Configuration objects
Index 2n02 Amplifier Settings Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
USINT
RO
0x7A (122dec)
12
Current loop integral time
Integral component of current controller.
Unit: 0.1 ms
UINT
RW
0xA (10dec)
13
Current loop proportional gain
Proportional component of current controller.
Unit: 0.1 V/A
UINT
RW
0x64 (100dec)
14
Velocity loop integral time
Integral component of velocity controller.
Unit: 0.1 ms
UDINT
RW
0x96 (150dec)
15
Velocity loop proportional gain
Proportional component of velocity controller.
Unit: mA / (rad/s)
UDINT
RW
0x14 (20dec)
17
Position loop proportional gain
Proportional component position controller.
Unit: (rad/s) / rad
UDINT
RW
0xA (10dec)
29
Amplifier I2T warn level
I²T model warning threshold.
Unit: %
USINT
RW
0x50 (80dec)
2A
Amplifier I2T error level
I²T model error threshold.
Unit: %
USINT
RW
0x69 (105dec)
31
Velocity limitation
Velocity limitation. If a gear ratio is configured (parameter 6091/6891), this limit value refers to the load side.
Unit: 1/min
UDINT
RW
0x186A0 (100000dec)
32
Short circuit brake duration max
Maximum holding time for anchor short-circuit braking
Unit: ms
UINT
RW
0x3E8 (1000dec)
33
Stand still window
Standstill window
Unit: 1/min
UINT
RW
0x1 (1dec)
49
Halt ramp deceleration
Halt ramp deceleration.
Unit: 0.1 rad / s²
UDINT
RW
0xF570 (62832dec)
54
Feature bits
Reserved. Please do not change.
UDINT
RW
0x0 (0dec)
55
Select info data 1
Possible values:
  • 2dec: DC link voltage (mV)
  • 4dec: PCB temperature (0.1 °C)
  • 7dec: I2T Motor
  • 8dec: I2T Amplifier
  • 10dec: Digital inputs
USINT
RW
0x2 (2dec)
56
Select info data 2
Possible values:
  • 7dec: I2T Motor
USINT
RW
0x4 (4dec)
57
Velocity feed forward gain
Scaling factor for velocity feedforward from the position interpolator.
USINT
RW
0x64 (100dec)
58
Select info data 3
Possible values:
  • 7dec: I2T Motor
USINT
RW
0x7 (7dec)
59
Error suppression mask
UDINT
RW
0x0 (0dec)
Subindex (hex)
Meaning
Data Type
Flags
Default
5F
Sensorless observer bandwidth
Observer bandwidth for sensorless control
Unit: Hz
UINT
RW
0xC8 (200dec)
62
Position loop deadband window
Deadband window of the position controller
Unit: increments
UDINT
RW
0x0 (0dec)
64
Commutation type
Possible values:
  • 5dec: Sensorless FOC with forced startup
USINT
RW
0x5 (5dec)
6D
Torque feed forward gain
Internal torque feedforward: scaling factor
UDINT
RW
0x0 (0dec)
6E
Torque feed forward filter time
Internal torque feedforward: filter time.
Unit: 0.1 ms
UDINT
RW
0xA (10dec)
71
Error Code Options
Choice of diagnostic messages that are displayed in 0x6n3F “Error code” (PDO mapping possible)
Possible values:
  • 1dec: Display Errors
  • 3dec: Display Errors Warnings
  • 7dec: Display Errors Warnings Infos
USINT
RW
0x7 (7dec)
72
Stand still torque limitation
Output standstill holding current for sensorless control
UINT
RW
0x1F4 (500dec)
73
Acceleration limitation
Maximum acceleration (setpoint limit)
Unit: 0.1 rad/s²
UDINT
RW
0xF570 (62832dec)
79
Sensorless Startup Current Scaling
Motor starting current for sensorless control. The current configured here is output at low speeds (“forced startup” phase).
Specified in parts per thousand of the rated motor current.
I.e. 1000 = rated motor current
UINT
RW
0x2EE (750dec)
7A
Sensorless Stall Reaction
Reaction to a detected commutation error (Motor Stall) in sensorless control.
Possible values:
  • 0dec: Stop motor with drive error
  • 1dec: Restart motor
  • 255dec: Disable Stall Monitoring
USINT
RW
0x0 (0dec)
Index 2n03 Motor Settings Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Motor Settings Ch.x
USINT
RO
0x34 (52dec)
11
Max current
Peak current
Unit: mA
UDINT
RW
0x445C (17500dec)
13
Motor pole pairs
Number of pole pairs
USINT
RW
0x1 (1dec)
16
Torque constant
Torque constant
Unit: mNm/A
UDINT
RW
0x12C (300dec)
18
Rotor moment of inertia
Motor moment of inertia
Unit: g cm²
UDINT
RW
0x1EF (495dec)
19
Winding inductance
Winding inductance
Unit: 0.1 mH
UINT
RW
0x186 (390dec)
29
Motor I2T warn level
I²t model warning threshold
Unit: %
USINT
RW
0x50 (80dec)
2A
Motor I2T error level
I²t model error threshold
Unit: %
USINT
RW
0x69 (105dec)
2D
Motor thermal time constant
Thermal time constant
Unit: 0.1 s
UINT
RW
0x28 (40dec)
2E
Rated speed
Rated speed
Unit: rpm
UDINT
RW
0x3E8 (1000dec)
30
Winding resistance
Winding resistance
Unit: mOhm
UDINT
RW
0x578 (1400dec)
31
Voltage constant
Motor back‑EMF voltage constant
Unit: µV/(1/min)
UDINT
RW
0x4E20 (20000dec)
34
Configured motor current
Limits the output current.
(The output current is limited to the lower of "Rated current" and "Configured motor current".)
This parameter allows you to prevent the channel from drawing a disproportionately large share of the available UP total current relative to the other channels.
UDINT
RW
0x1618 (5656dec)
Index 2n04 Brake Settings Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Brake Settings Ch.x
USINT
RO
0x18 (24dec)
01
Enable manual override
Enable for manual control of the holding brake. For example, during commissioning, the axis can be moved without being controlled.
If the parameter is set to “True,” the drive controller no longer affects the brake’s state
Must be set to "0" during normal operation.
RW
00
02
Manual brake state
Possible values:
  • 0dec: Release
  • 1dec: Apply
RW
00
05
Brake option
Configuration for inverted motor brakes
Possible values:
  • 0dec Enable output to release brake: Power is supplied to the brake output to release the brake. The brake holds the axis in the de-energized state.
  • 1decDisable output to release brake: Power is supplied to the brake output to engage the brake. The brake releases the axis in a de-energized state
USINT
RW
0x0 (0dec)
09
External override
Choice of a digital input that can be used to open the motor brake independently of the drive controller, e.g. for maintenance.
Possible values:
  • 0dec: Disabled
  • 2dec: Digital Input 1
  • 3dec: Digital Input 1 (only INIT/PREOP/SAFEOP)
  • 4dec: Digital Input 2
  • 5dec: Digital Input 2 (only INIT/PREOP/SAFEOP)
USINT
RW
0x0 (0dec)
11
Release delay
Time the holding brake requires for opening (releasing) after the current was applied.
Unit: ms
UINT
RW
0x0 (0dec)
12
Application delay
Time the holding brake requires for closing (holding) after the current was switched off.
Unit: ms
UINT
RW
0x0 (0dec)
13
Emergency application timeout
Time that the drive waits for the velocity to reach the standstill limit after a stop request.
If the waiting time is exceeded, the holding brake is triggered; regardless of the velocity.
  • Horizontal axes: This parameter must be set at least to the longest time the axis needs to come to a standstill after it has been switched torque-free.
  • Vertical axes: This parameter should be set to a low value to prevent the axis or load from falling very far.
Unit: ms
UINT
RW
0x0 (0dec)
14
Brake moment of inertia
Moment of inertia of the brake.
Unit: g cm²
UINT
RW
0x0 (0dec)
Subindex (hex)
Meaning
Data type
Flags
Default
18
Brake Output Features
Control of a motor brake (depending on the drive controller) via a digital output
Possible values:
  • 0dec: Disabled
  • 1dec: Use Digital Output 1 as additional brake output
  • 2dec: Use Digital Output 2 as additional brake output
USINT
RW
0x0 (0dec)
Index 2n05 Filter Settings Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
USINT
RO
0x19 (25dec)
10
Low pass frequency 1
Unit: Hz
REAL
RW
0.0
11
Low pass damping 1
REAL
RW
0.0
12
High pass frequency 1
Unit: Hz
REAL
RW
0.0
13
High pass damping 1
REAL
RW
0.0
14
Filter type 1
Possible values:
  • 0dec: No_Filter
  • 1dec: Low_pass_filter_1_order
  • 2dec: Phase_correction_filter_1_order
  • 3dec: Low_pass_filter_2_order
  • 4dec: Phase_correction_filter_2_order
  • 5dec: Notch_filter
INT
RW
0x0 (0dec)
15
Low pass frequency 2
Unit: Hz
REAL
RW
0.0
16
Low pass damping 2
REAL
RW
0.0
17
High pass frequency 2
Unit: Hz
REAL
RW
0.0
18
High pass damping 2
REAL
RW
0.0
19
Filter type 2
Possible values:
  • 0dec: No_Filter
INT
RW
0x0 (0dec)
Index 2n0A Digital Output Settings Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
USINT
RO
0x2 (2dec)
01
Use Output 1 as +24V power supply
If “TRUE”: The respective digital output is always active and serves as supply voltage, e.g. for limit switches
RW
00
02
Use Output 2 as +24V power supply
RW
00
Index 2n10 Feedback Settings Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
Feedback Settings Ch.1
USINT
RO
0x17 (23dec)
11
Device type
UDINT
RW
0x0 (0dec)
12
Singleturn bits
Number of single-turn bits used to represent the position in the process image.
The sum of the single-turn bits and multi-turn bits must be 32.
USINT
RW
0x14 (20dec)
13
Multiturn bits
Number of multi-turn bits used to represent the position in the process image.
USINT
RW
0xC (12dec)
14
Observer bandwidth
Bandwidth of the velocity observer in Hz
UINT
RW
0xC8 (200dec)
15
Observer feed-forward
Load ratio in % between internal rotor inertia of the motor and the total inertia of the driven system.
Load ratio = internal moment of inertia / (internal moment of inertia + mass moment of inertia of the load).
Examples:
100 % = load-free
50 % = moments of inertia of input and output are equal
USINT
RW
0x64 (100dec)
17
Position offset
The position offset is subtracted from the raw position of the encoder.
It can only be written with the axis stopped.
DINT
RW
0x0 (0dec)
Index 2n20 Vendor data Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Vendor data Ch.x
USINT
RO
0x18 (24dec)
11
Amplifier peak current
Amplifier peak current (peak value)
Unit: mA
UDINT
RW
0x445C (17500dec)
12
Amplifier rated current
Amplifier rated current (peak value)
Unit: mA
UDINT
RW
0x1618 (5656dec)
13
Amplifier thermal time constant
Unit: 0.1 s
UINT
RW
0x23 (35dec)
14
Amplifier overcurrent threshold
Per‑phase instantaneous current threshold for short‑circuit detection
Unit: mA
UDINT
RW
0x7530 (30000dec)
15
Max rotary field frequency
Maximum rotary field frequency
Unit: Hz
UINT
RW
0x257 (599dec)
18
Vendor feature bits
UDINT
RW
0x0 (0dec)
1A
Amplifier Rated Sum Current
Unit: mA
UDINT
RW
0x2C30 (11312dec)
Index 2n08 DMC Settings Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
DMC Settings Ch.x
USINT
RO
0x17 (23dec)
07
Emergency deceleration
Deceleration for the emergency stop ramp. (In ms from rated motor speed to standstill)
UINT
RW
0x64 (100dec)
08
Calibration position
If homing is successful, the “Actual position” is set to this value.
LINT
RW
0x0 (0dec)
09
Calibration velocity (towards plc cam)
Velocity when hitting the cam in 10000ths of the rated motor speed.
INT
RW
0x64 (100dec)
0A
Calibration Velocity (off plc cam)
Velocity when driving off the cam in 10000ths of the rated motor speed.
INT
RW
0xA (10dec)
0E
Modulo factor
Feedback increments for one mechanical revolution.
LINT
RW
0x100000000 (4294967296dec)
12
Block calibration torque limit
Torque limitation for approaching the end stop. In parts per thousand of the rated motor current.
UINT
RW
0x64 (100dec)
13
Block calibration stop distance
After reaching the calibration position, the axis moves out of the end position by this distance.
LINT
RW
14
Block calibration lag threshold
When this following error is exceeded, the axis is in the end position.
LINT
RW
15
Target position window
Target position window:
The in-target bit is set when the axis is within this window for at least the time set under subindex 16.
LINT
RW
0x16C16C1 (23860929dec)
16
Target position monitor time
See subindex 15
Unit: ms
UINT
RW
0x14 (20dec)
17
Target position timeout
When the setpoint generator has reached its end position and the axis is not in the target window after this time has elapsed, the task is terminated and the in-target bit is not set.
Unit: ms
UINT
RW
0x1770 (6000dec)
Index 2n09 DMC Features Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
DMC Features Ch.x
USINT
RO
0x1B (27dec)
13
Invert calibration cam search direction
Invert the direction of movement to search for the limit switch.
Default: FALSE = search with positive direction of rotation.
RW
00
14
Invert sync impulse search direction
Invert the direction of rotation to exit the limit switch.
Default: TRUE = exit in negative direction of rotation.
RW
01
19
Calibration cam source
Source for the reference switch:
  • 0dec: Input 1
  • 1dec: Input 2
USINT
RW
0x0 (0dec)
1A
Calibration cam active level
State of the reference switch in the actuated state:
  • 0dec: Hi
  • 1dec: Low
USINT
RW
0x0 (0dec)
1B
Latch source
Source for the latch unit:
  • 0dec: Input 1
  • 1dec: Input 2
USINT
RW
0x0 (0dec)
F800 DRV Amplifier Settings
Index (hex)
Meaning
Data Type
Flags
Default
F800:0
USINT
RO
0x17 (23dec)
F800:10
Nominal DC link voltage
Rated DC link voltage.
Unit: mV
UDINT
RW
0xBB80 (48000dec)
F800:11
Min DC link voltage
Minimum DC link voltage.
Unit: mV
UDINT
RW
0x1A90 (6800dec)
F800:12
Max DC link voltage
Maximum DC link voltage.
Unit: mV
UDINT
RW
0xEA60 (60000dec)
F800:15
Amplifier Temperature warn level
Amplifier temperature warning threshold.
Unit: 0.1 °C
UINT
RW
0x320 (800dec)
F800:16
Amplifier Temperature error level
Amplifier temperature error threshold.
Unit: 0.1 °C
UINT
RW
0x3E8 (1000dec)
F800:17
Feature bits
UDINT
RW
0x0 (0dec)