Current measurement "AI_1xC" measuring ranges
1. Set the measuring range via index 0x80AD:11 “Input type”
(see table “Measuring ranges and scaling type”).
2. Select the scaling type via index 0x80AD:12 “Scaler”:
Scaling type
0x80AD:12
"Scaler"
Resolution 1 LSB
Meaning
0x0000 (0dec)
(pre-set)
Extended Range
Current measurement "AI_1xC" measuring ranges 1:
This type of scaling allows the nominal measuring range to be exceeded or undershot by approx. 7 %.
  • Technical measuring range: The technically usable range is -107 % to +107 % of the respective full scale value.
  • Nominal measuring range: For the “Extended Range”, the PDO value ±30518 (0x7736) is defined as ±100 % for 16 bits.
0x0003 (3dec)
Legacy Range
Current measurement "AI_1xC" measuring ranges 2:
This scaling type shows the range from -100 % to +100 %.
  • +100 % corresponds to +32767
  • -100 % corresponds to -32768
Nominal measuring range = Technical measuring range
0x80AD:11
“Input type”
Current measuring ranges
Extended Range
0x80AD:12 "Scaler" = 0x0000 (0dec)
Legacy Range
0x80AD:12 "Scaler" = 0x0003 (3dec)
Full scale value (FSV)
0x0011 (17dec)
-21.474 … +21.474 mA
-20 … +20 mA
20 mA
0x0012 (18dec)
0 … +21.474 mA
0 … +20 mA
20 mA
0x0013 (19dec)
0 … +21.474 mA
4 … +20 mA
20 mA
The following status bits indicate that the measuring range has been exceeded:
A complete description of these status bits can be found in the chapter Measuring range monitoring.
Schematic diagram of the measuring ranges
Current measurement "AI_1xC" measuring ranges 3: