Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Supply voltages | |
Connection | See EtherCAT P connection |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current: IS,sum |
max. 3 A |
Current consumption from US |
100 mA |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP sum current: IP,sum |
max. 3 A |
Current consumption from UP | None. UP is only forwarded. |
RTD inputs | |
Number |
4 |
Connectors |
4 x M12 socket |
Sensor types |
Connection technology |
Electrical isolation |
The measuring channels have a common isolated ground potential. |
Measuring current RL+, RL- |
Max. 0.5 mA, load-dependent |
Measuring range |
Platinum RTD: -200…+850 °C Nickel RTD: -60…+250 °C (Ni120: -60…+320 °C) Resistance: 0…4095 Ω |
Measuring error |
max. ±0.5 K (Pt sensors in 4-wire connection) |
Digital resolution |
16 Bit |
Value of an LSB |
Temperature measurement: Resistance measurement: |
Filter |
Digital filter. Cut-off frequency parameterizable: 5 Hz … 30 kHz.. |
Conversion time |
2…800 ms, depending on the parameterization Default: approx. 85 ms |
Diagnostics |
Environmental conditions | |
Ambient temperature during operation | -25 … +60 °C |
Ambient temperature during storage | -40 … +85 °C |
Vibration resistance, shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 |
Protection class | IP65, IP66, IP67 (conforms to EN 60529) |
Housing data | |
Dimensions W x H x D | 30 mm x 126 mm x 26.5 mm (without connectors) |
Weight | approx. 165 g |
Material |
PA6 (polyamide) |
Approvals / markings | |
Approvals / markings *) | CE, cULus |
Additional tests
The devices have undergone the following additional tests:
Test | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |