Input TxPDO-MapSamples 22 Ch.1
1A16:0 | Analog Input TxPDO-MapSamples 22 Ch.1 | PDO Mapping TxPDO 23 | UINT8 | RO | 0x01 (1dec) |
1A16:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x16 ()) | UINT32 | RO | 0x6001:16, 16 |
Index 1A17 Analog Input TxPDO-MapSamples 23 Ch.1
1A17:0 | Analog Input TxPDO-MapSamples 23 Ch.1 | PDO Mapping TxPDO 24 | UINT8 | RO | 0x01 (1dec) |
1A17:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x17 ()) | UINT32 | RO | 0x6001:17, 16 |
Index 1A18 Analog Input TxPDO-MapSamples 24 Ch.1
1A18:0 | Analog Input TxPDO-MapSamples 24 Ch.1 | PDO Mapping TxPDO 25 | UINT8 | RO | 0x01 (1dec) |
1A18:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x18 ()) | UINT32 | RO | 0x6001:18, 16 |
Index 1A19 Analog Input TxPDO-MapSamples 25 Ch.1
1A19:0 | Analog Input TxPDO-MapSamples 25 Ch.1 | PDO Mapping TxPDO 26 | UINT8 | RO | 0x01 (1dec) |
1A19:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x19 ()) | UINT32 | RO | 0x6001:19, 16 |
Index 1A1A Analog Input TxPDO-MapSamples 26 Ch.1
1A1A:0 | Analog Input TxPDO-MapSamples 26 Ch.1 | PDO Mapping TxPDO 27 | UINT8 | RO | 0x01 (1dec) |
1A1A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1A ()) | UINT32 | RO | 0x6001:1A, 16 |
Index 1A1B Analog Input TxPDO-MapSamples 27 Ch.1
1A1B:0 | Analog Input TxPDO-MapSamples 27 Ch.1 | PDO Mapping TxPDO 28 | UINT8 | RO | 0x01 (1dec) |
1A1B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1B ()) | UINT32 | RO | 0x6001:1B, 16 |
Index 1A1C Analog Input TxPDO-MapSamples 28 Ch.1
1A1C:0 | Analog Input TxPDO-MapSamples 28 Ch.1 | PDO Mapping TxPDO 29 | UINT8 | RO | 0x01 (1dec) |
1A1C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1C ()) | UINT32 | RO | 0x6001:1C, 16 |
Index 1A1D Analog Input TxPDO-MapSamples 29 Ch.1
1A1D:0 | Analog Input TxPDO-MapSamples 29 Ch.1 | PDO Mapping TxPDO 30 | UINT8 | RO | 0x01 (1dec) |
1A1D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1D ()) | UINT32 | RO | 0x6001:1D, 16 |
Index 1A1E Analog Input TxPDO-MapSamples 30 Ch.1
1A1E:0 | Analog Input TxPDO-MapSamples 30 Ch.1 | PDO Mapping TxPDO 31 | UINT8 | RO | 0x01 (1dec) |
1A1E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1E ()) | UINT32 | RO | 0x6001:1E, 16 |
Index 1A1F Analog Input TxPDO-MapSamples 31 Ch.1
1A1F:0 | Analog Input TxPDO-MapSamples 31 Ch.1 | PDO Mapping TxPDO 32 | UINT8 | RO | 0x01 (1dec) |
1A1F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1F ()) | UINT32 | RO | 0x6001:1F, 16 |
Index 1A20 Analog Input TxPDO-MapSamples 32 Ch.1
1A20:0 | Analog Input TxPDO-MapSamples 32 Ch.1 | PDO Mapping TxPDO 33 | UINT8 | RO | 0x01 (1dec) |
1A20:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x20 ()) | UINT32 | RO | 0x6001:20, 16 |
Index 1A21 Analog Input TxPDO-MapSamples 33 Ch.1
1A21:0 | Analog Input TxPDO-MapSamples 33 Ch.1 | PDO Mapping TxPDO 34 | UINT8 | RO | 0x01 (1dec) |
1A21:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x21 ()) | UINT32 | RO | 0x6001:21, 16 |
Index 1A22 Analog Input TxPDO-MapSamples 34 Ch.1
1A22:0 | Analog Input TxPDO-MapSamples 34 Ch.1 | PDO Mapping TxPDO 35 | UINT8 | RO | 0x01 (1dec) |
1A22:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x22 ()) | UINT32 | RO | 0x6001:22, 16 |
Index 1A23 Analog Input TxPDO-MapSamples 35 Ch.1
1A23:0 | Analog Input TxPDO-MapSamples 35 Ch.1 | PDO Mapping TxPDO 36 | UINT8 | RO | 0x01 (1dec) |
1A23:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x23 ()) | UINT32 | RO | 0x6001:23, 16 |
Index 1A24 Analog Input TxPDO-MapSamples 36 Ch.1
1A24:0 | Analog Input TxPDO-MapSamples 36 Ch.1 | PDO Mapping TxPDO 37 | UINT8 | RO | 0x01 (1dec) |
1A24:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x24 ()) | UINT32 | RO | 0x6001:24, 16 |
Index 1A25 Analog Input TxPDO-MapSamples 37 Ch.1
1A25:0 | Analog Input TxPDO-MapSamples 37 Ch.1 | PDO Mapping TxPDO 38 | UINT8 | RO | 0x01 (1dec) |
1A25:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x25 ()) | UINT32 | RO | 0x6001:25, 16 |
Index 1A26 Analog Input TxPDO-MapSamples 38 Ch.1
1A26:0 | Analog Input TxPDO-MapSamples 38 Ch.1 | PDO Mapping TxPDO 39 | UINT8 | RO | 0x01 (1dec) |
1A26:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x26 ()) | UINT32 | RO | 0x6001:26, 16 |
Index 1A27 Analog Input TxPDO-MapSamples 39 Ch.1
1A27:0 | Analog Input TxPDO-MapSamples 39 Ch.1 | PDO Mapping TxPDO 40 | UINT8 | RO | 0x01 (1dec) |
1A27:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x27 ()) | UINT32 | RO | 0x6001:27, 16 |
Index 1A28 Analog Input TxPDO-MapSamples 40 Ch.1
1A28:0 | Analog Input TxPDO-MapSamples 40 Ch.1 | PDO Mapping TxPDO 41 | UINT8 | RO | 0x01 (1dec) |
1A28:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x28 ()) | UINT32 | RO | 0x6001:28, 16 |
Index 1A29 Analog Input TxPDO-MapSamples 41 Ch.1
1A29:0 | Analog Input TxPDO-MapSamples 41 Ch.1 | PDO Mapping TxPDO 42 | UINT8 | RO | 0x01 (1dec) |
1A29:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x29 ()) | UINT32 | RO | 0x6001:29, 16 |
Index 1A2A Analog Input TxPDO-MapSamples 42 Ch.1
1A2A:0 | Analog Input TxPDO-MapSamples 42 Ch.1 | PDO Mapping TxPDO 43 | UINT8 | RO | 0x01 (1dec) |
1A2A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2A ()) | UINT32 | RO | 0x6001:2A, 16 |
Index 1A2B Analog Input TxPDO-MapSamples 43 Ch.1
1A2B:0 | Analog Input TxPDO-MapSamples 43 Ch.1 | PDO Mapping TxPDO 44 | UINT8 | RO | 0x01 (1dec) |
1A2B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2B ()) | UINT32 | RO | 0x6001:2B, 16 |
Index 1A2C Analog Input TxPDO-MapSamples 44 Ch.1
1A2C:0 | Analog Input TxPDO-MapSamples 44 Ch.1 | PDO Mapping TxPDO 45 | UINT8 | RO | 0x01 (1dec) |
1A2C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2C ()) | UINT32 | RO | 0x6001:2C, 16 |
Index 1A2D Analog Input TxPDO-MapSamples 45 Ch.1
1A2D:0 | Analog Input TxPDO-MapSamples 45 Ch.1 | PDO Mapping TxPDO 46 | UINT8 | RO | 0x01 (1dec) |
1A2D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2D ()) | UINT32 | RO | 0x6001:2D, 16 |
Index 1A2E Analog Input TxPDO-MapSamples 46 Ch.1
1A2E:0 | Analog Input TxPDO-MapSamples 46 Ch.1 | PDO Mapping TxPDO 47 | UINT8 | RO | 0x01 (1dec) |
1A2E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2E ()) | UINT32 | RO | 0x6001:2E, 16 |
Index 1A2F Analog Input TxPDO-MapSamples 47 Ch.1
1A2F:0 | Analog Input TxPDO-MapSamples 47 Ch.1 | PDO Mapping TxPDO 48 | UINT8 | RO | 0x01 (1dec) |
1A2F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2F ()) | UINT32 | RO | 0x6001:2F, 16 |
Index 1A30 Analog Input TxPDO-MapSamples 48 Ch.1
1A30:0 | Analog Input TxPDO-MapSamples 48 Ch.1 | PDO Mapping TxPDO 49 | UINT8 | RO | 0x01 (1dec) |
1A30:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x30 ()) | UINT32 | RO | 0x6001:30, 16 |
Index 1A31 Analog Input TxPDO-MapSamples 49 Ch.1
1A31:0 | Analog Input TxPDO-MapSamples 49 Ch.1 | PDO Mapping TxPDO 50 | UINT8 | RO | 0x01 (1dec) |
1A31:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x31 ()) | UINT32 | RO | 0x6001:31, 16 |
Index 1A32 Analog Input TxPDO-MapSamples 50 Ch.1
1A32:0 | Analog Input TxPDO-MapSamples 50 Ch.1 | PDO Mapping TxPDO 51 | UINT8 | RO | 0x01 (1dec) |
1A32:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Samples), entry 0x32 ()) | UINT32 | RO | 0x6001:32, 16 |
Index 1A40 Analog Input TxPDO-MapStatus Ch.2
1A40:0 | Analog Input TxPDO-MapStatus Ch.2 | PDO Mapping TxPDO 65 | UINT8 | RO | 0x09 (9dec) |
1A40:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (Status), entry 0x01 (Underrange)) | UINT32 | RO | 0x6010:01, 1 |
1A40:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (Status), entry 0x02 (Overrange)) | UINT32 | RO | 0x6010:02, 1 |
1A40:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (Status), entry 0x03 (Limit 1)) | UINT32 | RO | 0x6010:03, 2 |
1A40:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (Status), entry 0x05 (Limit 2)) | UINT32 | RO | 0x6010:05, 2 |
1A40:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (Status), entry 0x07 (Error)) | UINT32 | RO | 0x6010:07, 1 |
1A40:06 | SubIndex 006 | 6. PDO Mapping entry (6 bits align) | UINT32 | RO | 0x0000:00, 6 |
1A40:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (Status), entry 0x0E (Sync error)) | UINT32 | RO | 0x6010:0E, 1 |
1A40:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (Status), entry 0x0F (TxPDO State)) | UINT32 | RO | 0x6010:0F, 1 |
1A40:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (Status), entry 0x10 (TxPDO Toggle)) | UINT32 | RO | 0x6010:10, 1 |
Index 1A41 Analog Input TxPDO-MapSamples 1 Ch.2
1A41:0 | Analog Input TxPDO-MapSamples 1 Ch.2 | PDO Mapping TxPDO 66 | UINT8 | RO | 0x01 (1dec) |
1A41:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x01 ()) | UINT32 | RO | 0x6011:01, 16 |
Index 1A42 Analog Input TxPDO-MapSamples 2 Ch.2
1A42:0 | Analog Input TxPDO-MapSamples 2 Ch.2 | PDO Mapping TxPDO 67 | UINT8 | RO | 0x01 (1dec) |
1A42:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x02 ()) | UINT32 | RO | 0x6011:02, 16 |
Index 1A43 Analog Input TxPDO-MapSamples 3 Ch.2
1A43:0 | Analog Input TxPDO-MapSamples 3 Ch.2 | PDO Mapping TxPDO 68 | UINT8 | RO | 0x01 (1dec) |
1A43:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x03 ()) | UINT32 | RO | 0x6011:03, 16 |
Index 1A44 Analog Input TxPDO-MapSamples 4 Ch.2
1A44:0 | Analog Input TxPDO-MapSamples 4 Ch.2 | PDO Mapping TxPDO 69 | UINT8 | RO | 0x01 (1dec) |
1A44:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x04 ()) | UINT32 | RO | 0x6011:04, 16 |
Index 1A45 Analog Input TxPDO-MapSamples 5 Ch.2
1A45:0 | Analog Input TxPDO-MapSamples 5 Ch.2 | PDO Mapping TxPDO 70 | UINT8 | RO | 0x01 (1dec) |
1A45:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x05 ()) | UINT32 | RO | 0x6011:05, 16 |
Index 1A46 Analog Input TxPDO-MapSamples 6 Ch.2
1A46:0 | Analog Input TxPDO-MapSamples 6 Ch.2 | PDO Mapping TxPDO 71 | UINT8 | RO | 0x01 (1dec) |
1A46:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x06 ()) | UINT32 | RO | 0x6011:06, 16 |
Index 1A47 Analog Input TxPDO-MapSamples 7 Ch.2
1A47:0 | Analog Input TxPDO-MapSamples 7 Ch.2 | PDO Mapping TxPDO 72 | UINT8 | RO | 0x01 (1dec) |
1A47:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x07 ()) | UINT32 | RO | 0x6011:07, 16 |
Index 1A48 Analog Input TxPDO-MapSamples 8 Ch.2
1A48:0 | Analog Input TxPDO-MapSamples 8 Ch.2 | PDO Mapping TxPDO 73 | UINT8 | RO | 0x01 (1dec) |
1A48:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples),), entry 0x08 ()) | UINT32 | RO | 0x6011:08, 16 |
Index 1A49 Analog Input TxPDO-MapSamples 9 Ch.2
1A49:0 | Analog Input TxPDO-MapSamples 9 Ch.2 | PDO Mapping TxPDO 74 | UINT8 | RO | 0x01 (1dec) |
1A49:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x09 ()) | UINT32 | RO | 0x6011:09, 16 |
Index 1A4A Analog Input TxPDO-MapSamples 10 Ch.2
1A4A:0 | Analog Input TxPDO-MapSamples 10 Ch.2 | PDO Mapping TxPDO 75 | UINT8 | RO | 0x01 (1dec) |
1A4A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0A ()) | UINT32 | RO | 0x6011:0A, 16 |
Index 1A4B Analog Input TxPDO-MapSamples 11 Ch.2
1A4B:0 | Analog Input TxPDO-MapSamples 11 Ch.2 | PDO Mapping TxPDO 76 | UINT8 | RO | 0x01 (1dec) |
1A4B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0B ()) | UINT32 | RO | 0x6011:0B, 16 |
Index 1A4C Analog Input TxPDO-MapSamples 12 Ch.2
1A4C:0 | Analog Input TxPDO-MapSamples 12 Ch.2 | PDO Mapping TxPDO 77 | UINT8 | RO | 0x01 (1dec) |
1A4C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0C ()) | UINT32 | RO | 0x6011:0C, 16 |
Index 1A4D Analog Input TxPDO-MapSamples 13 Ch.2
1A4D:0 | Analog Input TxPDO-MapSamples 13 Ch.2 | PDO Mapping TxPDO 78 | UINT8 | RO | 0x01 (1dec) |
1A4D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0D ()) | UINT32 | RO | 0x6011:0D, 16 |
Index 1A4E Analog Input TxPDO-MapSamples 14 Ch.2
1A4E:0 | Analog Input TxPDO-MapSamples 14 Ch.2 | PDO Mapping TxPDO 79 | UINT8 | RO | 0x01 (1dec) |
1A4E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0E ()) | UINT32 | RO | 0x6011:0E, 16 |
Index 1A4F Analog Input TxPDO-MapSamples 15 Ch.2
1A4F:0 | Analog Input TxPDO-MapSamples 15 Ch.2 | PDO Mapping TxPDO 80 | UINT8 | RO | 0x01 (1dec) |
1A4F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0F ()) | UINT32 | RO | 0x6011:0F, 16 |
Index 1A50 Analog Input TxPDO-MapSamples 16 Ch.2
1A50:0 | Analog Input TxPDO-MapSamples 16 Ch.2 | PDO Mapping TxPDO 81 | UINT8 | RO | 0x01 (1dec) |
1A50:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x10 ()) | UINT32 | RO | 0x6011:10, 16 |
Index 1A51 Analog Input TxPDO-MapSamples 17 Ch.2
1A51:0 | Analog Input TxPDO-MapSamples 17 Ch.2 | PDO Mapping TxPDO 82 | UINT8 | RO | 0x01 (1dec) |
1A51:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x11 ()) | UINT32 | RO | 0x6011:11, 16 |
Index 1A52 Analog Input TxPDO-MapSamples 18 Ch.2
1A52:0 | Analog Input TxPDO-MapSamples 18 Ch.2 | PDO Mapping TxPDO 83 | UINT8 | RO | 0x01 (1dec) |
1A52:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x12 ()) | UINT32 | RO | 0x6011:12, 16 |
Index 1A53 Analog Input TxPDO-MapSamples 19 Ch.2
1A53:0 | Analog Input TxPDO-MapSamples 19 Ch.2 | PDO Mapping TxPDO 84 | UINT8 | RO | 0x01 (1dec) |
1A53:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x13 ()) | UINT32 | RO | 0x6011:13, 16 |
Index 1A54 Analog Input TxPDO-MapSamples 20 Ch.2
1A54:0 | Analog Input TxPDO-MapSamples 20 Ch.2 | PDO Mapping TxPDO 85 | UINT8 | RO | 0x01 (1dec) |
1A54:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x14 ()) | UINT32 | RO | 0x6011:14, 16 |
Index 1A55 Analog Input TxPDO-MapSamples 21 Ch.2
1A55:0 | Analog Input TxPDO-MapSamples 21 Ch.2 | PDO Mapping TxPDO 86 | UINT8 | RO | 0x01 (1dec) |
1A55:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x15 ()) | UINT32 | RO | 0x6011:15, 16 |
Index 1A56 Analog Input TxPDO-MapSamples 22 Ch.2
1A56:0 | Analog Input TxPDO-MapSamples 22 Ch.2 | PDO Mapping TxPDO 87 | UINT8 | RO | 0x01 (1dec) |
1A56:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x16 ()) | UINT32 | RO | 0x6011:16, 16 |
Index 1A57 Analog Input TxPDO-MapSamples 23 Ch.2
1A57:0 | Analog Input TxPDO-MapSamples 23 Ch.2 | PDO Mapping TxPDO 88 | UINT8 | RO | 0x01 (1dec) |
1A57:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x17 ()) | UINT32 | RO | 0x6011:17, 16 |
Index 1A58 Analog Input TxPDO-MapSamples 24 Ch.2
1A58:0 | Analog Input TxPDO-MapSamples 24 Ch.2 | PDO Mapping TxPDO 89 | UINT8 | RO | 0x01 (1dec) |
1A58:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x18 ()) | UINT32 | RO | 0x6011:18, 16 |
Index 1A59 Analog Input TxPDO-MapSamples 25 Ch.2
1A59:0 | Analog Input TxPDO-MapSamples 25 Ch.2 | PDO Mapping TxPDO 90 | UINT8 | RO | 0x01 (1dec) |
1A59:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x19 ()) | UINT32 | RO | 0x6011:19, 16 |
Index 1A5A Analog Input TxPDO-MapSamples 26 Ch.2
1A5A:0 | Analog Input TxPDO-MapSamples 26 Ch.2 | PDO Mapping TxPDO 91 | UINT8 | RO | 0x01 (1dec) |
1A5A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1A ()) | UINT32 | RO | 0x6011:1A, 16 |
Index 1A5B Analog Input TxPDO-MapSamples 27 Ch.2
1A5B:0 | Analog Input TxPDO-MapSamples 27 Ch.2 | PDO Mapping TxPDO 92 | UINT8 | RO | 0x01 (1dec) |
1A5B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1B ()) | UINT32 | RO | 0x6011:1B, 16 |
Index 1A5C Analog Input TxPDO-MapSamples 28 Ch.2
1A5C:0 | Analog Input TxPDO-MapSamples 28 Ch.2 | PDO Mapping TxPDO 93 | UINT8 | RO | 0x01 (1dec) |
1A5C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1C ()) | UINT32 | RO | 0x6011:1C, 16 |
Index 1A5D Analog Input TxPDO-MapSamples 29 Ch.2
1A5D:0 | Analog Input TxPDO-MapSamples 29 Ch.2 | PDO Mapping TxPDO 94 | UINT8 | RO | 0x01 (1dec) |
1A5D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1D ()) | UINT32 | RO | 0x6011:1D, 16 |
Index 1A5E Analog Input TxPDO-MapSamples 30 Ch.2
1A5E:0 | Analog Input TxPDO-MapSamples 30 Ch.2 | PDO Mapping TxPDO 95 | UINT8 | RO | 0x01 (1dec) |
1A5E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1E ()) | UINT32 | RO | 0x6011:1E, 16 |
Index 1A5F Analog Input TxPDO-MapSamples 31 Ch.2
1A5F:0 | Analog Input TxPDO-MapSamples 31 Ch.2 | PDO Mapping TxPDO 96 | UINT8 | RO | 0x01 (1dec) |
1A5F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1F ()) | UINT32 | RO | 0x6011:1F, 16 |
Index 1A60 Analog Input TxPDO-MapSamples 32 Ch.2
1A60:0 | Analog Input TxPDO-MapSamples 32 Ch.2 | PDO Mapping TxPDO 97 | UINT8 | RO | 0x01 (1dec) |
1A60:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x20 ()) | UINT32 | RO | 0x6011:20, 16 |
Index 1A61 Analog Input TxPDO-MapSamples 33 Ch.2
1A61:0 | Analog Input TxPDO-MapSamples 33 Ch.2 | PDO Mapping TxPDO 98 | UINT8 | RO | 0x01 (1dec) |
1A61:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x21 ()) | UINT32 | RO | 0x6011:21, 16 |
Index 1A62 Analog Input TxPDO-MapSamples 34 Ch.2
1A62:0 | Analog Input TxPDO-MapSamples 34 Ch.2 | PDO Mapping TxPDO 99 | UINT8 | RO | 0x01 (1dec) |
1A62:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x22 ()) | UINT32 | RO | 0x6011:22, 16 |
Index 1A63 Analog Input TxPDO-MapSamples 35 Ch.2
1A63:0 | Analog Input TxPDO-MapSamples 35 Ch.2 | PDO Mapping TxPDO 100 | UINT8 | RO | 0x01 (1dec) |
1A63:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x23 ()) | UINT32 | RO | 0x6011:23, 16 |
Index 1A64 Analog Input TxPDO-MapSamples 36 Ch.2
1A64:0 | Analog Input TxPDO-MapSamples 36 Ch.2 | PDO Mapping TxPDO 101 | UINT8 | RO | 0x01 (1dec) |
1A64:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x24 ()) | UINT32 | RO | 0x6011:24, 16 |
Index 1A65 Analog Input TxPDO-MapSamples 37 Ch.2
1A65:0 | Analog Input TxPDO-MapSamples 37 Ch.2 | PDO Mapping TxPDO 102 | UINT8 | RO | 0x01 (1dec) |
1A65:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x25 ()) | UINT32 | RO | 0x6011:25, 16 |
Index 1A66 Analog Input TxPDO-MapSamples 38 Ch.2
1A66:0 | Analog Input TxPDO-MapSamples 38 Ch.2 | PDO Mapping TxPDO 103 | UINT8 | RO | 0x01 (1dec) |
1A66:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x26 ()) | UINT32 | RO | 0x6011:26, 16 |
Index 1A67 Analog Input TxPDO-MapSamples 39 Ch.2
1A67:0 | Analog Input TxPDO-MapSamples 39 Ch.2 | PDO Mapping TxPDO 104 | UINT8 | RO | 0x01 (1dec) |
1A67:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x27 ()) | UINT32 | RO | 0x6011:27, 16 |
Index 1A68 Analog Input TxPDO-MapSamples 40 Ch.2
1A68:0 | Analog Input TxPDO-MapSamples 40 Ch.2 | PDO Mapping TxPDO 105 | UINT8 | RO | 0x01 (1dec) |
1A68:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x28 ()) | UINT32 | RO | 0x6011:28, 16 |
Index 1A69 Analog Input TxPDO-MapSamples 41 Ch.2
1A69:0 | Analog Input TxPDO-MapSamples 41 Ch.2 | PDO Mapping TxPDO 106 | UINT8 | RO | 0x01 (1dec) |
1A69:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x29 ()) | UINT32 | RO | 0x6011:29, 16 |
Index 1A6A Analog Input TxPDO-MapSamples 42 Ch.2
1A6A:0 | Analog Input TxPDO-MapSamples 42 Ch.2 | PDO Mapping TxPDO 107 | UINT8 | RO | 0x01 (1dec) |
1A6A:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2A ()) | UINT32 | RO | 0x6011:2A, 16 |
Index 1A6B Analog Input TxPDO-MapSamples 43 Ch.2
1A6B:0 | Analog Input TxPDO-MapSamples 43 Ch.2 | PDO Mapping TxPDO 108 | UINT8 | RO | 0x01 (1dec) |
1A6B:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2B ()) | UINT32 | RO | 0x6011:2B, 16 |
Index 1A6C Analog Input TxPDO-MapSamples 44 Ch.2
1A6C:0 | Analog Input TxPDO-MapSamples 44 Ch.2 | PDO Mapping TxPDO 109 | UINT8 | RO | 0x01 (1dec) |
1A6C:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2C ()) | UINT32 | RO | 0x6011:2C, 16 |
Index 1A6D Analog Input TxPDO-MapSamples 45 Ch.2
1A6D:0 | Analog Input TxPDO-MapSamples 45 Ch.2 | PDO Mapping TxPDO 110 | UINT8 | RO | 0x01 (1dec) |
1A6D:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2D ()) | UINT32 | RO | 0x6011:2D, 16 |
Index 1A6E Analog Input TxPDO-MapSamples 46 Ch.2
1A6E:0 | Analog Input TxPDO-MapSamples 46 Ch.2 | PDO Mapping TxPDO 111 | UINT8 | RO | 0x01 (1dec) |
1A6E:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2E ()) | UINT32 | RO | 0x6011:2E, 16 |
Index 1A6F Analog Input TxPDO-MapSamples 47 Ch.2
1A6F:0 | Analog Input TxPDO-MapSamples 47 Ch.2 | PDO Mapping TxPDO 112 | UINT8 | RO | 0x01 (1dec) |
1A6F:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2F ()) | UINT32 | RO | 0x6011:2F, 16 |
Index 1A70 Analog Input TxPDO-MapSamples 48 Ch.2
1A70:0 | Analog Input TxPDO-MapSamples 48 Ch.2 | PDO Mapping TxPDO 113 | UINT8 | RO | 0x01 (1dec) |
1A70:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x30 ()) | UINT32 | RO | 0x6011:30, 16 |
Index 1A71 Analog Input TxPDO-MapSamples 49 Ch.2
1A71:0 | Analog Input TxPDO-MapSamples 49 Ch.2 | PDO Mapping TxPDO 114 | UINT8 | RO | 0x01 (1dec) |
1A71:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Samples), entry 0x31 ()) | UINT32 | RO | 0x6011:31, 16 |
Index 1A72 Analog Input TxPDO-MapSamples 50 Ch.2
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1A72:0 |
Analog Input TxPDO-MapSamples 50 Ch.2 |
PDO Mapping TxPDO 115 |
UINT8 |
RO |
0x01 (1dec) |
1A72:01 |
SubIndex 001 |
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x32 ()) |
UINT32 |
RO |
0x6011:32, 16 |
Index 1A80 Analog Input Timestamp TxPDO-Map NextSync1Time
1A80:0 | Analog Input Timestamp TxPDO-Map NextSync1Time | PDO Mapping TxPDO 129 | UINT8 | RO | 0x01 (1dec) |
1A80:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6020 (NextSync1Time), entry 0x01 ()) | UINT32 | RO | 0x6020:01, 64 |
Index 1A81 Analog Input Timestamp TxPDO-Map Sample Count
1A81:0 | Analog Input Timestamp TxPDO-Map Sample Count | PDO Mapping TxPDO 130 | UINT8 | RO | 0x01 (1dec) |
1A81:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6021 (SampleCount), entry 0x01 (Sample Count)) | UINT32 | RO | 0x6021:01, 16 |
Index 1C00 Sync manager type
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C00:0 |
Sync manager type |
Using the sync managers |
UINT8 |
RO |
0x04 (4dec) |
1C00:01 |
SubIndex 001 |
Sync-Manager Type Channel 1: Mailbox Write |
UINT8 |
RO |
0x01 (1dec) |
1C00:02 |
SubIndex 002 |
Sync-Manager Type Channel 2: Mailbox Read |
UINT8 |
RO |
0x02 (2dec) |
1C00:03 |
SubIndex 003 |
Sync-Manager Type Channel 3: Process Data Write (Outputs) |
UINT8 |
RO |
0x03 (3dec) |
1C00:04 |
SubIndex 004 |
Sync-Manager Type Channel 4: Process Data Read (Inputs) |
UINT8 |
RO |
0x04 (4dec) |
Index 1C12 RxPDO assign
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
1C12:0 |
RxPDO assign |
PDO Assign Outputs |
UINT8 |
RW |
0x00 (0dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x06 (6dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A00 (6656dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A01 (6657dec) |
1C13:03 | Subindex 003 | 3. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A40 (6720dec) |
1C13:04 | Subindex 004 | 4. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A41 (6721dec) |
1C13:05 | Subindex 005 | 5. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A80 (6784dec) |
1C13:06 | Subindex 006 | 6. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A81 (6785dec) |
1C13:07 | Subindex 007 | 7. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
1C13:69 | Subindex 105 | 105. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x0000 (0dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0022 (34dec) |
1C33:02 | Cycle time | as 0x1C32:02 | UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0x0C06 (3078dec) |
1C33:05 | Minimum cycle time | as 0x1C32:05 | UINT32 | RO | 0x00002710 (10000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Command | as 0x1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:0B | SM event missed counter | as 0x1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 0x1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 0x1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 0x1C32:32 | BOOLEAN | RO | 0x00 (0dec) |
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F000:0 |
Modular device profile |
General information for the modular device profile |
UINT8 |
RO |
0x02 (2dec) |
F000:01 |
Module index distance |
Index distance of the objects of the individual channels |
UINT16 |
RO |
0x0010 (16dec) |
F000:02 |
Maximum number of modules |
Number of channels |
UINT16 |
RO |
0x0003 (3dec) |
Index F008 Code word
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F008:0 |
Code word |
reserved |
UINT32 |
RW |
0x00000000 (0dec) |
Index F010 Module list
Index (hex) |
Name |
Meaning |
Data type |
Flags |
Default |
F010:0 |
Module list |
Maximum subindex |
UINT8 |
RW |
0x03 (3dec) |
F010:01 |
SubIndex 001 |
Profile AI |
UINT32 |
RW |
0x0000012C (300dec) |
F010:02 |
SubIndex 002 |
Profile AI |
UINT32 |
RW |
F010:03 |
SubIndex 003 |
Profile AI |
UINT32 |
RW |