Objects to be parameterized during commissioning
Index 1011: Restore default parameters
Index (hex)
Meaning
Data type
Flags
Default
1011:0
UINT8
RO
0x01 (1dec)
1011:01
SubIndex 001
If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state.
UINT32
RW
0x00000000 (0dec)
Index 8000: RTD Settings Ch.1
Index (hex)
Meaning
Data type
Flags
Default
8000:0
RTD Settings Ch.1
Maximum subindex
UINT8
RO
0x1B (27dec)
8000:01
Enable user scale
Activates user scaling
BOOLEAN
RW
0x00 (0dec)
8000:02
Presentation
Presentation of the measured value
BIT3
RW
0x00 (0dec)
0
Signed, in two's complement
1
Most significant bit as sign
2
High-resolution (1/100 °C steps)
8000:05
Siemens bits
The S5 bits are displayed in the three low-order bits
BOOLEAN
RW
0x00 (0dec)
8000:06
Enable filter
Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x00 (0dec)
8000:07
Enable limit 1
Activates limit check for limit 1
BOOLEAN
RW
0x00 (0dec)
8000:08
Enable limit 2
Activates limit check for limit 2
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable user calibration
Activates user calibration
BOOLEAN
RW
0x00 (0dec)
8000:0B
Enable vendor calibration
Activates vendor calibration
BOOLEAN
RW
0x01 (1dec)
8000:0E
Swap limit bits
Swaps the two limit bits, in order to achieve compatibility with older hardware versions.
BOOLEAN
RW
0x00 (0dec)
8000:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
8000:12
User scale gain
Gain of the user scaling
INT32
RW
0x00010000 (65536dec)
8000:13
Limit 1
Value for limit 1
INT16
RW
0x0000 (0dec)
8000:14
Limit 2
Value for limit 2
INT16
RW
0x0000 (0dec)
8000:15
Filter settings
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz
1
60 Hz
2
100 Hz
3
500 Hz
4
1 kHz
5
2 kHz
6
3.75 kHz
7
7.5 kHz
8
15 kHz
9
30 kHz
10
5 Hz
11
10 Hz
8000:16
Calibration interval
reserved
UINT16
RW
0x0000 (0dec)
8000:17
User calibration offset
INT16
RW
0x0000 (0dec)
8000:18
User calibration gain
Gain of the user calibration
UINT16
RW
0x4000 (16384dec)
8000:19
RTD element
Sensor type
UINT16
RW
0x0000 (0dec)
0
Pt100
1
Ni100
2
Pt1000
3
Pt500
4
Pt200
5
Ni1000
6
Ni1000 (Siemens)
7
Ni120
8
Resistance measurement with 1/16 ohm resolution
9
Resistance measurement with 1/64 ohm resolution
Index (hex)
Meaning
Data type
Flags
Default
8000:1A
Connection technology
Connection technology:
UINT16
RW
0x0000 (0dec)
0
2-wire
1
3-wire
2
4-wire
3
No sensor connected (only supported by hardware version 00):
This setting skips the whole measurement, thus speeding up the data acquisition for the other channels. The green status LED of the respective channel remains lit. The error bit of a deactivated channel is canceled and no longer set.
8000:1B
Wire calibration 1/32 Ohm
Only for 2-wire measurements:
contains the resistance of the supply line for the temperature sensor (in 1/32 ohm).
INT16
RW
0x0000 (0dec)
Index 8010: RTD Settings Ch.2
Index (hex)
Meaning
Data type
Flags
Default
8010:0
RTD Settings Ch.2
Maximum subindex
UINT8
RO
0x1B (27dec)
8010:01
Enable user scale
BOOLEAN
RW
0x00 (0dec)
8010:02
Presentation
BIT3
RW
0x00 (0dec)
0
1
2
8010:05
Siemens bits
BOOLEAN
RW
0x00 (0dec)
8010:06
Enable filter
BOOLEAN
RW
0x00 (0dec)
8010:07
Enable limit 1
BOOLEAN
RW
0x00 (0dec)
8010:08
Enable limit 2
BOOLEAN
RW
0x00 (0dec)
8010:0A
BOOLEAN
RW
0x00 (0dec)
8010:0B
Activates manufacturer calibration
BOOLEAN
RW
0x01 (1dec)
8010:0E
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8010:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
8010:12
User scale gain
INT32
RW
8010:13
Limit 1
Value for limit 1
INT16
RW
0x0000 (0dec)
8010:14
Limit 2
Value for limit 2
INT16
RW
0x0000 (0dec)
8010:15
Filter settings
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz
1
60 Hz
2
100 Hz
3
500 Hz
4
1 kHz,
5
2 kHz
6
3.75 kHz
7
7.5 kHz
8
15 kHz
9
30 kHz
10
5 Hz
11
10 Hz
8010:16
reserved
UINT16
RW
0x0000 (0dec)
8010:17
INT16
RW
0x0000 (0dec)
8010:18
UINT16
RW
0x4000 (16384dec)
Index (hex)
Meaning
Data type
Flags
Default
8010:19
RTD element
Sensor type
UINT16
RW
0x0000 (0dec)
0
Pt100
1
Ni100
2
Pt1000
3
Pt500
4
Pt200
5
Ni1000
6
Ni1000 (Siemens)
7
Ni120
8
9
8010:1A
UINT16
RW
0x0000 (0dec)
0
2-wire
1
3-wire
2
4-wire
3
This setting skips the whole measurement, thus speeding up the data acquisition for the other channels. The green status LED of the respective channel remains lit. The error bit of a deactivated channel is cancelled and no longer set.
8010:1B
INT16
RW
0x0000 (0dec)
Index 8020: RTD Settings Ch.3
Index (hex)
Meaning
Data type
Flags
Default
8020:0
RTD Settings Ch.3
Maximum subindex
UINT8
RO
0x1B (27dec)
8020:01
Enable user scale
BOOLEAN
RW
0x00 (0dec)
8020:02
Presentation
BIT3
RW
0x00 (0dec)
0
1
2
8020:05
Siemens bits
BOOLEAN
RW
0x00 (0dec)
8020:06
Enable filter
BOOLEAN
RW
0x00 (0dec)
8020:07
Enable limit 1
BOOLEAN
RW
0x00 (0dec)
8020:08
Enable limit 2
BOOLEAN
RW
0x00 (0dec)
8020:0A
BOOLEAN
RW
0x00 (0dec)
8020:0B
BOOLEAN
RW
0x01 (1dec)
8020:0E
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8020:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
8020:12
User scale gain
INT32
RW
8020:13
Limit 1
Value for limit 1
INT16
RW
0x0000 (0dec)
8020:14
Limit 2
Value for limit 2
INT16
RW
0x0000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
8020:15
Filter settings
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz
1
60 Hz
2
100 Hz
3
500 Hz
4
1 kHz,
5
2 kHz
6
3.75 kHz
7
7.5 kHz
8
15 kHz
9
30 kHz
10
5 Hz
11
10 Hz
8020:16
reserved
UINT16
RW
0x0000 (0dec)
8020:17
INT16
RW
0x0000 (0dec)
8020:18
UINT16
RW
0x4000 (16384dec)
8020:19
RTD element
Sensor type
UINT16
RW
0x0000 (0dec)
0
Pt100
1
Ni100
2
Pt1000
3
Pt500
4
Pt200
5
Ni1000
6
Ni1000 (Siemens)
7
Ni120
8
9
8020:1A
UINT16
RW
0x0000 (0dec)
0
2-wire
1
3-wire
2
4-wire
3
8020:1B
INT16
RW
0x0000 (0dec)
Index 8030: RTD Settings Ch.4
Index (hex)
Meaning
Data type
Flags
Default
8030:0
RTD Settings Ch.4
Maximum subindex
UINT8
RO
0x1B (27dec)
8030:01
Enable user scale
BOOLEAN
RW
0x00 (0dec)
8030:02
Presentation
BIT3
RW
0x00 (0dec)
0
1
2
8030:05
Siemens bits
BOOLEAN
RW
0x00 (0dec)
8030:06
Enable filter
BOOLEAN
RW
0x00 (0dec)
8030:07
Enable limit 1
BOOLEAN
RW
0x00 (0dec)
8030:08
Enable limit 2
BOOLEAN
RW
0x00 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
8030:0A
BOOLEAN
RW
0x00 (0dec)
8030:0B
BOOLEAN
RW
0x01 (1dec)
8030:0E
Swap limit bits
BOOLEAN
RW
0x00 (0dec)
8030:11
User scale offset
User scaling offset
INT16
RW
0x0000 (0dec)
8030:12
User scale gain
INT32
RW
8030:13
Limit 1
Value for limit 1
INT16
RW
0x0000 (0dec)
8030:14
Limit 2
Value for limit 2
INT16
RW
0x0000 (0dec)
8030:15
Filter settings
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz
1
60 Hz
2
100 Hz
3
500 Hz
4
1 kHz,
5
2 kHz
6
3.75 kHz
7
7.5 kHz
8
15 kHz
9
30 kHz
10
5 Hz
11
10 Hz
8030:16
reserved
UINT16
RW
0x0000 (0dec)
8030:17
INT16
RW
0x0000 (0dec)
8030:18
UINT16
RW
0x4000 (16384dec)
8030:19
RTD element
Sensor type
UINT16
RW
0x0000 (0dec)
0
Pt100
1
Ni100
2
Pt1000
3
Pt500
4
Pt200
5
Ni1000
6
Ni1000 (Siemens)
7
Ni120
8
9
8030:1A
UINT16
RW
0x0000 (0dec)
0
2-wire
1
3-wire
2
4-wire
3
8030:1B
INT16
RW
0x0000 (0dec)