Input data, output data
Index 2n08 Inputs Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Inputs Ch.x
USINT
RO
0x6 (6dec)
01
Info data 1
Synchronous information
Selection via subindex 2n02:55
UINT
RO
02
Info data 2
Selection via subindex 2n02:56
UINT
RO
03
Info data 3
Selection via subindex 2n02:58
UINT
RO
04
Dyninput cycle counter
USINT
RO
06
Velocity resulting from differentiation
DINT
RO
Index 2n0B Remote Outputs Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Remote Outputs Ch.x
USINT
RO
0xF (15dec)
04
Dynoutput cycle counter
USINT
RO
06
Target velocity
Configured target velocity
232/16000 increments correspond to one motor revolution per second
DINT
RO
09
Target torque
Configured target torque
The value is specified in thousandths (1/1000) of parameter 6075 "Motor rated current".
Calculation formula:
M = ((Torque actual value / 1000) × rated current)) × torque constant (0x2003:16)
INT
RO
0A
Torque offset
External torque feedforward
INT
RO
0E
Commutation angle
Commutation angle for CSTCA mode.
Unit: 216 / 360°
UINT
RO
0F
Velocity offset
External velocity feedforward
DINT
RO
Index 2n00 DMC Inputs Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
DMC Inputs Ch.x
USINT
RO
0x3C (60dec)
02
DMC__FeedbackStatus__Latch extern valid
An edge was detected on the external input and latched.
RO
03
DMC__FeedbackStatus__Set counter done
The setting of the feedback position was successful.
This bit remains present until “Set counter” is released again
RO
0D
DMC__FeedbackStatus__Status of extern latch
Status of the external latch input.
RO
11
DMC__DriveStatus__Ready to enable
The drive hardware is ready for activation.
RO
12
The drive hardware is activated.
RO
13
DMC__DriveStatus__Warning
A warning is pending in the drive.
RO
14
DMC__DriveStatus__Error
An error is pending in the drive.
The “Ready to enable” bit and the “Ready” bit are set to FALSE.
RO
15
DMC__DriveStatus__Moving positive
The axis moves in positive direction.
RO
16
DMC__DriveStatus__Moving negative
The axis moves in negative direction.
RO
1C
DMC__DriveStatus__Digital input 1
Status of the first digital input.
RO
1D
DMC__DriveStatus__Digital input 2
Status of the second digital input.
RO
21
DMC__PositioningStatus__Busy
The positioning task is running.
RO
22
DMC__PositioningStatus__In-Target
The axis is at the target position.
RO
Subindex (hex)
Meaning
Data Type
Flags
Default
23
DMC__PositioningStatus__Warning
Warning.
RO
24
DMC__PositioningStatus__Error
Error.
RO
25
DMC__PositioningStatus__Calibrated
The axis is calibrated.
RO
26
DMC__PositioningStatus__Accelerate
The axis accelerates.
RO
27
DMC__PositioningStatus__Decelerate
The axis is decelerating.
RO
28
DMC__PositioningStatus__Ready to execute
The drive motion control is ready to accept a command.
This bit is FALSE
  • ... if the drive has a fault
  • ... if the drive is not activated
... as long as the “PositioningControl__Execute” is pending.
RO
31
DMC__Set position
Current target position specified by the ramp generator in feedback increments.
LINT
RO
32
DMC__Set velocity
Current velocity specified by the ramp generator in 10000ths of the rated motor speed
INT
RO
33
DMC__Actual drive time
The time since the start of the travel command in ms.
Stops when the target position is reached.
UDINT
RO
34
DMC__Actual position lag
Following error.
LINT
RO
35
DMC__Actual velocity
Current velocity in 10000ths of the rated motor speed.
INT
RO
36
Current position from the feedback (incl. possible offsets due to homing, ...).
LINT
RO
37
DMC__Error id
Error Id (Identical to Diag History).
UDINT
RO
38
DMC__Input cycle counter
Incremented with each process data cycle.
USINT
RO
39
DMC__Channel id
USINT
RO
3A
DMC__Latch value
Feedback position at latch time.
LINT
RO
3B
DMC__Cyclic info data 1
Synchronous info data
INT
RO
3C
DMC__Cyclic info data 2
INT
RO
Index 2n04 DMC Outputs Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
DMC Outputs Ch.x
USINT
RO
0x36 (54dec)
02
DMC__FeedbackControl__Enable latch extern on positive edge
Latches to the positive edge of the external input
RO
03
DMC__FeedbackControl__Set counter
With a rising edge, “Actual position” is set to the value of “Set counter value”.
RO
04
DMC__FeedbackControl__Enable latch extern on negative edge
Latches to the negative edge of the external input
RO
11
DMC__DriveControl__Enable
Activate drive
RO
12
DMC__DriveControl__Reset
Perform a reset of the drive hardware
RO
21
DMC__PositioningControl__Execute
Start motion command with rising edge
The task runs as long as this bit is set or until the command is completed.
If the level drops during travel, the axis is brought to a standstill with the deceleration specified for the task.
RO
22
DMC__PositioningControl__Emergency stop
In the event of a rising edge, decelerate to a standstill with the emergency stop ramp
RO
31
DMC__Set counter value
s. 0x2n04:03
LINT
RO
32
DMC__Target position
Position specification in feedback increments
LINT
RO
33
DMC__Target velocity
Maximum velocity during the motion command in 10000ths of the rated motor speed
INT
RO
34
DMC__Start type
Type of positioning task:
0x0001: Absolute
0x0002: Relative
0x0003: Endless +
0x0004: Endless -
0x0105: Modulo short
0x0205: Modulo +
0x0305: Modulo -
0x6000: Cali PLC cam
0x6200: Cali Block
0x6E00: Cali set
0x6F00: Cali clear
UINT
RO
35
DMC__Target acceleration
Acceleration: time in ms from standstill to reaching the rated motor speed
UINT
RO
36
DMC__Target deceleration
Deceleration: time in ms for the deceleration from the rated motor speed to standstill
UINT
RO
Index 6n3E TxPDO Data Invalid Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
TxPDO Data Invalid Ch.1
USINT
RO
0x2 (2dec)
02
Position actual value
RO
Index 6n3F Error code Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Error code Ch.x
UINT
RO
Index 6n40 Controlword Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Controlword Ch.x
Bit 0: Switch on
Bit 1: Enable voltage
Bit 2: reserved
Bit 3: Enable operation
Bit 4 - 6: reserved
Bit 7: Fault reset
Bit 8 - 15: reserved
UINT
RO
Index 6n41 Statusword Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Statusword Ch.x
Bit 0: Ready to switch on
Bit 1: Switched on
Bit 2: Operation enabled
Bit 3: Fault
Bit 4: reserved
Bit 5: reserved
Bit 6: Switch on disabled
Bit 7: Warning
Bit 8 + 9: reserved
Bit 10: TxPDOToggle
Bit 11: Internal limit active
Bit 12: Drive follows the command value
Bit 13: Input cycle counter
Bit 14 - 15: reserved
UINT
RO
Index 6n5E Fault reaction option code Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Possible values:
  • 0: Disable drive function, motor is free to rotate
  • 1: Slow down on slow down ramp
UINT
RO
0x0001 (1dec)
Index 6n60 Modes of operation Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Possible values:
  • -125dec: Drive Motion Control (DMC)
  • -9dec: Cyclic synchronous velocity mode remote (CSVr)
  • 8dec: Cyclic synchronous position mode (CSP)
  • 9dec: Cyclic synchronous velocity mode (CSV)
  • 11dec: Cyclic synchronous torque mode with commutation angle (CSTCA)
SINT
RO
0x08 (8dec)
Index 6n61 Modes of operation display Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Possible values:
USINT
RO
Index 6n64 Position actual value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Actual position
220 increments correspond to one motor revolution
DINT
RO
Index 6n65 Following error window Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
The specified value must be multiplied by the corresponding scaling factor
  • 0xFFFFFFFF (-1dec) = Following error monitoring off.
  • Any other value = following error monitoring on
UDINT
RO
0xFFFFFFFF (-1dec)
Index 6n66 Following error time out Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Following error monitoring timeout
Unit: [ms]
If the following error exceeds the following‑error window for longer than the timeout set here, the system triggers an error response.
UINT
RO
Index 6n6C Velocity actual value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Actual velocity
DINT
RO
Index 6n7B Position range limit Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
USINT
RO
0x2 (2dec)
01
Min position range limit
Minimum value for the position display of setpoints and actual values. If the value falls below this limit, it underflows to "Max position range limit"
"Min position range limit" must always be lower than "Max position range limit"
DINT
RW
0x80000000 (-2147483648dec)
02
Maximum value for the position display of setpoints and actual values. If this limit is exceeded, the value overflows to "Min position range limit"
"Max position range limit" must always be greater than "Min position range limit"
DINT
RW
0x7FFFFFFF (2147483647dec)
Index 6n71 Target torque Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Target torque Ch.x
INT
RO
Index 6n72 Max torque Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Max torque Ch.x
Maximum torque
UINT
RO
Index 6n75 Motor rated current Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Nominal current of the motor
Unit: [mA]
UDINT
RO
Index 6n77 Torque actual value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Actual torque
INT
RO
Index 6n79 DC link circuit voltage Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Measured value of the DC link voltage
Unit: [mV]
UDINT
RO
Index 6n7A Target position Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Configured actual position
DINT
RO
Index 6n7E Polarity Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Polarity Ch.x
Possible values:
  • 0: global polarity inversion disabled
  • 1: global polarity inversion
USINT
RO
0
Index 6n80 Max motor speed Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Maximum velocity of the motor
Unit: [1/min]
UDINT
RO
0x000186A0 (100000dec)
Index 6n91 Gear ratio Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
Gear ratio Ch.x
USINT
RO
0x2 (2dec)
01
Motor shaft revolutions
These parameters are used to scale all positions and velocities from the motor side to the load side of a gear unit.
Motor shaft revolutions” describes the number of motor revolutions required to achieve the number of load revolutions configured in “Driving shaft revolutions”.
Example: For a reduction gear in which 5 motor revolutions result in 2 load revolutions, set the parameters as follows:
  • Motor shaft revolutions = 5
  • Driving shaft revolutions = 2
UDINT
RW
0x1 (1dec)
02
UDINT
RW
0x1 (1dec)
Index 6nB1 Velocity offset Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
DINT
RO
Index 6nB2 Torque offset Ch.x
Index (hex)
Meaning
Data type
Flags
Default
0
Torque offset Ch.x
INT
RO
Index 6nB8 Touch probe function Ch.x
Index (hex)
Meaning
Data type
Flags
Default
0
  • Bit 0: TP1 enable
  • Bit 1: TP1 Continous
  • Bit 2: TP1 Trigger mode
  • Bit 3: -
  • Bit 4: TP1 Enable pos. Edge
  • Bit 5: TP1 Enable neg. edge
  • Bit 6: -
  • Bit 7: -
  • Bit 8: TP2 Enable
  • Bit 9: TP2 Continous
  • Bit 10: TP2 Trigger mode
  • Bit 11: -
  • Bit 12: TP2 Enable pos. Edge
  • Bit 13: TP2 Enable neg. edge
  • Bit 14: -
  • Bit 15: -
UINT
RO
Index 6nB9 Touch probe status Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
  • Bit 0: TP1 Enable
  • Bit 1: TP1 Pos. value stored
  • Bit 2: TP1 Input
  • Bit 7: TP1 Input
  • Bit 8: TP2 Enable
  • Bit 9: TP2 Pos. value stored
  • Bit 10: TP2 Neg. value stored
  • Bit 15: TP2 Input
UINT
RO
Index 6nBA Touch probe 1 positive edge Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Position value at the last detected rising edge of TP1.
DINT
RO
Index 6nBB Touch probe 1 negative edge Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
DINT
RO
Index 6nBC Touch probe 2 positive edge Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Position value at the last detected rising edge of TP2.
DINT
RO
Index 6nBD Touch probe 2 negative edge Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Position value at the last detected falling edge of TP2.
DINT
RO
6nD0 Touch probe source Ch.x
Subindex (hex)
Meaning
Data Type
Flags
Default
0
USINT
RO
0x2 (2dec)
01
Touch probe 1 source
Possible values:
  • 1dec: Touch probe input 1
INT
RW
0x1 (1dec)
02
Touch probe 2 source
Possible values:
  • 2dec: Touch probe input 2
INT
RW
0x2 (2dec)
Index 6nD1 Touch probe time stamp 1 positive value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
UDINT
RO
Index 6nD2 Touch probe time stamp 1 negative value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Position value at the last detected falling edge of TP1
UDINT
RO
Index 6nD3 Touch probe time stamp 2 positive value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
UDINT
RO
Index 6nD4 Touch probe time stamp 2 negative value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
UDINT
RO
Index 6nD9 Supported synchronization functions Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
UDINT
RO
0x0000003 (3dec)
Index 6nDA Synchronization function settings Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
UDINT
RO
Index 6nE0 Positive torque limit value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Torque limit in the positive direction of rotation
UINT
RO
0x7FFF (32767dec)
Index 6nE1 Negative torque limit value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Negative torque limit value Ch.1
Torque limit in the negative direction of rotation
UINT
RO
0x7FFF (32767dec)
Index 6nEA Commutation angle Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Commutation angle for the CSTCA operating mode
Unit: 216 / 360°
UINT
RO
Index 6nF4 Following error actual value Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Current following error
DINT
RO
Index 6nFD Digital Inputs Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Digital Inputs Ch.x
UDINT
RO
Index 6nFE Digital Outputs Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
USINT
RO
0x1 (1dec)
01
Digital Outputs
Controls the digital outputs of the digital combination channels:
  • DIO1: Bit 16 (0x00010000)
  • DIO2: Bit 17 (0x00020000)
UDINT
RW
0x0 (0dec)
Index 6nFF Target velocity Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Configured actual velocity
DINT
RO
Index 6n02 Supported drive modes Ch.x
Subindex (hex)
Meaning
Data type
Flags
Default
0
Specification of the supported operating modes:
  • Bit 0: PP
  • Bit 1: VL
  • Bit 2: PV
  • Bit 3: TQ
  • Bit 4: R
  • Bit 5: HM
  • Bit 6: IP
  • Bit 7: CSP
  • Bit 8: CSV
  • Bit 9: CST
  • Bit 10: CSTCA
  • Bit 11…15: reserved
  • Bit 16…31: Manufacturer-specific
UDINT
RO
0x00000580 (1408dec)
