ZS2001 digital inputs
ZS2001 digital inputs 1:
The ZS2001 connectors are not included in the scope of delivery. See chapter Accessories.
Notice
Different pin numbering
Danger of confusion: The pins are numbered differently on the box than on the ZS2001.
Pin
Imprint on the ZS2001
Us1
24
Sensor power supply: 24 V DC from US
1
0
Input 1
2
1
Input 2
3
2
Input 3
4
3
Input 4
5
4
Input 5
6
5
Input 6
7
6
Input 7
8
7
Input 8
GNDs
0 V
GNDS
Use the output voltage Us1 as supply voltage for the sensors. Make sure that the total of the supply currents of all connected sensors does not exceed the total current of 0.5 A.
ZS2001-0004 has three rows with ten terminal contacts each. The first row is occupied as shown in the table. The second and third rows are designed to distribute the supply voltage and ground. See connection examples.
Connection examples
ZS2001 digital inputs 2:
ZS2001 digital inputs 3:
ZS2001-0001
ZS2002-0002
ZS2001-0004
The diagram shows the connection of 8 sensors in single-wire technology as well as one sensor in two-wire and one sensor in three-wire technology.
Note for ZS2001-0004 connector: Two jumpers [1] are required to distribute the supply voltage and GND.