Calibration and scaling
There are three calibration and scaling functions in the signal path:
User scale
The user scale is disabled in the factory setting. It can be enabled via
index 0x80B0:01 "Enable user scale".
Parameterization is carried out via the indices:
0x80B0:11 (offset user scale and 0x80B0:12 (gain user scale).
User calibration
Notice
The user calibration affects the measuring range monitoring.
Incorrect calibration coefficients can lead to the Status bits and Status LEDs no longer behaving as expected; see Output range monitoring.
The user calibration is disabled in the factory setting. It can be enabled via
Index 0x80B0:07 "Enable user calibration".
0x80B0:17 (offset user calibration) and 0x80B0:18 (gain user calibration).
Vendor calibration
The vendor calibration is enabled in the factory setting. It can be disabled via
Index 0x80B0:08 "Enable vendor calibration".
The parameterization of the vendor calibration is carried out via the indices: 0x80BF:01 (offset vendor calibration) and 0x80BF:02 (gain vendor calibration).
Calibration and scaling 1:
Output error with disabled vendor calibration
  • If you use the user calibration, it may be a good idea to disable the vendor calibration.
  • The vendor reserves the right to carry out the basic calibration of the terminals. Therefore, the vendor calibration cannot be changed.
Summary
Calibration / scaling
Status
Conversion
Meaning
User scale
enabled:
0x80B0:01 = TRUE
YSC= YS1 x AS x 2-16 + BS
YSC: Value after user scale
YS1: Value before user scale
AS: Gain user scale (0x80B0:12)
BS: Offset user scale (0x80B0:11)
Disabled (default):
0x80B0:01 = FALSE
YSC = YS1
User calibration
enabled:
0x80A0:07 = TRUE
XDAC = YSC x AA x 2-20 + BA
XDAC: Output value with enabled user calibration with:
BA: Offset user calibration (0x80B0:15)
AA: Gain user calibration (0x80B0:16)
Vendor calibration
enabled (default):
0x80B0:08 = TRUE
XDAC = YSC x AH x 2-16 + BH
XDAC: Output value with enabled vendor calibration with:
BH: Offset vendor calibration (0x80BF:01)
AH: Gain vendor calibration (0x80BF:02)
No calibration
0x80B0:01 = FALSE,
0x80B0:08 = FALSE,
0x80A0:07 = FALSE
XDAC = YSC
XDAC: Output value if vendor and user calibration are disabled.