Overload protection
Each supply voltage output X60 ... X63 has overload protection for the output voltages US and UP. If an output voltage is switched off due to overload, all other output voltages remain switched on.
The overload protection comprises two protection mechanisms:
- Overload switch-off, configurable
 - Current limitation, not configurable
If an output current exceeds the nominal current (factory setting 4 A), the status bit "Warning" is set. In this range, the protection mechanisms are active as follows:
- Below 4.4 A, only the overload switch-off is active. It switches off the respective output voltage according to the configured tripping characteristic.
See chapter Configure overload switch-off. - At 4.4 A, the current limitation limits the current.
The overload switch-off and current limiter are now active simultaneously. The output voltage is either switched off by the overload switch-off according to the switch-off characteristic or by the starting current limitation in the event of thermal overload.
You can use the data logger to determine which of the two protection mechanisms has switched off an output voltage. See chapter Troubleshooting with the data logger.
Overload message
If the overload protection has switched off an output voltage, this is reported as follows:
- The status bit "Error Us" or "Error Up" of the output is set.
 - The output voltage status LED of the output lights up red.
Resetting an error state
If an output voltage has been switched off by the overload protection, it can be enabled again by one of the following actions:
- a positive edge at the output variable "DPO Inputs Channel n" > "Reset Ux" of the respective supply voltage output.
 - a positive edge on the output variable "DPO Outputs Device" > "Global Reset"
This also resets the status bit "Error".