Configure overload switch-off
You can configure the overload switch-off for each output voltage individually.
The configuration of the overload switch-off is similar to the selection of a fuse: you select the nominal current and the tripping characteristic.
The nominal current can be set between 1000 and 4000 mA.
Connection | Nominal current in mA | Tripping characteristic |
1 | 8000:12 „Nominal Current Us“ 8000:13 „Nominal Current Up“ | 8000:11 „Characteristic“ |
2 | 8010:12 „Nominal Current Us“ 8010:13 „Nominal Current Up“ | 8010:11 „Characteristic“ |
3 | 8020:12 „Nominal Current Us“ 8020:13 „Nominal Current Up“ | 8020:11 „Characteristic“ |
4 | 8030:12 „Nominal Current Us“ 8030:13 „Nominal Current Up“ | 8030:11 „Characteristic“ |
If the nominal current is exceeded, the status bit "Warning" is set.
Examples of maximum switch-off times
The following table shows the maximum switch-off time of the overload switch-off for different currents and tripping characteristics.
![]() | Shorter switch-off time with current limitation The switch-off times shown only apply to output currents below the current limit. If the current limitation is active, the output may be switched off earlier than the configured switch-off time. |
EP92x4-0023 from firmware 20 and EP92x4-0024:
% of the nominal current | Very fast acting | Fast acting | Slow acting | Time delay |
105 % | 3600 s | 3600 s | 3600 s | 3600 s |
135 % | 420 s | 3600 s | 3600 s | 3600 s |
200 % | 0.5 s | 20 s | 20 s | 100 s |
300 % | 0.02 s | 0.1 s | 1 s | 3 s |
EP92x4-0023 with firmware below 20:
Nominal current |
Very fast acting |
Fast acting |
Slow acting |
Time delay |
100 % |
1 h |
110 % |
1 h |
4 h |
120 % |
7 min |
4 h |
150 % |
30 s |
30 min |
1 h |
4 h |
210 % |
500 ms |
20 s |
20 s |
100 s |
275 % |
500 ms |
1 s |
20 s |
10 s |
300 % |
20 ms |
100 ms |
1 s |
3 s |